Can't add A9XMC1D3 (Power Tag C IO) to PAS800,600 or 400

Gateways and Energy Servers

Schneider Electric support forum to share knowledge about product selection, installation and troubleshooting for EcoStruxure Panel Server, PowerTag, Com'X, Link150…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Gateways and Energy Servers
  • Can't add A9XMC1D3 (Power Tag C IO) to PAS800,600 or 400
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Romain_Polette
Kirk Romain_Polette Kirk
116
Guillaume_Evrard
Captain Guillaume_Evrard Captain
58
Randi_Dolan
Commander Randi_Dolan Commander
46
Thierry_Baudard
Commander Thierry_Baudard Commander
32
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Gateways and Energy Servers
Start a Topic
Solved
RWG924
Ensign RWG924 Ensign
Ensign

Posted: ‎2025-01-01 11:08 PM

0 Likes
3
673
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-01-01 11:08 PM

Can't add A9XMC1D3 (Power Tag C IO) to PAS800,600 or 400

When I try to pair the A9XMC1D3 to PAS600, it does work for 10 seconds and disconnect and removes by itself.

Can anyone shed me some lights please?  

Labels
  • Labels:
  • Legacy Gateways & Energy Servers
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Eric_HAVAS
Lt. Commander Eric_HAVAS Lt. Commander
Lt. Commander

Posted: ‎2025-01-01 11:56 PM . Last Modified: ‎2025-01-02 01:56 AM

0 Likes
1
665
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-01-01 11:56 PM

Hello @RWG924 
Powertag Control with firmware >= v2 are supported by panel server family and not PowerTag Control with firmware v1. (Firmware version of PwT C are displayed in Panel Server webpages or EcoStruxure Power Commission Desktop application)

you can also identified Pwt C v2 visually as they have a QR code on their side and not a Data Matrix.
Please refer to enclosed pdf for photos.

Take the opportunity to check also that you're panel server has the latest firmware.

Regards
 

See Answer In Context

Attachments
Reply
Replies 3
Eric_HAVAS
Lt. Commander Eric_HAVAS Lt. Commander
Lt. Commander

Posted: ‎2025-01-01 11:56 PM . Last Modified: ‎2025-01-02 01:56 AM

0 Likes
1
666
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-01-01 11:56 PM

Hello @RWG924 
Powertag Control with firmware >= v2 are supported by panel server family and not PowerTag Control with firmware v1. (Firmware version of PwT C are displayed in Panel Server webpages or EcoStruxure Power Commission Desktop application)

you can also identified Pwt C v2 visually as they have a QR code on their side and not a Data Matrix.
Please refer to enclosed pdf for photos.

Take the opportunity to check also that you're panel server has the latest firmware.

Regards
 

Attachments
Reply
RWG924
Ensign RWG924 Ensign
Ensign

Posted: ‎2025-01-02 12:45 AM

0 Likes
0
640
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-01-02 12:45 AM

Thx Eric. Is there any chance to upgrade PowerTag Control with firmware v1 to V2?

Reply
Eric_HAVAS
Lt. Commander Eric_HAVAS Lt. Commander
Lt. Commander

Posted: ‎2025-01-02 01:21 AM

0 Likes
0
632
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-01-02 01:21 AM

Unfortunately @RWG924 , up to now, there is no possibility to upgrade PowerTag Control firmware.

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore