Hello Experts,
I am trying to export log data from ComX 510 to EMS server automatically.
I have successfully tested with FTP.
May i know how can i use HTTP & HTTPS methods for data export, as client restrict us to use FTP method.
Thanks in Advance.
Link copied. Please paste this link to share this article on your social media post.
Hello,
To export data log file from the Com'X via HTTP or HTTPs, you will have to setup a web server and configure it to receive files from the Com'X. Typically this is done with a script written in cgi or perl.
Here is a document on how to do this on the EGX300. The Com'X works the same way. Although, the fieldname is different.
EGX 300 - Logged Data Export over HTTP ====================================== Rationale --------- Provide export of EGX300 logged data over HTTP. This allows EGX's inside firewalled and/or NAT'ed (Network Address Translated) networks to export their logged data to external servers without port-forwarding or other complications. Background ---------- EGX 300 supports exporting logged data over Email (SMTP) and FTP. This project adds the capability to "push" logged data over an HTTP POST message. By doing so, common HTTP servers can aggregate logged data from one or many EGX's. Approach -------- Provide export of EGX300 logged data over HTTP 'POST' method. Any WWW server that supports POST messages and installing one's own CGI handlers is sufficient. Our testing used Apache 1.3.34 (www.apache.org) running on FreeBSD (www.freebsd.org). The same scripts will work on a variety of WWW servers and operating systems. (Linux, OpenBSD, Solaris, etc.) The EGX will post a message specifying the filename of where to deposit the POST data. By default this is 'datafile1', but this can be customized in the EGX web interface. This would be useful in the case where you already have a POST handler that uses a different field name for this purpose. Sample Upload handler - Python ------------------------------ The following is the full text of an EGX-compatible Python script that accepts HTTP uploads from EGX's. Install it into the directory on your chosen web server where CGI scripts reside. (this varies by hosting provider) #! /usr/bin/env python # # based on http://webpython.codepoint.net/cgi_tutorial # import cgi, os # cgitb module gives specific tracebacks when there is a problem, # rather than just a generic failure message. import cgitb cgitb.enable() try: # Windows needs stdio set for binary mode. import msvcrt msvcrt.setmode (0, os.O_BINARY) # stdin = 0 msvcrt.setmode (1, os.O_BINARY) # stdout = 1 except ImportError: pass form = cgi.FieldStorage() # Generator to buffer file chunks def fbuffer(f, chunk_size=10000): while True: chunk = f.read(chunk_size) if not chunk: break yield chunk # A nested FieldStorage instance holds the file fileitem = form['datafile1'] # Test if the file was uploaded if fileitem.filename: # strip leading path from file name to avoid directory traversal attacks fn = os.path.basename(fileitem.filename) # Customize this directory to match your WWW server outfil = open('/usr/local/www/data/uploads/' + fn, 'wb', 10000) # Read the file in chunks for chunk in fbuffer(fileitem.file): outfil.write(chunk) outfil.close() message = 'The file "' + fn + '" was uploaded successfully\n' else: message = 'No file was uploaded' print """\ Content-Type: text/html\n <html><body> <p>%s</p> </body></html> """ % (message,) Sample Upload handler - PERL ---------------------------- The following is the full text of an EGX-compatible PERL script to accept HTTP file uploads. #!/usr/bin/perl -wT use strict; use CGI; # set maximum allowable size to 5MB $CGI::POST_MAX = 1024 * 5000; my $safe_filename_characters = "a-zA-Z0-9_.-"; my $upload_dir = "/usr/local/www/data/uploads"; my $query = new CGI; my $filename = $query->param('datafile1'); if ( !$filename ) { print $query->header ( ); print "There was a problem uploading your file; try a smaller file."; exit; } my ( $name, $path, $extension ) = fileparse ( $filename, '\..*' ); $filename = $name . $extension; $filename =~ tr/ /_/; $filename =~ s/[^$safe_filename_characters]//g; if ( $filename =~ /^([$safe_filename_characters]+)$/ ) { $filename = $1; } else { die "Filename contains invalid characters"; } open ( UPLOADFILE, ">", "$upload_dir/$filename" ) or die "$!"; binmode(UPLOADFILE); my $upload_filehandle = $query->upload("datafile1"); while ( <$upload_filehandle> ) { print UPLOADFILE; } close UPLOADFILE; print $query->header ( ); print <<END_HTML; <html> <body> <p>The file $filename was uploaded successfully</p> </body> </html> END_HTML Microsoft Internet Information Services (IIS) --------------------------------------------- IIS can most naturally use Active Server Pages (ASP) or ASP.NET to upload files. Alternately, IIS can be configured to support CGI. Unfortunately, IIS does not support CGI as installed "out of the box". Then one may use PERL/Python/etc. CGI scripts as above. Sample Upload handler - Microsoft Internet Information Services (IIS) w/ ASP.NET -------------------------------------------------------------------------------- using System; using System.Collections.Generic; using System.Linq; using System.Web; using System.Web.UI; using System.Web.UI.WebControls; using System.IO; namespace EnergyDataReceiver { public partial class filepost : System.Web.UI.Page { protected void Page_Load(object sender, EventArgs e) { String TempFileName; HttpFileCollection myFileCollection = Request.Files; for (int Loop1 = 0; Loop1 < myFileCollection.Count; Loop1++) { string fname = myFileCollection[Loop1].FileName; // Create a new file name. TempFileName = "C:\\TempFiles\\File_" + Loop1.ToString() + "_" + Path.GetFileName(fname); // Save the file. myFileCollection[Loop1].SaveAs(TempFileName); } } } } References ---------- 1. RFC 1867 "Form-based File Upload in HTML", http://www.ietf.org/rfc/rfc1867.txt 2. File Upload with ASP.NET, http://www.codeproject.com/KB/aspnet/fileupload.aspx 3. Uploading a file to IIS using a browser, http://support.microsoft.com/default.aspx/kb/189651 4. Google Search of "IIS cgi" yields quite a few pointers and tutorials: http://www.google.com/search?q=IIS+cgi
Best regards,
Randi
Link copied. Please paste this link to share this article on your social media post.
Hello,
To export data log file from the Com'X via HTTP or HTTPs, you will have to setup a web server and configure it to receive files from the Com'X. Typically this is done with a script written in cgi or perl.
Here is a document on how to do this on the EGX300. The Com'X works the same way. Although, the fieldname is different.
EGX 300 - Logged Data Export over HTTP ====================================== Rationale --------- Provide export of EGX300 logged data over HTTP. This allows EGX's inside firewalled and/or NAT'ed (Network Address Translated) networks to export their logged data to external servers without port-forwarding or other complications. Background ---------- EGX 300 supports exporting logged data over Email (SMTP) and FTP. This project adds the capability to "push" logged data over an HTTP POST message. By doing so, common HTTP servers can aggregate logged data from one or many EGX's. Approach -------- Provide export of EGX300 logged data over HTTP 'POST' method. Any WWW server that supports POST messages and installing one's own CGI handlers is sufficient. Our testing used Apache 1.3.34 (www.apache.org) running on FreeBSD (www.freebsd.org). The same scripts will work on a variety of WWW servers and operating systems. (Linux, OpenBSD, Solaris, etc.) The EGX will post a message specifying the filename of where to deposit the POST data. By default this is 'datafile1', but this can be customized in the EGX web interface. This would be useful in the case where you already have a POST handler that uses a different field name for this purpose. Sample Upload handler - Python ------------------------------ The following is the full text of an EGX-compatible Python script that accepts HTTP uploads from EGX's. Install it into the directory on your chosen web server where CGI scripts reside. (this varies by hosting provider) #! /usr/bin/env python # # based on http://webpython.codepoint.net/cgi_tutorial # import cgi, os # cgitb module gives specific tracebacks when there is a problem, # rather than just a generic failure message. import cgitb cgitb.enable() try: # Windows needs stdio set for binary mode. import msvcrt msvcrt.setmode (0, os.O_BINARY) # stdin = 0 msvcrt.setmode (1, os.O_BINARY) # stdout = 1 except ImportError: pass form = cgi.FieldStorage() # Generator to buffer file chunks def fbuffer(f, chunk_size=10000): while True: chunk = f.read(chunk_size) if not chunk: break yield chunk # A nested FieldStorage instance holds the file fileitem = form['datafile1'] # Test if the file was uploaded if fileitem.filename: # strip leading path from file name to avoid directory traversal attacks fn = os.path.basename(fileitem.filename) # Customize this directory to match your WWW server outfil = open('/usr/local/www/data/uploads/' + fn, 'wb', 10000) # Read the file in chunks for chunk in fbuffer(fileitem.file): outfil.write(chunk) outfil.close() message = 'The file "' + fn + '" was uploaded successfully\n' else: message = 'No file was uploaded' print """\ Content-Type: text/html\n <html><body> <p>%s</p> </body></html> """ % (message,) Sample Upload handler - PERL ---------------------------- The following is the full text of an EGX-compatible PERL script to accept HTTP file uploads. #!/usr/bin/perl -wT use strict; use CGI; # set maximum allowable size to 5MB $CGI::POST_MAX = 1024 * 5000; my $safe_filename_characters = "a-zA-Z0-9_.-"; my $upload_dir = "/usr/local/www/data/uploads"; my $query = new CGI; my $filename = $query->param('datafile1'); if ( !$filename ) { print $query->header ( ); print "There was a problem uploading your file; try a smaller file."; exit; } my ( $name, $path, $extension ) = fileparse ( $filename, '\..*' ); $filename = $name . $extension; $filename =~ tr/ /_/; $filename =~ s/[^$safe_filename_characters]//g; if ( $filename =~ /^([$safe_filename_characters]+)$/ ) { $filename = $1; } else { die "Filename contains invalid characters"; } open ( UPLOADFILE, ">", "$upload_dir/$filename" ) or die "$!"; binmode(UPLOADFILE); my $upload_filehandle = $query->upload("datafile1"); while ( <$upload_filehandle> ) { print UPLOADFILE; } close UPLOADFILE; print $query->header ( ); print <<END_HTML; <html> <body> <p>The file $filename was uploaded successfully</p> </body> </html> END_HTML Microsoft Internet Information Services (IIS) --------------------------------------------- IIS can most naturally use Active Server Pages (ASP) or ASP.NET to upload files. Alternately, IIS can be configured to support CGI. Unfortunately, IIS does not support CGI as installed "out of the box". Then one may use PERL/Python/etc. CGI scripts as above. Sample Upload handler - Microsoft Internet Information Services (IIS) w/ ASP.NET -------------------------------------------------------------------------------- using System; using System.Collections.Generic; using System.Linq; using System.Web; using System.Web.UI; using System.Web.UI.WebControls; using System.IO; namespace EnergyDataReceiver { public partial class filepost : System.Web.UI.Page { protected void Page_Load(object sender, EventArgs e) { String TempFileName; HttpFileCollection myFileCollection = Request.Files; for (int Loop1 = 0; Loop1 < myFileCollection.Count; Loop1++) { string fname = myFileCollection[Loop1].FileName; // Create a new file name. TempFileName = "C:\\TempFiles\\File_" + Loop1.ToString() + "_" + Path.GetFileName(fname); // Save the file. myFileCollection[Loop1].SaveAs(TempFileName); } } } } References ---------- 1. RFC 1867 "Form-based File Upload in HTML", http://www.ietf.org/rfc/rfc1867.txt 2. File Upload with ASP.NET, http://www.codeproject.com/KB/aspnet/fileupload.aspx 3. Uploading a file to IIS using a browser, http://support.microsoft.com/default.aspx/kb/189651 4. Google Search of "IIS cgi" yields quite a few pointers and tutorials: http://www.google.com/search?q=IIS+cgi
Best regards,
Randi