Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Brand Logo
Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
close
  • Community Home
  • Forums
    • By Topic
    • By Topic
      EcoStruxure Building
      • Field Devices Forum
      • SmartConnector Forum
      EcoStruxure Power & Grid
      • Gateways and Energy Servers
      • Metering & Power Quality
      • Protection & Control
      APC UPS, Critical Power, Cooling and Racks
      • APC UPS Data Center & Enterprise Solutions Forum
      • APC UPS for Home and Office Forum
      EcoStruxure IT
      • EcoStruxure IT forum
      • EcoStruxure IT™ Advisor CFD
      Remote Operations
      • EcoStruxure Geo SCADA Expert Forum
      • Remote Operations Forum
      Industrial Automation
      • Alliance System Integrators Forum
      • AVEVA Plant SCADA Forum
      • CPG Expert Forum DACH
      • EcoStruxure Automation Expert / IEC 61499 Forum
      • Fabrika ve Makina Otomasyonu Çözümleri
      • Harmony Control Customization Forum
      • Industrial Edge Computing Forum
      • Industry Automation and Control Forum
      • Korea Industrial Automation Forum
      • Machine Automation Forum
      • Modicon PAC Forum
      • PLC Club Indonesia
      Schneider Electric Wiser
      • Schneider Electric Wiser Forum
      Power Distribution IEC
      • Eldistribution & Fastighetsautomation
      • Elektrik Tasarım Dağıtım ve Uygulama Çözümleri
      • Paneelbouw & Energie Distributie
      • Power Distribution and Digital
      • Solutions for Motor Management
      • Specifiers Club ZA Forum
      • Електропроектанти България
      Power Distribution NEMA
      • Power Monitoring and Energy Automation NAM
      Power Distribution Software
      • EcoStruxure Power Design Forum
      • LayoutFAST User Group Forum
      Energy & Sustainability Services
      • Green Building Scoring and Certification Forum
      Light and Room Control
      • SpaceLogic C-Bus Forum
      Solutions for your Business
      • Solutions for your Business Forum
      Support
      • Ask the Community
  • Knowledge Center
    • Building Automation Knowledge Base
    • Remote Operations Devices Knowledge Base
    • Geo SCADA Knowledge Base
    • Industrial Automation How-to videos
    • Digital E-books
    • Success Stories Corner
    • EcoStruxure IT Help Center
  • Events & Webinars
    • All Events
    • Innovation Talks
    • Innovation Summit
    • Let's Exchange Series
    • Partner Success
    • Process Automation Talks
    • Technology Partners
  • Ideas
    • EcoStruxure Building
      • EcoStruxure Building Advisor Ideas
      Remote Operations
      • EcoStruxure Geo SCADA Expert Ideas
      • Remote Operations Devices Ideas
      Industrial Automation
      • Modicon Ideas & new features
  • Blogs
    • By Topic
    • By Topic
      EcoStruxure Power & Grid
      • Backstage Access Resources
      EcoStruxure IT
      • EcoStruxure IT™ Advisor CFD
      Remote Operations
      • Remote Operations Blog
      Industrial Automation
      • Industrie du Futur France
      • Industry 4.0 Blog
      Power Distribution NEMA
      • NEMA Power Foundations Blog
      Energy & Sustainability Services
      • Active Energy Management Blog
      Light and Room Control
      • KNX Blog
      Knowledge Center
      • Digital E-books
      • Geo SCADA Knowledge Base
      • Industrial Automation How-to videos
      • Remote Operations Devices Knowledge Base
      • Success Stories Corner
  • companyImpact

Important Announcement: Community Back to Full Functionality

Dear Members, we are thrilled to announce that our Community is back to full functionality and that posts publication is now enabled again! We appreciate your patience during the last weeks. Learn more about our Community Guidelines. Thank you, Schneider Electric Community Team.

Is a Replacement CO2 Sensor Available For a Living Space Sensor

Field Devices Forum

Schneider Electric support forum about all Field Devices brands of Sensors, Thermostats, Glass Touch Panels, Valves and Actuators

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Communities
  • EcoStruxure Building
  • Field Devices
  • Field Devices Forum
  • Is a Replacement CO2 Sensor Available For a Living Space Sensor
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
CraigEl
Administrator CraigEl Administrator
12
DavidChild
Sisko DavidChild Sisko
7
Gary
Captain Gary Captain
7
Troy_Wecker
Ensign Troy_Wecker Ensign
5
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Field Devices Forum
Solved
arlena
Lieutenant | EcoXpert Master arlena Lieutenant | EcoXpert Master
Lieutenant | EcoXpert Master

Posted: ‎2022-05-09 10:34 AM

0 Likes
6
1998
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-05-09 10:34 AM

Is a Replacement CO2 Sensor Available For a Living Space Sensor

The Co2 sensor is removable from the SXWSBTXCXSXX , but I can't find the part number to order a replacement.  Are they available?

Labels
  • Labels:
  • Temperature Humidity & Air quality Sensors
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
CraigEl
Administrator CraigEl Administrator
Administrator

Posted: ‎2022-05-15 05:42 PM

0 Likes
0
1906
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-05-15 05:42 PM

I don't believe that this is intended as a field replaceable item

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Troy_Wecker
Ensign Troy_Wecker Ensign
Ensign

Posted: ‎2022-06-01 09:27 PM

0 Likes
4
1785
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-06-01 09:27 PM

The CO2 Sensor is Non Dispersion InfraRed (NDIR).  It does not contain a chemical element.  That provides for a typical longer life and reliability,  is not intended for field replacement.  The product electronics continually monitors the sensor and provides continued accuracy.

 

CO2 detect 06012022.jpg

See Answer In Context

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 6
CraigEl
Administrator CraigEl Administrator
Administrator

Posted: ‎2022-05-15 05:42 PM

0 Likes
0
1907
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-05-15 05:42 PM

I don't believe that this is intended as a field replaceable item

Reply

Link copied. Please paste this link to share this article on your social media post.

Troy_Wecker
Ensign Troy_Wecker Ensign
Ensign

Posted: ‎2022-06-01 09:27 PM

0 Likes
4
1786
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-06-01 09:27 PM

The CO2 Sensor is Non Dispersion InfraRed (NDIR).  It does not contain a chemical element.  That provides for a typical longer life and reliability,  is not intended for field replacement.  The product electronics continually monitors the sensor and provides continued accuracy.

 

CO2 detect 06012022.jpg

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

arlena
Lieutenant | EcoXpert Master arlena Lieutenant | EcoXpert Master
Lieutenant | EcoXpert Master

Posted: ‎2022-06-09 06:23 PM

In response to Troy_Wecker
0 Likes
3
1688
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-06-09 06:23 PM

We are seeing maybe 1or 2% failure (as in reading 0) within 1 year.  If they were not meant to be replaceable, SE should save the money and solder them to the board without using a socket!

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

CraigEl
Administrator CraigEl Administrator
Administrator

Posted: ‎2022-06-09 06:29 PM

In response to arlena
1 Like
0
1686
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-06-09 06:29 PM

I dare say that they also aren't designed to have that sort of failure rate either... I suggest that you contact your local support channel to have them replaced under warranty. You might also request a failure analysis, known in SE as a TEX request.

Reply

Link copied. Please paste this link to share this article on your social media post.

Troy_Wecker
Ensign Troy_Wecker Ensign
Ensign

Posted: ‎2022-06-10 08:37 AM

In response to arlena
0 Likes
1
1671
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-06-10 08:37 AM

The CO2 sensor on the SXWSBTXCXSXX isn't socketed.  It's not field replaceable. 

 

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

arlena
Lieutenant | EcoXpert Master arlena Lieutenant | EcoXpert Master
Lieutenant | EcoXpert Master

Posted: ‎2022-06-10 11:42 AM . Last Modified: ‎2022-06-10 11:45 AM

In response to Troy_Wecker
1 Like
0
1664
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-06-10 11:42 AM . Last Modified: ‎2022-06-10 11:45 AM

The one in front of me is 🙂

 

See attachment.   So the only reason it is not field replaceable is because SE chooses not to make it available for replacement.

Attachments
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

Additional options
You do not have permission to remove this product association.
 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this forum after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2023 Schneider Electric, Inc