Welcome to the new Schneider Electric Community

It's your place to connect with experts and peers, get continuous support, and share knowledge.

  • Explore the new navigation for even easier access to your community.
  • Bookmark and use our new, easy-to-remember address (community.se.com).
  • Get ready for more content and an improved experience.

Contact SchneiderCommunity.Support@se.com if you have any questions.

Close
Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
Send Invite Cancel
84562members
353832posts

Bagaimana Pengaturan Power Supply pada aplikasi medis ?

Expert on Demand for Standards & Regulations

Solved
ArtawanSiregar
Crewman
Crewman
0 Likes
3
164

Bagaimana Pengaturan Power Supply pada aplikasi medis ?

Sore mau tanya, bagaimana pengaturan power supply pada aplikasi medis ya? Apakah ada standardnya? Terima kasih.

Tags (1)

Accepted Solutions
HelvinHermanT
Captain Captain
Captain
0 Likes
2
161

Re: Bagaimana Pengaturan Power Supply pada aplikasi medis ?

Selamat Siang,

 

Untuk Suplai Daya pada aplikasi medis bisa dilihat pada PUIL 2020 (SNI 0225) bagian 7-710 atau pada IEC 60364-7-710 Ed2.

 

Pada PUIL 2020 Bagian 7-710, beberapa point penting :

 

1. Adanya Changeover switch yang memungkinkan tukar-alih otomatis (Sumber Utama dan Sumber keselamatan) :

 

710.313 Suplai daya
710.313.1 Umum
Dalam lokasi medis, sistem distribusi sebaiknya didesain dan dipasang untuk memungkinkan tukar-alih otomatis dari jaringan distribusi utama ke sumber keselamatan listrik yang menyuplai beban esensial (sesuai SNI 0225-5-55, ayat 556).

 

710.55.1 Sirkit pencahayaan
Dalam lokasi medis kelompok 1 dan kelompok 2, paling sedikit harus dilengkapi dengan dua sumber suplai yang berbeda untuk beberapa luminer dengan 2 sirkit. Salah satu dari dua sirkit harus dihubungkan ke layanan keselamatan.

 

710.55.3 Sirkit stopkontak dalam sistem IT medis untuk lokasi medis kelompok 2
Pada setiap tempat perawatan pasien, misalnya kepala tempat tidur, susunan stopkontak harus seperti berikut:
 harus dipasang minimum dua sirkit terpisah yang menyulang stopkontak; atau
 setiap stopkontak masing-masing harus diproteksi terhadap arus lebih;

 

2. Persyatan layanan suplai daya keselamatan dapat dilihat pada :

 

710.556.5.2.2 Persyaratan rinci untuk layanan suplai daya keselamatan
710.556.5.2.2.1 Sumber suplai daya dengan periode tukar alih kurang dari atau sama dengan 0,5 detik
Pada kejadian kegagalan voltase pada satu atau lebih konduktor lin di panel distribusi, sumber suplai daya keselamatan khusus harus mempertahankan luminer meja ruang bedah dan luminer penting lain, misalnya endoskopi, untuk periode minimum 3 jam. Sumber ini harus memulihkan suplai dalam periode tukar alih tidak melebihi 0,5 detik.
710.556.5.2.2.2 Sumber suplai daya dengan periode tukar alih kurang dari atau sama dengan 15 detik
Peralatan menurut 710.556.7.5 dan 710.556.8 harus dihubungkan dalam 15 detik ke sumber suplai daya keselamatan yang mampu mempertahankannya untuk periode minimum 24 jam, ketika voltase satu atau lebih konduktor lin pada panel distribusi utama untuk layanan keselamatan telah berkurang lebih dari 10% dari nilai nominal voltase suplai dan dengan durasi lebih besar dari 3 detik.
CATATAN Durasi selama 24 jam dapat dikurangi hingga minimum 3 jam jika persyaratan medis dan penggunaan lokasi, termasuk setiap perawatan, dapat ditutup dan jika gedung dapat dievakuasi dengan baik dalam waktu kurang dari 24 jam.

 

710.556.5.2.2.3 Sumber suplai daya dengan periode tukar alih yang lebih lama dari 15 detik

Peralatan selain yang dicakup dalam 710.556.5.2.2.1 dan 710.556.5.2.2.2, yang disyaratkan untuk pemeliharaan layanan rumah sakit, dapat dihubungkan secara otomatis atau secara manual ke sumber suplai daya keselamatan yang mampu mempertahankannya selama periode 24 jam. Peralatan ini dapat termasuk, misalnya:
 peralatan sterilisasi;
 instalasi teknik gedung, khususnya sistem pengondisi udara, pemanasan dan
ventilasi, layanan gedung dan sistem pembuangan limbah;
 peralatan pendinginan;
 peralatan masak;
 pengisi aki.

 

710.556.7 Sirkit pencahayaan keselamatan
710.556.7.6 Pencahayaan keselamatan
Pada kejadian kegagalan daya jaringan, iluminasi minimum yang perlu harus disediakan dari sumber layanan keselamatan untuk lokasi berikut. Periode tukar alih ke sumber keselamatan tidak boleh melebihi 15 detik:
 rute penyelamatan darurat;
 pencahayaan tanda keluar;
 lokasi untuk PSDK untuk set generator darurat dan untuk panel distribusi utama dari suplai daya normal dan sumber daya untuk layanan keselamatan;
 ruangan yang ditujukan untuk layanan penting. Dalam setiap ruangan paling sedikit satu luminer harus disuplai dari sumber daya untuk layanan keselamatan;
 ruangan lokasi medis kelompok 1. Dalam setiap ruangan paling sedikit satu luminer harus disuplai dari sumber suplai daya untuk layanan keselamatan;
 ruangan untuk lokasi medis kelompok 2. Minimum 50 % dari pencahayaan harus disuplai dari sumber daya untuk layanan keselamatan.

 

710.556.8 Layanan lain
Layanan selain pencahayaan yang mensyaratkan suplai layanan keselamatan dengan periode tukar alih yang tidak melebihi 15 detik dapat mencakup, misalnya, yang berikut:
 lift yang ditentukan untuk anggota pemadam kebakaran;
 sistem ventilasi untuk ekstraksi asap;
 sistem pemanggilan;
 peralatan listrik medis yang digunakan dalam lokasi medis kelompok 2 yang melayani pembedahan atau tindakan lain yang sangat vital. Peralatan tersebut ditentukan oleh staf yang bertanggungjawab;
 peralatan listrik untuk suplai gas medis termasuk udara kompresi, suplai vakum dan tindakan pembiusan (anestesi) maupun gawai pemantaunya;
 sistem deteksi kebakaran, alarm kebakaran dan pemadam kebakaran

 

 

See Answer In Context

Tags (1)
HelvinHermanT
Captain Captain
Captain
0 Likes
1
159

Re: Bagaimana Pengaturan Power Supply pada aplikasi medis ?

Update terbaru dari IEC 6036407-710 Low-voltage electrical installations – Part 7-710: Requirements for special installations or locations – Medical locations yang dikeluarkan pada Mei 2021, perihal Suplai Daya bisa dilihat dibawah ini :

 

1. Distribution Board comply dengan IEC 61439 (Type Tested Panel) --> Contoh PrismaSet & Blokset  & Okken dari Schneider.

2. Medical IT Panel ditempatkan dalam arak maximal 25 meter untuk lokasi group 2 dan pada lantai yang sama.

3. Rekomendasi untuk menghindari gangguan EMC (elektromagnetik)

 

 

710.51.101 Distribution boards
710.51.101.1 General
Distribution boards shall be in accordance with IEC 61439 (all parts).
Separate distribution boards shall be provided for the general power supply and the electricsupply system for safety services.

 

710.51.101.2 Medical locations of group 2
Distribution boards for group 2 medical locations shall be installed in close proximity to the areas they serve and be clearly labelled. Distribution boards shall be installed outside the group 2 medical locations and should be safely secured against operation by unauthorized persons.
The medical IT distribution board should be located within 25 m of the area it serves. Leakage currents should be taken into consideration.


NOTE 1 The 25 m are related to possible capacitive leakage current.

Recommendations for the minimum distances from the isolating transformers of the medical IT system to the equipment used within the patient environment are shown in informative Annex B.
The distribution board should be easily accessible for maintenance and be located on the same level and within the same fire compartment as the load it serves.


NOTE 2 A distribution board for medical locations is one that fulfils the functions for the supplied medical location area assigned to it and where the main power supply voltage is monitored for operating the change-over to the electric supply system for safety services in accordance with 710.313.1.101 and 710.313.1.102.

 

See Answer In Context

Tags (1)
3 Replies 3
HelvinHermanT
Captain Captain
Captain
0 Likes
2
162

Re: Bagaimana Pengaturan Power Supply pada aplikasi medis ?

Selamat Siang,

 

Untuk Suplai Daya pada aplikasi medis bisa dilihat pada PUIL 2020 (SNI 0225) bagian 7-710 atau pada IEC 60364-7-710 Ed2.

 

Pada PUIL 2020 Bagian 7-710, beberapa point penting :

 

1. Adanya Changeover switch yang memungkinkan tukar-alih otomatis (Sumber Utama dan Sumber keselamatan) :

 

710.313 Suplai daya
710.313.1 Umum
Dalam lokasi medis, sistem distribusi sebaiknya didesain dan dipasang untuk memungkinkan tukar-alih otomatis dari jaringan distribusi utama ke sumber keselamatan listrik yang menyuplai beban esensial (sesuai SNI 0225-5-55, ayat 556).

 

710.55.1 Sirkit pencahayaan
Dalam lokasi medis kelompok 1 dan kelompok 2, paling sedikit harus dilengkapi dengan dua sumber suplai yang berbeda untuk beberapa luminer dengan 2 sirkit. Salah satu dari dua sirkit harus dihubungkan ke layanan keselamatan.

 

710.55.3 Sirkit stopkontak dalam sistem IT medis untuk lokasi medis kelompok 2
Pada setiap tempat perawatan pasien, misalnya kepala tempat tidur, susunan stopkontak harus seperti berikut:
 harus dipasang minimum dua sirkit terpisah yang menyulang stopkontak; atau
 setiap stopkontak masing-masing harus diproteksi terhadap arus lebih;

 

2. Persyatan layanan suplai daya keselamatan dapat dilihat pada :

 

710.556.5.2.2 Persyaratan rinci untuk layanan suplai daya keselamatan
710.556.5.2.2.1 Sumber suplai daya dengan periode tukar alih kurang dari atau sama dengan 0,5 detik
Pada kejadian kegagalan voltase pada satu atau lebih konduktor lin di panel distribusi, sumber suplai daya keselamatan khusus harus mempertahankan luminer meja ruang bedah dan luminer penting lain, misalnya endoskopi, untuk periode minimum 3 jam. Sumber ini harus memulihkan suplai dalam periode tukar alih tidak melebihi 0,5 detik.
710.556.5.2.2.2 Sumber suplai daya dengan periode tukar alih kurang dari atau sama dengan 15 detik
Peralatan menurut 710.556.7.5 dan 710.556.8 harus dihubungkan dalam 15 detik ke sumber suplai daya keselamatan yang mampu mempertahankannya untuk periode minimum 24 jam, ketika voltase satu atau lebih konduktor lin pada panel distribusi utama untuk layanan keselamatan telah berkurang lebih dari 10% dari nilai nominal voltase suplai dan dengan durasi lebih besar dari 3 detik.
CATATAN Durasi selama 24 jam dapat dikurangi hingga minimum 3 jam jika persyaratan medis dan penggunaan lokasi, termasuk setiap perawatan, dapat ditutup dan jika gedung dapat dievakuasi dengan baik dalam waktu kurang dari 24 jam.

 

710.556.5.2.2.3 Sumber suplai daya dengan periode tukar alih yang lebih lama dari 15 detik

Peralatan selain yang dicakup dalam 710.556.5.2.2.1 dan 710.556.5.2.2.2, yang disyaratkan untuk pemeliharaan layanan rumah sakit, dapat dihubungkan secara otomatis atau secara manual ke sumber suplai daya keselamatan yang mampu mempertahankannya selama periode 24 jam. Peralatan ini dapat termasuk, misalnya:
 peralatan sterilisasi;
 instalasi teknik gedung, khususnya sistem pengondisi udara, pemanasan dan
ventilasi, layanan gedung dan sistem pembuangan limbah;
 peralatan pendinginan;
 peralatan masak;
 pengisi aki.

 

710.556.7 Sirkit pencahayaan keselamatan
710.556.7.6 Pencahayaan keselamatan
Pada kejadian kegagalan daya jaringan, iluminasi minimum yang perlu harus disediakan dari sumber layanan keselamatan untuk lokasi berikut. Periode tukar alih ke sumber keselamatan tidak boleh melebihi 15 detik:
 rute penyelamatan darurat;
 pencahayaan tanda keluar;
 lokasi untuk PSDK untuk set generator darurat dan untuk panel distribusi utama dari suplai daya normal dan sumber daya untuk layanan keselamatan;
 ruangan yang ditujukan untuk layanan penting. Dalam setiap ruangan paling sedikit satu luminer harus disuplai dari sumber daya untuk layanan keselamatan;
 ruangan lokasi medis kelompok 1. Dalam setiap ruangan paling sedikit satu luminer harus disuplai dari sumber suplai daya untuk layanan keselamatan;
 ruangan untuk lokasi medis kelompok 2. Minimum 50 % dari pencahayaan harus disuplai dari sumber daya untuk layanan keselamatan.

 

710.556.8 Layanan lain
Layanan selain pencahayaan yang mensyaratkan suplai layanan keselamatan dengan periode tukar alih yang tidak melebihi 15 detik dapat mencakup, misalnya, yang berikut:
 lift yang ditentukan untuk anggota pemadam kebakaran;
 sistem ventilasi untuk ekstraksi asap;
 sistem pemanggilan;
 peralatan listrik medis yang digunakan dalam lokasi medis kelompok 2 yang melayani pembedahan atau tindakan lain yang sangat vital. Peralatan tersebut ditentukan oleh staf yang bertanggungjawab;
 peralatan listrik untuk suplai gas medis termasuk udara kompresi, suplai vakum dan tindakan pembiusan (anestesi) maupun gawai pemantaunya;
 sistem deteksi kebakaran, alarm kebakaran dan pemadam kebakaran

 

 

Tags (1)
HelvinHermanT
Captain Captain
Captain
0 Likes
1
160

Re: Bagaimana Pengaturan Power Supply pada aplikasi medis ?

Update terbaru dari IEC 6036407-710 Low-voltage electrical installations – Part 7-710: Requirements for special installations or locations – Medical locations yang dikeluarkan pada Mei 2021, perihal Suplai Daya bisa dilihat dibawah ini :

 

1. Distribution Board comply dengan IEC 61439 (Type Tested Panel) --> Contoh PrismaSet & Blokset  & Okken dari Schneider.

2. Medical IT Panel ditempatkan dalam arak maximal 25 meter untuk lokasi group 2 dan pada lantai yang sama.

3. Rekomendasi untuk menghindari gangguan EMC (elektromagnetik)

 

 

710.51.101 Distribution boards
710.51.101.1 General
Distribution boards shall be in accordance with IEC 61439 (all parts).
Separate distribution boards shall be provided for the general power supply and the electricsupply system for safety services.

 

710.51.101.2 Medical locations of group 2
Distribution boards for group 2 medical locations shall be installed in close proximity to the areas they serve and be clearly labelled. Distribution boards shall be installed outside the group 2 medical locations and should be safely secured against operation by unauthorized persons.
The medical IT distribution board should be located within 25 m of the area it serves. Leakage currents should be taken into consideration.


NOTE 1 The 25 m are related to possible capacitive leakage current.

Recommendations for the minimum distances from the isolating transformers of the medical IT system to the equipment used within the patient environment are shown in informative Annex B.
The distribution board should be easily accessible for maintenance and be located on the same level and within the same fire compartment as the load it serves.


NOTE 2 A distribution board for medical locations is one that fulfils the functions for the supplied medical location area assigned to it and where the main power supply voltage is monitored for operating the change-over to the electric supply system for safety services in accordance with 710.313.1.101 and 710.313.1.102.

 

Tags (1)
ArtawanSiregar
Crewman
Crewman

Re: Bagaimana Pengaturan Power Supply pada aplikasi medis ?

Baik, terima kasih atas informasinya.

Tags (1)