As you probably already know, the Com'X200 comes with 3 ways to get powered:
What you might less be aware of is that you can use multiple ways to power your box to provide redundancy.
For example you can use Option 1 (VAC) and have a small 24V UPS on Option 2. Which means that if Option 1 goes down, it will automatically switch to Option 2.
Order of redundancy is as described: first the box will use the VAC, if not available, it goes to VDC. Finally if not available it goes to PoE.
Finally not that only one of the ethernet port is PoE enabled and there's a small marking on the box to remind you which one (the left one!).
Link copied. Please paste this link to share this article on your social media post.
Would there be any issues if the customer were to power up ComX200 with 240VAC and 24VDC at the same time, where 24VDC is a back up supply.
or POE with 240VAC/24VDC as a back up supply simulateously.
Would there be any priority issue?
Link copied. Please paste this link to share this article on your social media post.
No issue at all! That's the all point. ![]()
The priority goes as followed: VAC, then VDC, then PoE.
So again, typically I would plug the VAC and then have a small DIN-Railed 24VDC UPS for backup!
Link copied. Please paste this link to share this article on your social media post.
Posted: 2014-04-29 10:56 PM
Link copied. Please paste this link to share this article on your social media post.
Do we have SE PoE supply offer?
thanks
Link copied. Please paste this link to share this article on your social media post.
Not aware of any, but doesn't mean we don't have one...
Link copied. Please paste this link to share this article on your social media post.
Is the PoE Injector Kit, TCSEAV0100, what you are looking for?
Here is a link to the installation guide (63230-319-206): http://download.schneider-electric.com/files?L=en&p=&p_docId=&p_docId=&p_Reference=63230-319-206&p_E... guide&p_File_Id=27448644&p_File_Name=63230-319-206.pdf
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
This is soooo good! As per this old thread we really really needed this (especially now that it has the latest Ethernet Gateway functionality!) and this fixes a lot of problems we were having creating redundancy (unable with EGX)
Any chance this could also be an ION Protocol Gateway in a future firmware? (basically - a straight serial port encapsulation with no protocol conversion) - - we are buying Lantronix now for this. Why not offer it as a setting for our new device here?
Link copied. Please paste this link to share this article on your social media post.
ION protocol is on the roadmap. You will see it on the new gateway offers first. Later it will make its way on to the Energy Servers.
Posted: 2014-07-07 08:18 AM
Link copied. Please paste this link to share this article on your social media post.
Is the Com'X 200 (210/510) powered by POE able to power all the Outputs, wireless, and future expansion modules without limitations? Do we know the limitations if any? Any increase thermal issues?
Link copied. Please paste this link to share this article on your social media post.
Hi Jonathan,
there's at least one limitation specified (on the technical Leaflet that comes with the datalogger) which is that the GPRS dongle can't work with PoE.
On top of that, the PoE standard (802.3af) on COM'X200 grant at most around 13W, while the COMX max consumption is 26W. So it's possible that there are more limitations.
Hope it helps
Posted: 2014-07-07 09:03 AM
Link copied. Please paste this link to share this article on your social media post.
Thanks for the quick answer. Is this a short term situation (with GPRS) that will be fixed with a FW or HW (210 / 510) update?