Welcome to the new Schneider Electric Community

It's your place to connect with experts and peers, get continuous support, and share knowledge.

  • Explore the new navigation for even easier access to your community.
  • Bookmark and use our new, easy-to-remember address (community.se.com).
  • Get ready for more content and an improved experience.

Contact SchneiderCommunity.Support@se.com if you have any questions.

Close
Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
Send Invite Cancel
84416members
353604posts

Bagaimana cara seleksi kapasitas relay thermal?

Expert on Demand for Standards & Regulations

Solved
IbrahimKurniawan
Crewman
Crewman
0 Likes
2
147

Bagaimana cara seleksi kapasitas relay thermal?

Siang, mau tanya, relay thermal itu seleksi kapasitasnya bagaimana ya? Thanks


Accepted Solutions
HelvinHermanT
Captain Captain
Captain
0 Likes
1
123

Re: Bagaimana cara seleksi kapasitas relay thermal?

Selamat Siang Pak,

 

Terima kasih atas pertanyaannya.

 

Setting Thermal Overload Relay (TOR) bisa dengan:
1. Cek Full Load Current yang ada pada Nameplate Motor
2. Pastikan setting 125% dari Full Load Current.

    Contoh: Full Load Current 60 Ampere, maka TOR perlu di-setting di 75 Ampere (60 Ampere + 25%)
3. Beberapa produsen sudah built setting TOR nya sebagai 125%. Untuk TOR yang seperti itu tidak perlu ditambahkan 25%.       

    Contoh: Full Load Current 60 Ampere, maka TOR bulit in 125% perlu di-setting di 60 Ampere

 

Khusus untuk Produk Schneider Electric, bisa cek d Price List book Bab 8, ada tabel pemilihan bersadarkan besaran Motor dan jenis koneksinya (Direct Online / Star Delta). Pada tabel ada recomendari CB+Relay Thermal dan Kontaktornya.

 

@AP @HendySE 

See Answer In Context

Tags (1)
2 Replies 2
HelvinHermanT
Captain Captain
Captain
0 Likes
1
124

Re: Bagaimana cara seleksi kapasitas relay thermal?

Selamat Siang Pak,

 

Terima kasih atas pertanyaannya.

 

Setting Thermal Overload Relay (TOR) bisa dengan:
1. Cek Full Load Current yang ada pada Nameplate Motor
2. Pastikan setting 125% dari Full Load Current.

    Contoh: Full Load Current 60 Ampere, maka TOR perlu di-setting di 75 Ampere (60 Ampere + 25%)
3. Beberapa produsen sudah built setting TOR nya sebagai 125%. Untuk TOR yang seperti itu tidak perlu ditambahkan 25%.       

    Contoh: Full Load Current 60 Ampere, maka TOR bulit in 125% perlu di-setting di 60 Ampere

 

Khusus untuk Produk Schneider Electric, bisa cek d Price List book Bab 8, ada tabel pemilihan bersadarkan besaran Motor dan jenis koneksinya (Direct Online / Star Delta). Pada tabel ada recomendari CB+Relay Thermal dan Kontaktornya.

 

@AP @HendySE 

Tags (1)
IbrahimKurniawan
Crewman
Crewman
0 Likes
0
115

Re: Bagaimana cara seleksi kapasitas relay thermal?

Oke paham Pak @HelvinHermanT , thanks!

Tags (1)