Hello,
I'm making a custom driver to read the registers of a Kamstrup 602 Multical meter. So far measurements are ok except for one value, "water volume". heat energy, power and temperature are fine. I just don't know why the water volume is incorrect. When i read the registers with some external software "Cas Modbus scan" the values indicated in float 32 are equal to the device display(206131m³), but in the com'X510 i get the value 205824m³. when reading the device register with the Com'X I get the same values in HEX so i gues there is an error in the conversion to float 32



Best regards
Koen
Link copied. Please paste this link to share this article on your social media post.
Hi Koen,
I apologize for the late response. We have made modifications to the conversion algorithms, which may correct this issue. These modifications are available in firmware version 5.2.0 and later.
Best regards,
Randi