Panel Server / Power Operation

Gateways and Energy Servers

Schneider Electric support forum to share knowledge about product selection, installation and troubleshooting for EcoStruxure Panel Server, PowerTag, Com'X, Link150…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Gateways and Energy Servers
  • Panel Server / Power Operation
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Romain_Polette
Spock Romain_Polette Spock
96
Randi_Dolan
Commander Randi_Dolan Commander
46
Guillaume_Evrard
Commander Guillaume_Evrard Commander
41
Thierry_Baudard
Commander Thierry_Baudard Commander
30
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Gateways and Energy Servers
milica_dukic_
Ensign milica_dukic_
Ensign

Posted: ‎2023-06-28 05:35 AM . Last Modified: ‎2023-06-28 05:36 AM

0 Likes
8
1512
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-06-28 05:35 AM

Panel Server / Power Operation

Dear all,

 

 

is there a Device Type / Device Profile in Power Operation for Panel Server, or LINK150?

 

If not, what is the simpliest way for this intergration?

 

Thanks in advance.

 

Best regards

Labels
  • Labels:
  • Commissioning
  • Legacy Gateways & Energy Servers
Reply
  • All forum topics
  • Previous Topic
  • Next Topic
Replies 8
RobGraham
Commander RobGraham Commander
Commander

Posted: ‎2023-06-28 02:01 PM

0 Likes
1
1494
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-06-28 02:01 PM

I haven't played with the Panel Server yet, but the Link150 is just a gateway.  The device profile needs to be built for the downstream serial device.  When you add the device using the I/O Device Manager, add it as "Modbus/RTU via Gateway" (assuming Modbus protocol) using the Link150's IP address as the gateway and the device's Modbus address for the device address.

Reply
milica_dukic_
Ensign milica_dukic_
Ensign

Posted: ‎2023-06-28 11:18 PM . Last Modified: ‎2023-06-28 11:18 PM

0 Likes
0
1489
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-06-28 11:18 PM

Downstream serial devices are ZBRN2.

Is there device profile for it?

Reply
RobGraham
Commander RobGraham Commander
Commander

Posted: ‎2023-06-29 05:04 AM

1 Like
1
1464
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-06-29 05:04 AM

That makes things more difficult because the ZBRN's Modbus register list depends upon the Zigbee devices connected to it, as I understand.  I've never had to deal with one of these in the field.

 

I don't see any existing device types that use the ZBRN (aside from the SMD, which requires a separate PLC).  If you expect to have a large number of downstream devices, I would recommend building a device type in Profile Editor using functional addressing so the type only needs to be built once, then can be added into the project with the correct offsets.

 

Unfortunately, I don't know if anyone has done this before for the Zigbee devices connected to a ZBRN2.

Reply
Guillaume_Evrard
Commander Guillaume_Evrard Commander
Commander

Posted: ‎2023-06-29 09:52 PM

1 Like
0
1448
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-06-29 09:52 PM

Hello,

 

With ZBRN you have 2 modes of operation :

- each sensor is accessible as a modbus device (one modbus id) and depending on the type of sensor you are always having the same register table. You are able to select the starting modbus Id based on table selection.

- each sensor is accessible at register address increment at always the same modbus ID. For TH/CL address increment is +33.

Not sure if it helps.

Reply
Romain_Polette
Spock Romain_Polette Spock
Spock

Posted: ‎2023-06-29 11:54 PM . Last Modified: ‎2023-06-29 11:55 PM

0 Likes
0
1443
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-06-29 11:54 PM

Hello @milica_dukic_ , 


If you are using a PAS600L or PAS800L, you have 2x DI integrated in the device: In this case you may need to create a new Profil using MODNET or PWRMODBUS drivers to access DI cumulated values (WAGES or Breaker Status).

Internal Panel Server registers are provided with the PAS Modbus file.

 

Link150 have no exploitable Modbus registers.

 

If your architecture is Panel Server + ZBRN2 + CL110 / TH110, check following posts:

  • https://community.se.com/t5/Gateways-and-Energy-Servers/How-to-get-Modbus-register-of-the-Wireless-T...
  • https://community.se.com/t5/Gateways-and-Energy-Servers/Connect-Zigbee-to-LINK150/m-p/373011

Regards,

 

Regards, 

Romain POLETTE
Solution Architect - France Operations
Reply
milica_dukic_
Ensign milica_dukic_
Ensign

Posted: ‎2023-06-30 12:18 AM

1 Like
0
1441
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-06-30 12:18 AM

Hi everyone,

 

First of all, thanks for answering so quickly.

My architecture is shown below.

 

milica_dukic__0-1688109360299.png

I would say thats the same thing @Romain_Polette said?

Please correct me if i am wrong.

 

Best regards,
Milica

 

Reply
Romain_Polette
Spock Romain_Polette Spock
Spock

Posted: ‎2023-06-30 02:53 AM

0 Likes
1
1427
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-06-30 02:53 AM

Hello @milica_dukic_ , 


please check:

  • This post: https://community.se.com/t5/Gateways-and-Energy-Servers/How-to-get-Modbus-register-of-the-Wireless-T...
  • the Modbus section of the ZBRN2 guide (focus on p. 107).

Romain_Polette_1-1688118655351.png

 

You will learn how to implement ZBRN2 registers into your Device Profile 

 

For example if you want to read Temp + Hum of CL110 number 0 and 1 paired with the ZBRN2 you need to read:

  • register address 16 => sensor 0 temp
  • register address 17 => sensor 0 relative hum.
  • register address 49 (=16+33) => sensor 1 temp
  • register address 50 (=17+33) => sensor 1 relative hum.
  • register address 82 (=49+33) => sensor 2 temp
  • register address 83 (=50+33) => sensor 2 relative hum.
  • etc.

Regards, 

 

Romain POLETTE
Solution Architect - France Operations
Reply
Guillaume_Evrard
Commander Guillaume_Evrard Commander
Commander

Posted: ‎2023-07-02 10:28 PM

1 Like
0
1358
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-07-02 10:28 PM

If you are using ZBRN32, you might have to handle the timeout information, less required for CL110 as battery power. Just keep in ming that ZBRN32 will provide the last measurement received (if one was received) or 0 if no measurement yet received. Timeout = 1 means that the value is not refreshed.

 

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of