Ask our Experts
Didn't find what you are looking for? Ask our experts!
Share Your Feedback – Help Us Improve Search on Community! Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately. Click here to take the survey
Schneider Electric support forum to share knowledge about product selection, installation and troubleshooting for EcoStruxure Panel Server, PowerTag, Com'X, Link150…
Search in
Link copied. Please paste this link to share this article on your social media post.
Hello Team,
I have created Custom drivers depending on Schneider make PM5310 model to get extra available parameters form device in ComX510, but unfortunately newly added parameters are not matched with real-time data on meter.
please find attach document to understand the actual activity i have did.
same problem i have face during Cummins DG communication with ComX510.
please correct me.....
Thanks in advance.
Link copied. Please paste this link to share this article on your social media post.
Best bet would be to contact technical support and include a copy of your custom driver. One thing that has happened to me sometimes is address verses register is off by one I can't remember if I needed to increase the address by 1 or decrease it by 1.
Posted: 2018-06-26 08:28 AM
Link copied. Please paste this link to share this article on your social media post.
Hi Sushant,
Can you attach an export of your Custom Model? I'd be happy to hook up a meter here and take a look if I can help you fix the model.
Best,
Colton
Link copied. Please paste this link to share this article on your social media post.
Charles MurisonColton Peltier
Sorry for delayed revert...Facing some Community login issue.
Problem was resolved by decreasing addressing by 1.
You’ve reached the end of your document
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.