Dear Experts,
I have a question, ZBRCETH module has 2 Modbus TCP/IP ports with daisy chain topology but I need to confirm if I can comunicate the ZBRN1 with a HMI and a PC simultaneously.
Thanks for your assistance.
Regards.
- Labels:
-
Product selection
Accepted Solutions
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
ZBRN1+ ZBRCETH being a slave modbus tcp device it can answer to multiple masters. Not sure what you refer to with HMI, but ZBRN1 is not supported by SMD MV no SMD LV.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
ZBRN1+ ZBRCETH being a slave modbus tcp device it can answer to multiple masters. Not sure what you refer to with HMI, but ZBRN1 is not supported by SMD MV no SMD LV.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Hi Expert, does ZBRn32 supported by SMD MV and SMD LV?
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Hello @Gig_DSA ,
Answer is yes for SMD MV. But Panel Server can also replace the ZBRN32 for SMD MV.
No for SMD LV (you must use Panel Server or PowerTag Link regarding your application).
Please refer to the ESXP IEC Design Guide (section Thermal Monitoring) for more info.
https://www.se.com/in/en/download/document/ESXP_DigitalApplications_guide/
Regards,
Solution Architect - France Operations
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
For SMD MV only ZBRN32 is supported
For SMD LV PTL or PAS(depending on location) can be used