Ask Me About Webinar: Data Center Assets - Modeling, Cooling, and CFD Simulation Join our 30-minute expert session on July 10, 2025 (9:00 AM & 5:00 PM CET), to explore Digital Twins, cooling simulations, and IT infrastructure modeling. Learn how to boost resiliency and plan power capacity effectively.Register now to secure your spot!
What happens if there is a power outage during a UPS firmware upgrade?
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
A UPS firmware upgrade cannot be initiated if the UPS is On battery.
If a firmware upgrade is already in progress when the input power is interrupted:
– Once the firmware upgrade was initiated with Output Power Off, the firmware upgrade will complete.
– If the firmware upgrade was initiated with Output Power On, power supply from the UPS to the connected devices will be interrupted, and connected devices will not be shut down gracefully. The firmware upgrade will complete successfully.