When I try to pair the A9XMC1D3 to PAS600, it does work for 10 seconds and disconnect and removes by itself.
Can anyone shed me some lights please?
- Labels:
-
Legacy Gateways & Energy Servers
Accepted Solutions
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Hello @RWG924
Powertag Control with firmware >= v2 are supported by panel server family and not PowerTag Control with firmware v1. (Firmware version of PwT C are displayed in Panel Server webpages or EcoStruxure Power Commission Desktop application)
you can also identified Pwt C v2 visually as they have a QR code on their side and not a Data Matrix.
Please refer to enclosed pdf for photos.
Take the opportunity to check also that you're panel server has the latest firmware.
Regards
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Hello @RWG924
Powertag Control with firmware >= v2 are supported by panel server family and not PowerTag Control with firmware v1. (Firmware version of PwT C are displayed in Panel Server webpages or EcoStruxure Power Commission Desktop application)
you can also identified Pwt C v2 visually as they have a QR code on their side and not a Data Matrix.
Please refer to enclosed pdf for photos.
Take the opportunity to check also that you're panel server has the latest firmware.
Regards
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Thx Eric. Is there any chance to upgrade PowerTag Control with firmware v1 to V2?
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Unfortunately @RWG924 , up to now, there is no possibility to upgrade PowerTag Control firmware.