Com'X510 Standalone Logging Time

Gateways and Energy Servers

Schneider Electric support forum to share knowledge about product selection, installation and troubleshooting for EcoStruxure Panel Server, PowerTag, Com'X, Link150…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Gateways and Energy Servers
  • Com'X510 Standalone Logging Time
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Romain_Polette
Kirk Romain_Polette Kirk
117
Guillaume_Evrard
Captain Guillaume_Evrard Captain
59
Randi_Dolan
Commander Randi_Dolan Commander
46
View All

Recommended Forums

  • Metering & Power Quality

  • SmartConnector Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Gateways and Energy Servers
Start a Topic
Solved
KuanKhoon
Lt. Commander KuanKhoon Lt. Commander
Lt. Commander

Posted: ‎2016-01-04 06:06 PM

0 Likes
6
2532
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2016-01-04 06:06 PM

Com'X510 Standalone Logging Time

Good Morning to all,

My inaugural post for 2016. Starting with a very simple question, what is the duration the Com'X 510 can log for given the following,

1) Number of devices logging

2) Number of parameters logged per device

3) Logging frequency (1 minute, 5 minute, etc.)

I understand from the previous webex training that the logging time can be very flexible and also very long dependent on the above. However to date we do not have a documented guaranteed deliverable to the customer with the exception of saying we have a 4GB SD card (and the customer comes back to say can they have more? 4GB? we are going to 32GB standard.).

This is unlike for the previous EGX300 where we know, for every device, it is allotted 171072 entries. The more parameters, and the higher the logging frequency, you scale down accordingly.

Does the Com'X 510 work the same way?

Best Regards,

Tan Kuan Khoon

Senior Product Specialist

Partner & Industry Business

Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
JamesJeanette
Commander JamesJeanette Commander
Commander

Posted: ‎2016-01-15 09:56 AM

0 Likes
5
2348
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2016-01-15 09:56 AM

Hello KK,

There are varying factors to consider; however here is what we support:

The Com'X 510 can support 32 devices at 30 topics each at 5 minute intervals for 2 years of stored historical data. 

The calculation above can be adapted...adding more devices, and less topics plus longer intervals or some variation.

We do not make any differences on the size of the SD Card. 

Adding Robert Jennings (Clay) here in case you need further information.

James

See Answer In Context

Reply
Replies 6
JamesJeanette
Commander JamesJeanette Commander
Commander

Posted: ‎2016-01-15 09:56 AM

0 Likes
5
2349
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2016-01-15 09:56 AM

Hello KK,

There are varying factors to consider; however here is what we support:

The Com'X 510 can support 32 devices at 30 topics each at 5 minute intervals for 2 years of stored historical data. 

The calculation above can be adapted...adding more devices, and less topics plus longer intervals or some variation.

We do not make any differences on the size of the SD Card. 

Adding Robert Jennings (Clay) here in case you need further information.

James

Reply
KuanKhoon
Lt. Commander KuanKhoon Lt. Commander
Lt. Commander

Posted: ‎2016-01-24 08:33 PM

0 Likes
3
2348
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2016-01-24 08:33 PM

Hi James,

Thanks for the insights. Was pretty tied up the previous 1.5 weeks hence omitted to reply you until now.

Thus, it would look like the Com'X 510 has a flexible "table assignment" that allows it to scale up or down the logging duration with respect to the number of topic logged, the number of devices logging and frequency of the individual logging.

If I were to do the following maths, (32 devices) x (30 topics) x (12 entries per hour) = 2 years

We derive a total of (32devices x 30topics/device x 12entries/hour x 24hour/day x 365day/year x 2years) = 201,830,400 entries (wow! 200 million entries ++)

Using the above base number, we should be able to freely determine the total logging time according to number of devices, topics, logging entries per hour, etc. Is this calculation reasonable?

Best Regards,

Kuan Khoon

Reply
JamesJeanette
Commander JamesJeanette Commander
Commander

Posted: ‎2016-01-26 10:33 AM

0 Likes
2
2348
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2016-01-26 10:33 AM

Hello KK,

I have confirmed with the team.

"The math is correct.  We store 10 bytes per measurement sample; any memory used for managing the data is negligible.  So 201,830,400 measurements * 10 bytes is only  2GByte of our 4 Gbyte SD card capacity."

James

Robert Jennings

Reply
KuanKhoon
Lt. Commander KuanKhoon Lt. Commander
Lt. Commander

Posted: ‎2016-01-26 06:43 PM

1 Like
0
2348
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2016-01-26 06:43 PM

Hi James,

Good to know the maths is correct. Hence, we are using 2GB out of the 4GB memory on the SD card and the automatic wear leveling algorithm on the SD card controller will do the magic to ensure longevity of the card.

On the side note, typical SD card memory cells have a longevity of 10000 write cycles, and we are writing in such a leisurely pace, I would expect the SD card to pretty much last "forever".

Best Regards,

Kuan Khoon

Reply
Erwin_Paal
Lieutenant JG Erwin_Paal Lieutenant JG
Lieutenant JG

Posted: ‎2016-02-02 08:00 AM

0 Likes
0
2348
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2016-02-02 08:00 AM

Hallo James,

I'm a little confused about the management of storage.

We are aware that Com'X 510 can manage max 64 physical devices (like EGX300). Is there no longer this limitation?

In the manual, I haven't found any limitation about maximal possible managed devices.

How are the 'virtual meters' considered? I meen devices defined in the custom library, based on I/O from physical devices.

How is the process for storage management in Com'X 510?

We thought it is similar to the EGX. Memory is divided into 64 parts.

Then each part is divided according to number of topics into 'n topics' parts.

Each topic part is managed dynamic according to the number of logging entries (depending of log interval):

I've found that when changing the logging parameters (whether topics number or interval), we have no data loss in ComX.


The primary question for me is about a description of storage management in Com'X.

Then maybe we can better understand, the impact of changes the logging parameters.

When is the risk that customers lose their data?

I can't confirm what Kuan Khoon TAN had write in this post: Com'X510 Loss Of Logging Data When Reconfiguring Logging Parameters

The problem with the publication is:

     - the first timestamp is always the last timestamp sent + 1 * Interval time.

     - in periodcal publication first timestamp is depending on the timezone set in Com'x (for UTC +1 it's 1:00, for UTC+4 it's 4:00)

       That is not what the customer expects, he wants to have his local time 00:00.

     - the last timestamp is depending of the selected publication frequency or the time when manual publication was selcted.

That means we have only one incremental export of data.

However if manual publication was chosen then missing data in the periodic publication.

It's very important for next FW to have the ability to export data for selected devices, periods, start time.


Best Regards


Erwin Paal

Reply
DavidVicente
Lieutenant DavidVicente Lieutenant
Lieutenant

Posted: ‎2018-07-23 03:35 AM

0 Likes
0
2348
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2018-07-23 03:35 AM

Hi James,

Does the same limit apply to ComX210, or do we have to consider that it can go up to more data based on his thinner firmware?

Thanks

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore