Bringing in data with Automation Server into Com'X510
Hello everyone,
I'd like to bring in data with Automation Server into Com'X510.
In other words,
Different kinds of meters with BACNet, Lonwork protocol is conneted to Automation Server.
I'd like to make Com'X510 bring in all the energy related data that Automation Server has.
Can we do this?
Best Regards,
Reply 1
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
2019-02-20
05:35 AM
You can set the Automation Server as a ModBus Server.
Create an interface ModBus TCP Server and under them add the values you want (and link these values to the "real" points).
Then you go to the COm'X and add the AS as a TCP Device and map the point you've created.