Gateways and Energy Servers
Schneider Electric support forum to share knowledge about product selection, installation and troubleshooting for EcoStruxure Panel Server, PowerTag, Com'X, Link150…
User | Count |
---|---|
82 | |
46 | |
29 | |
28 |
Link copied. Please paste this link to share this article on your social media post.
Hi Everyone
I installed a COM'X510 with 9 Power Meters. 4 of them are PM5330 and 5 of them are PM820MG. All of them are conected by a MODBUS, but i have a problem.
The COM'X detect all ID's, but only recognize the PM5330, the PM820MG doesn't recognize it.
What can I do?
Can be a problem with Firmware of the PM820?
Thanks for all!!
Regards!
Link copied. Please paste this link to share this article on your social media post.
Can start with confirming that the PM800s have the same serial settnigs (8E1 vs 8O1 vs 8N1) as other devices and that the baud rates match the gateway.
Link copied. Please paste this link to share this article on your social media post.
All are in Modbus RTU, 19200 Bdu, non parity.
Link copied. Please paste this link to share this article on your social media post.
Hi man, i can fix it. I must configure the Com X with "1" in the end bit!!
Thanks for all!
Posted: 2017-12-04 09:08 AM
Link copied. Please paste this link to share this article on your social media post.
Glad to hear you got it working!
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.