Hello Team,
I have created Custom drivers depending on Schneider make PM5310 model to get extra available parameters form device in ComX510, but unfortunately newly added parameters are not matched with real-time data on meter.
please find attach document to understand the actual activity i have did.
same problem i have face during Cummins DG communication with ComX510.
please correct me.....
Thanks in advance.
Link copied. Please paste this link to share this article on your social media post.
Best bet would be to contact technical support and include a copy of your custom driver. One thing that has happened to me sometimes is address verses register is off by one I can't remember if I needed to increase the address by 1 or decrease it by 1.
Posted: 2018-06-26 08:28 AM
Link copied. Please paste this link to share this article on your social media post.
Hi Sushant,
Can you attach an export of your Custom Model? I'd be happy to hook up a meter here and take a look if I can help you fix the model.
Best,
Colton
Link copied. Please paste this link to share this article on your social media post.
Charles MurisonColton Peltier
Sorry for delayed revert...Facing some Community login issue.
Problem was resolved by decreasing addressing by 1.