Bagaimana cara seleksi kapasitas relay thermal?

Expert on Demand for Standards & Regulations

Solved
IbrahimKurniawan
Crewman
Crewman
0 Likes
2
149

Bagaimana cara seleksi kapasitas relay thermal?

Siang, mau tanya, relay thermal itu seleksi kapasitasnya bagaimana ya? Thanks


Accepted Solutions
HelvinHermanT
Captain Captain
Captain
0 Likes
1
125

Re: Bagaimana cara seleksi kapasitas relay thermal?

Selamat Siang Pak,

 

Terima kasih atas pertanyaannya.

 

Setting Thermal Overload Relay (TOR) bisa dengan:
1. Cek Full Load Current yang ada pada Nameplate Motor
2. Pastikan setting 125% dari Full Load Current.

    Contoh: Full Load Current 60 Ampere, maka TOR perlu di-setting di 75 Ampere (60 Ampere + 25%)
3. Beberapa produsen sudah built setting TOR nya sebagai 125%. Untuk TOR yang seperti itu tidak perlu ditambahkan 25%.       

    Contoh: Full Load Current 60 Ampere, maka TOR bulit in 125% perlu di-setting di 60 Ampere

 

Khusus untuk Produk Schneider Electric, bisa cek d Price List book Bab 8, ada tabel pemilihan bersadarkan besaran Motor dan jenis koneksinya (Direct Online / Star Delta). Pada tabel ada recomendari CB+Relay Thermal dan Kontaktornya.

 

@AP @HendySE 

See Answer In Context

Tags (1)
2 Replies 2
HelvinHermanT
Captain Captain
Captain
0 Likes
1
126

Re: Bagaimana cara seleksi kapasitas relay thermal?

Selamat Siang Pak,

 

Terima kasih atas pertanyaannya.

 

Setting Thermal Overload Relay (TOR) bisa dengan:
1. Cek Full Load Current yang ada pada Nameplate Motor
2. Pastikan setting 125% dari Full Load Current.

    Contoh: Full Load Current 60 Ampere, maka TOR perlu di-setting di 75 Ampere (60 Ampere + 25%)
3. Beberapa produsen sudah built setting TOR nya sebagai 125%. Untuk TOR yang seperti itu tidak perlu ditambahkan 25%.       

    Contoh: Full Load Current 60 Ampere, maka TOR bulit in 125% perlu di-setting di 60 Ampere

 

Khusus untuk Produk Schneider Electric, bisa cek d Price List book Bab 8, ada tabel pemilihan bersadarkan besaran Motor dan jenis koneksinya (Direct Online / Star Delta). Pada tabel ada recomendari CB+Relay Thermal dan Kontaktornya.

 

@AP @HendySE 

Tags (1)
IbrahimKurniawan
Crewman
Crewman
0 Likes
0
117

Re: Bagaimana cara seleksi kapasitas relay thermal?

Oke paham Pak @HelvinHermanT , thanks!