Hello
If you have a Com´X with old firmware e.g comx510_1.1.44 (or erlier) and want to upgrade to the latest released version. Is it mandatory then to first upgrade to versions that has been released i between ?, if the latest firmware is used does all futures that was in the versions in between then included in the upgrade ?
Best Regards
Anders
Link copied. Please paste this link to share this article on your social media post.
Hello Anders.
No, you do not have to upgrade each version to get to the latest...you can go straight from 1.1.44 to 3.0.6.
Important Note:
Before you upgrade to 3.0.6, first ensure that you have updated the Date/Time settings in your Com'X 510.
For more information...
Please follow the newly released Quick Start Guide for the optimal experience
Com'X 510 Quick Start: https://community.se.com/servlet/JiveServlet/download/14218-1-39170/ComX%20510%20Commissioning%2…
James
Link copied. Please paste this link to share this article on your social media post.
Hello Anders.
No, you do not have to upgrade each version to get to the latest...you can go straight from 1.1.44 to 3.0.6.
Important Note:
Before you upgrade to 3.0.6, first ensure that you have updated the Date/Time settings in your Com'X 510.
For more information...
Please follow the newly released Quick Start Guide for the optimal experience
Com'X 510 Quick Start: https://community.se.com/servlet/JiveServlet/download/14218-1-39170/ComX%20510%20Commissioning%2…
James
Link copied. Please paste this link to share this article on your social media post.
Hello
Does this apply even if the firmware is older than 1.1.44 ?, is this principle the same on other Gateways e.g Com´X200/201, Link150
Link copied. Please paste this link to share this article on your social media post.
Please find the below link for the firmware upgrade for Link150.
Firmware Link 150 Version 5.0.23
Regards,
Kamal Kumar