Com'X 510 NS800N

Gateways and Energy Servers

Schneider Electric support forum to share knowledge about product selection, installation and troubleshooting for EcoStruxure Panel Server, PowerTag, Com'X, Link150…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Gateways and Energy Servers
  • Com'X 510 NS800N
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Romain_Polette
Kirk Romain_Polette Kirk
116
Guillaume_Evrard
Captain Guillaume_Evrard Captain
58
Randi_Dolan
Commander Randi_Dolan Commander
46
View All

Recommended Forums

  • Metering & Power Quality

  • SmartConnector Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Gateways and Energy Servers
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2019-08-07 05:42 AM

0 Likes
4
2069
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2019-08-07 05:42 AM

Com'X 510 NS800N

Hi

 

I am having some issues trying to read values from a NS800N breaker with Micrologix 5.0 E.

The breaker is connected to a Com'X 510, I am unable to find the NS800 breaker as a type in the Com'X.

 

I am however able to read some values in the Com'X by choosing e.g. Compact NSX E as the type, but I guess that is a coincident, that some registers are the same. When I add the breaker in management console, I choose Micrologix 2.0/5.0/6.0E, but when I try to add the link in Vista it displays "No managers".

 

So my first question is: How to add a NS800N with Micrologix 5.0 to a Com'X 510? The next step would be to implement it in PME. I have also asked this question in the PME community

 

Br Vegard

Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Randi_Dolan
Commander Randi_Dolan Commander
Commander

Posted: ‎2019-08-07 05:46 AM

0 Likes
3
2066
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2019-08-07 05:46 AM

Hello,

 

The Compact NS is in the same family as the Masterpact NT/NW.  So, you will want to select the Masterpact E as the device.  There are three selections for the Masterpact E based on the communication module.  If you are using the legacy BCM, you will select Masterpact E.  If you are using an IFM, you will select Masterpact E IFM.  If you are using an IFE, you will select the Masterpact E IFE.

 

Regards,

Randi

See Answer In Context

Reply
Replies 4
Randi_Dolan
Commander Randi_Dolan Commander
Commander

Posted: ‎2019-08-07 05:46 AM

0 Likes
3
2067
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2019-08-07 05:46 AM

Hello,

 

The Compact NS is in the same family as the Masterpact NT/NW.  So, you will want to select the Masterpact E as the device.  There are three selections for the Masterpact E based on the communication module.  If you are using the legacy BCM, you will select Masterpact E.  If you are using an IFM, you will select Masterpact E IFM.  If you are using an IFE, you will select the Masterpact E IFE.

 

Regards,

Randi

Reply
Anonymous user
Not applicable

Posted: ‎2019-08-07 05:58 AM

0 Likes
2
2064
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2019-08-07 05:58 AM

Thank you for the swift reply! I have not been to the site, so I am not really sure about the communication module. I have attached some pictures that the customer has sent me, maybe it is possible to see what the module is, based on the pictures? Both IFM and IFE types seem to work. The BCM did not work.

 

Br Vegard

Attachments
Reply
Randi_Dolan
Commander Randi_Dolan Commander
Commander

Posted: ‎2019-08-07 06:29 AM

0 Likes
1
2059
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2019-08-07 06:29 AM

I can't see the Comms module from the pictures.  However, you should be able to tell based on the device ID.  If it's 255, it's an IFE, if not, it's an IFM.

Reply
Anonymous user
Not applicable

Posted: ‎2019-08-07 06:34 AM

0 Likes
0
2057
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2019-08-07 06:34 AM

Ok, the ID is 8. So then it's an IFM. Thanks!

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore