Ask our Experts
Didn't find what you are looking for? Ask our experts!
Share Your Feedback – Help Us Improve Search on Community! Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately. Click here to take the survey
Schneider Electric support forum to share knowledge about product selection, installation and troubleshooting for EcoStruxure Panel Server, PowerTag, Com'X, Link150…
Search in
Link copied. Please paste this link to share this article on your social media post.
Hello,
I'm making a custom driver to read the registers of a Kamstrup 602 Multical meter. So far measurements are ok except for one value, "water volume". heat energy, power and temperature are fine. I just don't know why the water volume is incorrect. When i read the registers with some external software "Cas Modbus scan" the values indicated in float 32 are equal to the device display(206131m³), but in the com'X510 i get the value 205824m³. when reading the device register with the Com'X I get the same values in HEX so i gues there is an error in the conversion to float 32



Best regards
Koen
Link copied. Please paste this link to share this article on your social media post.
Hi Koen,
I apologize for the late response. We have made modifications to the conversion algorithms, which may correct this issue. These modifications are available in firmware version 5.2.0 and later.
Best regards,
Randi
You’ve reached the end of your document
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.