Ask our Experts
Didn't find what you are looking for? Ask our experts!
Launch of Consumer/Home Owner registration process! We are pleased to announce the commencement of the Consumer/Home Owner Registration Process on Community. Consumers/Home Owners may now proceed to register by clicking on Login/Register. The process is straightforward and designed to be completed in just a few steps.
Schneider Electric support forum to share knowledge about product selection, installation and troubleshooting for EcoStruxure Panel Server, PowerTag, Com'X, Link150…
Search in
User | Count |
---|---|
108 | |
52 | |
46 | |
32 |
Link copied. Please paste this link to share this article on your social media post.
Dear Experts,
I have a question, ZBRCETH module has 2 Modbus TCP/IP ports with daisy chain topology but I need to confirm if I can comunicate the ZBRN1 with a HMI and a PC simultaneously.
Thanks for your assistance.
Regards.
Link copied. Please paste this link to share this article on your social media post.
ZBRN1+ ZBRCETH being a slave modbus tcp device it can answer to multiple masters. Not sure what you refer to with HMI, but ZBRN1 is not supported by SMD MV no SMD LV.
Link copied. Please paste this link to share this article on your social media post.
ZBRN1+ ZBRCETH being a slave modbus tcp device it can answer to multiple masters. Not sure what you refer to with HMI, but ZBRN1 is not supported by SMD MV no SMD LV.
Link copied. Please paste this link to share this article on your social media post.
Hi Expert, does ZBRn32 supported by SMD MV and SMD LV?
Link copied. Please paste this link to share this article on your social media post.
Hello @Gig_DSA ,
Answer is yes for SMD MV. But Panel Server can also replace the ZBRN32 for SMD MV.
No for SMD LV (you must use Panel Server or PowerTag Link regarding your application).
Please refer to the ESXP IEC Design Guide (section Thermal Monitoring) for more info.
https://www.se.com/in/en/download/document/ESXP_DigitalApplications_guide/
Regards,
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
For SMD MV only ZBRN32 is supported
For SMD LV PTL or PAS(depending on location) can be used
You’ve reached the end of your document
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.