Gateways and Energy Servers
Schneider Electric support forum to share knowledge about product selection, installation and troubleshooting for EcoStruxure Panel Server, PowerTag, Com'X, Link150…
User | Count |
---|---|
82 | |
46 | |
29 | |
28 |
Link copied. Please paste this link to share this article on your social media post.
Team,
We have notified a weird issue in one of our REM EGX300. The Datalog files are sent in Chinese instead of English.
网关名称;网关序列号;网关IP地址;网关MAC地址;设备名称;设备本地 ID;设备类型ID;设备类型名称;记录间隔;历史间隔次数
EGX300;53109731;10.140.164.17;00:80:67:86:52:BE;CN-HZ1-M-25W-01;1;32500;PM3250/PM3255;15;0
;;;主题ID1;主题ID2;主题ID3;主题ID4;主题ID5
;;;1617;1621;1625;1731;1008
错误;时区(UTC偏移) (分钟);本地时间戳;视在电能 (kVAh);有功电能(kWh);无功电能(kVARh);需量有功 (kW);相电流平均值
0;480;2014-07-28 15:15:00;416311,690;411154,974;58915,331;222,820;350,485
0;480;2014-07-28 15:30:00;416368,144;411210,851;58923,379;223,480;354,485
0;480;2014-07-28 15:45:00;416423,598;411265,719;58931,424;219,495;336,480
0;480;2014-07-28 16:00:00;416477,742;411319,272;58939,394;214,210;328,482
I guess someone unaware changed a special setting in EGX300. Unfortunately I don't know how to recover the description setting in English. Who can do me a favor?
Many thanks in anticipation!
Best regards,
Quan
Link copied. Please paste this link to share this article on your social media post.
Hello Quan,
Log into your EGX300 as an Administrator and change the language setting to English:
1. Click on Setup
2. Click User Accounts
3. Change the Language for the Administrator user account
See images below:
I hope this helps.
James
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Hello James,
Thanks for your answer! It means that Datalog should be recorded into files with Admininistrator Language setting. Also I need to create a specific account which will be used by local maintance engineers. The admininstrator account might be hidden.
Thanks again.
Quan
Link copied. Please paste this link to share this article on your social media post.
Actually, there's an easier way that will avoid you to have to create different accounts. There's an hidden page that will allow you to set the export language to English. Just go to HTTP://<IP_Address>/evo_compatibility.shtml
Just check the box "Always Export in English".
Boom, you're done! 🙂
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.