Com'X 510 - Native Driver Editing/Communication Issue

Gateways and Energy Servers

Schneider Electric support forum to share knowledge about product selection, installation and troubleshooting for EcoStruxure Panel Server, PowerTag, Com'X, Link150…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Gateways and Energy Servers
  • Com'X 510 - Native Driver Editing/Communication Issue
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Romain_Polette
Spock Romain_Polette Spock
99
Randi_Dolan
Commander Randi_Dolan Commander
46
Guillaume_Evrard
Commander Guillaume_Evrard Commander
44
Thierry_Baudard
Commander Thierry_Baudard Commander
30
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Gateways and Energy Servers
engenharia_memt
Lieutenant | EcoXpert Master engenharia_memt Lieutenant | EcoXpert Master
Lieutenant | EcoXpert Master

Posted: ‎2019-07-29 06:18 AM

0 Likes
3
743
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2019-07-29 06:18 AM

Com'X 510 - Native Driver Editing/Communication Issue

Hello, 

 

I have two questions about Com'x 510 energy server: 

 

1 - Is it possible to edit a native driver for a downstream device in Com'x 510? I mean,  without creating a custom device, I would like to apply a scale in the energy modbus register (currently read in Wh for BCPM circuit channels, I wish it to be read in kWh) in the original device driver and keep it working properly after this change.  

 

2 - Is there any known issue related to the way that Com'x manages the packets which it reads from downstream devices (through modbus/TCP or modbus/RTU)? I can explain it by telling you two specific cases that I noticed in two different customers.

 

i - The first customer has some third party devices (ABB REF 615) that are being read by Com'x 210 via modbus/TCP in one ethernet port. In this case, the data logging is activated in Com'x because we intend to give more reliability to the collected data once the connected devices are physically close to the Com'x. The CSV files are exported to the server and later PME get them to its database via ETL. The customer requested us to available real time readings in PME because of operational reasons. But, when we do this, Com'x starts to work strangely and lose rows of data in the CSV files (the values come as null). 

 

ii - The second customer has Com'x 510 and BCPM A as downstream devices connected in RS485 port. The same way that reported above, the data logging is configured in the Com'x and also there are real time requests coming from PME. However, many times the .CSV files come with missing data.

 

I would be very greatful if anybody could give me some insights on where could be the problem in these cases or wheather there is a workaround for those. 


Thanks in advance! 

Reply
  • All forum topics
  • Previous Topic
  • Next Topic
Replies 3
Randi_Dolan
Commander Randi_Dolan Commander
Commander

Posted: ‎2019-07-29 07:40 AM

0 Likes
2
741
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2019-07-29 07:40 AM

Hello,

 

To answer your first question, no, you cannot modify the built in driver for a device without creating a custom model.  The Com'X manages all data in base SI units.  This is why the Energy readings are in Wh and not kWh.

 

In response to your second question, it was recently brought to our attention that if a data value is reported as "NaN" or as an invalid value from the device, this will invalidate the entire entry, as indicated with error code 19.  This issue will be resolved with the next firmware release.  If you are experiencing a different issue, you should contact the Customer Care Center with assistance in troubleshooting the issue you are seeing.

 

Regards,

Randi

Reply
engenharia_memt
Lieutenant | EcoXpert Master engenharia_memt Lieutenant | EcoXpert Master
Lieutenant | EcoXpert Master

Posted: ‎2019-08-06 11:20 AM

0 Likes
1
732
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2019-08-06 11:20 AM

Hello, 

Thank you for your reply! 

What would be your suggestion to have all the meters in the same base unit? I know that there aren't too many options, but using ETL to divide the energy readings by 1000 before loading them into DB would be a good path way? 

 

About the second problem, we are performing some more tests in order to verify if our case matches the error and characteristics that you mentioned. 

We keep you informed in this post. 

Thanks!

Reply
Randi_Dolan
Commander Randi_Dolan Commander
Commander

Posted: ‎2019-08-06 11:34 AM

0 Likes
0
730
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2019-08-06 11:34 AM

Hi,

 

If you are using the Com'x built-in device models, they should all be in the same units.  However, if you are using a custom model, you will have to change the scaling in the custom model.

 

Please let me know if you need further assistance.

 

Randi

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of