Bagaimana Pemasangan GPAS (RCCB / ELCB / RCBO) pada pelanggan 900VA ?

Expert on Demand for Standards & Regulations

Connect to Schneider Electric experts in your country for any inquiry about electrical installation and safety standards and regulations.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Power Distribution IEC
  • Expert on Demand for Standards & Regulations
  • Bagaimana Pemasangan GPAS (RCCB / ELCB / RCBO) pada pelanggan 900VA ?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
HelvinHermanT
Admiral HelvinHermanT Admiral
106
faisalamir
Lieutenant faisalamir Lieutenant
7
Dwinanto_Setyadi
Lieutenant JG Dwinanto_Setyadi Lieutenant JG
7
View All

Recommended Forums

  • Comunidade de Soluções Elétricas

  • Power Distribution and Digital Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Expert on Demand for Standards & Regulations
Start a Topic
Solved
HelvinHermanT
Admiral HelvinHermanT Admiral
Admiral

Posted: ‎2024-10-26 10:52 PM . Last Modified: ‎2024-10-28 01:06 AM

0 Likes
3
3086
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-10-26 10:52 PM . Last Modified: ‎2024-10-28 01:06 AM

Bagaimana Pemasangan GPAS (RCCB / ELCB / RCBO) pada pelanggan 900VA ?

Selamat Hari Listrik Nasional 2024

WhatsApp Image 2024-10-27 at 13.38.04.jpeg

 

Ada pertanyaan :


Bagaimana cara Pemasangan GPAS (RCCB/ELCB/RCBO) pada pelanggan 900VA atau 900 Watt ?

 

Mohon diberikan penjelasan.

 

 

Labels
  • Labels:
  • Indonesia
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
HelvinHermanT
Admiral HelvinHermanT Admiral
Admiral

Posted: ‎2024-10-26 11:05 PM . Last Modified: ‎2024-10-26 11:57 PM

0 Likes
0
3079
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-10-26 11:05 PM . Last Modified: ‎2024-10-26 11:57 PM

Dalam Pertanyaan diatas, sang penanya menggunakan istilah GPAS, ELCB, RCCB, RCBO dan Pelanggan 900VA.

 

Mari kita bahas secara bertahap.

 

  • GPAS adalah Gawai Proteksi Arus Sisa merupakan alat Pemutus Sirkit untuk Proteksi gangguan arus sisa. Menggunakan Standar SNI IEC 61008.
  • RCCB adalah Residual Current Circuit Breaker yang merupakan alat pemutus sirkit saat terdeteksi arus sisa (residual Current). Menggunakan Standar SNI IEC 61008.
  • GPAS adalah nama lain yang digunakan di Indonesia untuk menyebut RCCB. 

         GPAS = RCCB

  • ELCB adalah Earth Leakage Circuit Breaker atau teknologi lama untuk proteksi terhadap gangguan kebocoran arus ke bumi.
  • RCBO = Residual Circuit breaker dengan over current. RCBO adalah GPAS/RCCB dengan fungsi proteksi beban lebih. Menggunakan Standar SNI IEC 61009.
    RCBO  = GPAS/RCCB + MCB
  • Pelanggan 900VA atau 900 watt adalah Kategori Pelanggan Listrik PLN dengan Kapasitas langganan 900VA atau 900 watt.

 

Dalam penyebutan sehari hari seringkali orang salah kaprah menyebut GPAS/RCCB dengan sebutan ELCB.

Pada saat ini penjual atau pembeli menyebut ELCB, maka yang dimaksudkan adalah GPAS/RCCB.

 

RCCB = GPAS (Proteksi Arus Sisa)

RCBO = GPAS + MCB (Proteksi Arus sisa dengan proteksi arus lebih)

 

 

 

 

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

HelvinHermanT
Admiral HelvinHermanT Admiral
Admiral

Posted: ‎2024-10-26 11:16 PM . Last Modified: ‎2024-10-28 01:14 AM

0 Likes
0
3077
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-10-26 11:16 PM . Last Modified: ‎2024-10-28 01:14 AM

Bagaimana Denah dan diagram garis tunggal pada pelanggan 900VA, dapat dilihat dalam buku Keselamatan dan Pemasangan Instalasi Listrik Voltase Rendah untuk Rumah Tangga Edisi 2016 yang diterbitkan Kementerian Energi dan Sumber Daya Mineral - Direktorat Jenderal Ketenagalistrikan.

Keselamatan dan Pemasangan Instalasi Listrik Voltase Rendah Untuk Rumah Tangga Edisi 2016 

 

Instalasi 900VA PUIL.png

 

 

 

Bagaimana Pemasangan GPAS/RCCB & RCBO pada pelanggan 900VA, dapat dilihat dalam buku Keselamatan dan Pemasangan Instalasi Listrik Voltase Rendah untuk Rumah Tangga Edisi 2016 yang diterbitkan Kementerian Energi dan Sumber Daya Mineral - Direktorat Jenderal Ketenagalistrikan.

 

1. Penggunaan GPAS / RCCB untuk Daya 900 VA menggunakan contoh Daya ≤ 2 200 VA

Instalasi 900VA PUIL - RCCB.png

 

 

2. Penggunaan RCBO untuk Daya 900 VA menggunakan contoh daya ≤ 2200 VA

 

Instalasi 900VA PUIL - RCBO.png

 

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

HelvinHermanT
Admiral HelvinHermanT Admiral
Admiral

Posted: ‎2024-10-26 11:26 PM

0 Likes
0
3077
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-10-26 11:26 PM

Bisa dilihat pula Video dari Youtube yang membahas Penggunaan GPAS/RCCB dan RCBO pada pelanggan 900VA.

 

 

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
HelvinHermanT
Admiral HelvinHermanT Admiral
Admiral

Posted: ‎2024-10-26 11:05 PM . Last Modified: ‎2024-10-26 11:57 PM

0 Likes
0
3080
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-10-26 11:05 PM . Last Modified: ‎2024-10-26 11:57 PM

Dalam Pertanyaan diatas, sang penanya menggunakan istilah GPAS, ELCB, RCCB, RCBO dan Pelanggan 900VA.

 

Mari kita bahas secara bertahap.

 

  • GPAS adalah Gawai Proteksi Arus Sisa merupakan alat Pemutus Sirkit untuk Proteksi gangguan arus sisa. Menggunakan Standar SNI IEC 61008.
  • RCCB adalah Residual Current Circuit Breaker yang merupakan alat pemutus sirkit saat terdeteksi arus sisa (residual Current). Menggunakan Standar SNI IEC 61008.
  • GPAS adalah nama lain yang digunakan di Indonesia untuk menyebut RCCB. 

         GPAS = RCCB

  • ELCB adalah Earth Leakage Circuit Breaker atau teknologi lama untuk proteksi terhadap gangguan kebocoran arus ke bumi.
  • RCBO = Residual Circuit breaker dengan over current. RCBO adalah GPAS/RCCB dengan fungsi proteksi beban lebih. Menggunakan Standar SNI IEC 61009.
    RCBO  = GPAS/RCCB + MCB
  • Pelanggan 900VA atau 900 watt adalah Kategori Pelanggan Listrik PLN dengan Kapasitas langganan 900VA atau 900 watt.

 

Dalam penyebutan sehari hari seringkali orang salah kaprah menyebut GPAS/RCCB dengan sebutan ELCB.

Pada saat ini penjual atau pembeli menyebut ELCB, maka yang dimaksudkan adalah GPAS/RCCB.

 

RCCB = GPAS (Proteksi Arus Sisa)

RCBO = GPAS + MCB (Proteksi Arus sisa dengan proteksi arus lebih)

 

 

 

 

Reply

Link copied. Please paste this link to share this article on your social media post.

HelvinHermanT
Admiral HelvinHermanT Admiral
Admiral

Posted: ‎2024-10-26 11:16 PM . Last Modified: ‎2024-10-28 01:14 AM

0 Likes
0
3078
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-10-26 11:16 PM . Last Modified: ‎2024-10-28 01:14 AM

Bagaimana Denah dan diagram garis tunggal pada pelanggan 900VA, dapat dilihat dalam buku Keselamatan dan Pemasangan Instalasi Listrik Voltase Rendah untuk Rumah Tangga Edisi 2016 yang diterbitkan Kementerian Energi dan Sumber Daya Mineral - Direktorat Jenderal Ketenagalistrikan.

Keselamatan dan Pemasangan Instalasi Listrik Voltase Rendah Untuk Rumah Tangga Edisi 2016 

 

Instalasi 900VA PUIL.png

 

 

 

Bagaimana Pemasangan GPAS/RCCB & RCBO pada pelanggan 900VA, dapat dilihat dalam buku Keselamatan dan Pemasangan Instalasi Listrik Voltase Rendah untuk Rumah Tangga Edisi 2016 yang diterbitkan Kementerian Energi dan Sumber Daya Mineral - Direktorat Jenderal Ketenagalistrikan.

 

1. Penggunaan GPAS / RCCB untuk Daya 900 VA menggunakan contoh Daya ≤ 2 200 VA

Instalasi 900VA PUIL - RCCB.png

 

 

2. Penggunaan RCBO untuk Daya 900 VA menggunakan contoh daya ≤ 2200 VA

 

Instalasi 900VA PUIL - RCBO.png

 

Reply

Link copied. Please paste this link to share this article on your social media post.

HelvinHermanT
Admiral HelvinHermanT Admiral
Admiral

Posted: ‎2024-10-26 11:26 PM

0 Likes
0
3078
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-10-26 11:26 PM

Bisa dilihat pula Video dari Youtube yang membahas Penggunaan GPAS/RCCB dan RCBO pada pelanggan 900VA.

 

 

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore