Com'X510 Firmware 1.1.44 Custom Device Library Modbus Read Function Error

Gateways and Energy Servers

Schneider Electric support forum to share knowledge about product selection, installation and troubleshooting for EcoStruxure Panel Server, PowerTag, Com'X, Link150…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Gateways and Energy Servers
  • Com'X510 Firmware 1.1.44 Custom Device Library Modbus Read Function Error
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Romain_Polette
Kirk Romain_Polette Kirk
117
Guillaume_Evrard
Captain Guillaume_Evrard Captain
59
Randi_Dolan
Commander Randi_Dolan Commander
46
View All

Recommended Forums

  • Metering & Power Quality

  • SmartConnector Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Gateways and Energy Servers
Start a Topic
Solved
KuanKhoon
Lt. Commander KuanKhoon Lt. Commander
Lt. Commander

Posted: ‎2015-08-12 06:19 AM

0 Likes
15
3427
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2015-08-12 06:19 AM

Com'X510 Firmware 1.1.44 Custom Device Library Modbus Read Function Error

Hi Team,

Having done another round of testing with the Com'X 510 on Firmware 1.1.44 and I found something pretty interesting,

The custom device library tab, selecting FC04 : Read Input Registers for the Veris CWLP sensor,

7204

The Com'X510 actually calling FC03 : Reading Holding Registers,

7206

as you can see below from the Modscan32 screen capture,

7207

if FC04, read input register is correctly executed, the following should have been displayed,

7208

30001 is the CO2 level in PPM

30002 is the relative humidity in tenth of a %

30003 is the temperature in tenth of a Celcius or Fahrenheit


40001 is the CO2 level which will trigger the on-board relay on the CWLP sensor

40002 is the CO2 level deadband

40003 is the automatic calibration setting (0 = normal, 1= low, 2 = off)


Hence, from this perspective, the FC03 is implemented incorrectly and somehow it is resulting in the Com'X510 reading holding registers instead of the input registers called for.

Tags (4)
  • Tags:
  • comx510
  • fc03
  • fc04
  • modbus
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2015-08-25 11:12 PM

0 Likes
0
3246
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2015-08-25 11:12 PM

Hi,

I 'll send you the answer by email. As this issue should be handled through technical support team

global-ems-solutions-support@schneider-electric.com , global-ems-tech-support@schneider-electric.com 

See Answer In Context

Reply
Replies 15
JamesJeanette
Commander JamesJeanette Commander
Commander

Posted: ‎2015-08-12 07:23 AM

0 Likes
0
3246
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2015-08-12 07:23 AM

Thanks for this feedback KK.

Adding the engineering team here to review.

Team..please take a look.

Reply
Michael_Khela
Ensign Michael_Khela Ensign
Ensign

Posted: ‎2015-08-24 05:54 AM

0 Likes
0
3246
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2015-08-24 05:54 AM

Hi Kuan,

Sorry for the late replay. This issue appears to happen when a device have shared register numbers between (FC03 & FC04)

This is an issue with the Com'X510 v1.1.44. The development team is currently working on resolving this. I will keep you updated on the status of this issue.

Reply
Anonymous user
Not applicable

Posted: ‎2015-08-25 11:12 PM

0 Likes
0
3247
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2015-08-25 11:12 PM

Hi,

I 'll send you the answer by email. As this issue should be handled through technical support team

global-ems-solutions-support@schneider-electric.com , global-ems-tech-support@schneider-electric.com 

Reply
JamesJeanette
Commander JamesJeanette Commander
Commander

Posted: ‎2015-09-29 02:17 PM . Last Modified: ‎2022-10-18 10:46 PM

0 Likes
11
3246
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2015-09-29 02:17 PM

Hello everyone.

We have released Com'X 510 Firmware Version 1.1.45

Bug Fixes:

* [artf147374] : Custom Models - The custom device types units selection is not honored

* [artf147373] : Custom Models - The use of a fractional "Factor" is not properly supported in the Com'X 510 for all register formats

* [artf148188] : Custom Models - Function code x03 is used when x04 is specified

* [artf147384] : Custom Models - Overlapping frames causes topics to go offline

* [artf148273] : artf148273 : Energy Dashboards - Date Picker in Dashboards Does Not Honor The Date Time Format

On The Exchange Community:

https://community.se.com/docs/DOC-13405

On Shopping Kiosk:

http://shoppingkiosk.schneider-electric.com/doc_info.aspx?DocRef=ComX510v1-1-45_Firmware_EBX510&isdv...

I have also applied the update to our Com'X 510 demo in case you do not have time to upgrade yours.

Link: http://comx510.myenergyserver.com

Username: demo

Password: Com’X510

James

Robert Jennings

jef Maubert

Reply
Philippe_Morel
Commander Philippe_Morel Commander
Commander

Posted: ‎2015-10-05 01:36 AM

0 Likes
10
3246
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2015-10-05 01:36 AM

Hi James,

I still encounter a problem with Firmware Version 1.1.45. (also with previous version 1.1.44.)

5.jpg

I want to read a bit in a holding register of a Sepam device.

But I can't create a new device if the Custom Library Model uses 'Boolean'.

I get the message 'The product has not been created'. Still there is no problem with creating the Model itself.

1.bmp

The name of the Model that uses Boolean is SepamBit.

2.bmp

The other Model TestSepam3 does not uses Boolean and with this Model I can create a new device and I'm able to communicate with the Sepam.

On the next four screenshots you'll see the details of the two Models.

Model SEPAMBIT:

3.jpg

3b.bmp

Model TESTSEPAM3:

4.jpg

4b.jpg

Can you look at this?

Thank you!

Philippe

Reply
KuanKhoon
Lt. Commander KuanKhoon Lt. Commander
Lt. Commander

Posted: ‎2015-10-05 02:17 AM

1 Like
6
3246
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2015-10-05 02:17 AM

Hi Philippe,

Can you check that you are using Google Chrome for programming the Com'X? There seems to still be some problems for IE and Firefox doing programming on the Com'X and it will give you the "The product has not been created" problem.

From my end, I verify that the Veris CWLP and HWLP wall mounted sensors can be read properly without issues with the reading extracted from the Input Registers.

Best Regards,

Kuan Khoon

Reply
JamesJeanette
Commander JamesJeanette Commander
Commander

Posted: ‎2015-10-05 06:16 AM

0 Likes
5
3246
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2015-10-05 06:16 AM

Thanks KK.

Philippe...can you confirm this works for you using Google Chrome browser?  As KK mentions, we are aware of some issues using IE and Firefox which our on our roadmap to enhance.

James

Robert Jennings

Reply
Philippe_Morel
Commander Philippe_Morel Commander
Commander

Posted: ‎2015-10-07 12:03 AM

0 Likes
0
3246
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2015-10-07 12:03 AM

I'll try it this friday. If I remember correctly then I think that I already tried it with IE and Firefox.

Reply
Philippe_Morel
Commander Philippe_Morel Commander
Commander

Posted: ‎2015-10-09 05:50 AM

0 Likes
3
3246
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2015-10-09 05:50 AM

James Jeanette  Kuan Khoon TAN

Still the same problem with Firefox and Chrome.

Reply
JamesJeanette
Commander JamesJeanette Commander
Commander

Posted: ‎2015-10-09 03:28 PM

0 Likes
2
3246
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2015-10-09 03:28 PM

Thanks Philippe.

Clay...can you reproduce this issue?

Robert Jennings

Audie Sheridan

Reply
Philippe_Morel
Commander Philippe_Morel Commander
Commander

Posted: ‎2015-10-14 01:20 AM

0 Likes
1
3246
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2015-10-14 01:20 AM

Hi James Jeanette,

Do you have some feedback for me?

I need to integrate this solution at a client in the comming days.

Thanks!

Philippe

Reply
JamesJeanette
Commander JamesJeanette Commander
Commander

Posted: ‎2015-10-14 07:53 AM

0 Likes
0
3246
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2015-10-14 07:53 AM

Hello Philippe,

I have copied you on an email.  We should have a response soon.

Robert Jennings

Audie Sheridan

James

Reply
sesa12529_bridg
Ensign sesa12529_bridg Ensign
Ensign

Posted: ‎2015-10-14 08:27 AM

0 Likes
2
3246
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2015-10-14 08:27 AM

Hi Philippe,

Boolean support for custom models is currently broken in the Com'X 510 release.  There is no work-around at this time.  Effort is being made to have this corrected in v2.1 which is expected to release in November.

Reply
Philippe_Morel
Commander Philippe_Morel Commander
Commander

Posted: ‎2015-10-14 11:54 PM

0 Likes
1
3246
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2015-10-14 11:54 PM

Hi Robert Jennings,

OK Thanks!

I did send an email to the client to say that he must have some patience.

Can you confirm that I'll be able to read certain bits from a Sepam Series 40?

So that I understand the boolean function correctly.

Can I for example read bit 0 from the holding register with the address 010B to know the status of input I11?

sepam.jpg

Reply
Philippe_Morel
Commander Philippe_Morel Commander
Commander

Posted: ‎2015-11-05 07:38 AM

0 Likes
0
3246
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2015-11-05 07:38 AM

Hi Robert Jennings

Is the expected release still in November?

Mid or more end November?

Regards,

Philippe

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore