Posted: 2024-01-27 12:10 PM
For the TC900, i found that sometimes the setpoint are changed by itself to 26 degree celcius. Can we prevent this from happening?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-01-29 04:38 PM . Last Modified: 2024-02-04 03:03 PM
@nathanaelowen11 the factory default setpoint is 26°C, I suspect that the thermostat is going back to default after power failure. Please ensure that parameter 03 is set to 00
Refer to the Installation guide for details on accessing these parameters
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-01-29 04:38 PM . Last Modified: 2024-02-04 03:03 PM
@nathanaelowen11 the factory default setpoint is 26°C, I suspect that the thermostat is going back to default after power failure. Please ensure that parameter 03 is set to 00
Refer to the Installation guide for details on accessing these parameters
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-02-05 04:59 AM
Thank you for your reply. I see the factory default is 26°C. I already ensure the parameter 03 is already set to 00 (since its default value). Is it possible due to power blink? Because in the same project i have another pair of thermostat doing duty-standby FCU by turning off the power supply. Those pair of thermostat is not affected.
The one that is changing is the one standing individually, all over the building (76 units), changed to 26 at the same time.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2 weeks ago
How to set KP, KI from display of TC900 Thermostat.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2 weeks ago
@somprasong_rojp please contact your local product support who can provide you instructions.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2 weeks ago
Thank you for your reply.