SEAL / EBO BACnet Alarms problems

EcoStruxure SEAL Forum

This forum is for engineers working EcoStruxure Building Operation, wanting to leverage the SEAL application to improve the efficiency in the engineering process.

Search in

Improve your search experience:

  • Exact phrase β†’ Use quotes " " (e.g., "error 404")
  • Wildcard β†’ Use * for partial words (e.g., build*, *tion)
  • AND / OR β†’ Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short β†’ Use 2–3 relevant words , not full sentences
  • Filters β†’ Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results forΒ 
ShowΒ Β onlyΒ  | Search instead forΒ 
Did you mean:Β 
  • Home
  • Schneider Electric Community
  • EcoStruxure Building
  • EcoStruxure SEAL Forum
  • SEAL / EBO BACnet Alarms problems
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
StefanLundin
Commander StefanLundin Commander
35
Benji
Administrator Benji Administrator
16
Jim.T
Lieutenant JG Jim.T Lieutenant JG
5
APA
Lieutenant APA Lieutenant
4
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure SEAL Forum
Start a Topic
Solved
JohnnyCarlsen
Lieutenant JohnnyCarlsen Lieutenant
Lieutenant

Posted: β€Ž2025-04-07 12:38 AM . Last Modified: β€Ž2025-04-08 03:52 AM

0 Likes
2
591
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2025-04-07 12:38 AM . Last Modified: β€Ž2025-04-08 03:52 AM

SEAL / EBO BACnet Alarms problems

I want to change BACnet Alarm from "Floating to Out of range", but can not make it work. 😞

If I delete BACnet object "bacnet.pt.eventparameters.FL" and create an new 

"bacnet.pt.eventparameters.OOR" it look fine from SEAL but then at open properties on the BACnet Alarm, it still is an Floating Alarm and the "Save Disk" appears. Are there some properties in the BACnet object there has to be changed to ??
 
CODE:
if(object.typeName.match("bacnet.pt.eventparameters.FL")) {
            // Floating BACnet alarm
            const result = await sdkClient.IObjectManagement.DeleteObject({ objectPath: object.fullPath}) // Delete Floating alarm
            if(!result.failed) {
                // Change name
                const newname =  object.fullPath.replace("Floating limit event parameters","Out of range event parameters") 
                // Create Out of range BACnet alarm
                await sdkClient.IAdvanced.CreateObject({path : newname , typeName: "bacnet.pt.eventparameters.OOR", isAggregated: true, isHidden: true })
        }
 }
 
OUTPUT:
IObjectManagement.DeleteObject: Operation executed successfully! Status: Ok Path: /RPC/BACnet Interface/IP Network/RPC/Application/RPC/Alarmer/TE001_A/Floating limit event parameters
 
IAdvanced.CreateObject: Operation executed successfully! Status: Ok Path: /RPC/BACnet Interface/IP Network/RPC/Application/RPC/Alarmer/TE001_A/Out of range event parameters
ISession.Save: Operation executed successfully! Status: Ok
 
RESULT;
JohnnyCarlsen_0-1744011500669.png

 

 
Labels
  • Labels:
  • Script
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
MikaelBodereau
Lieutenant MikaelBodereau Lieutenant
Lieutenant

Posted: β€Ž2025-04-08 12:54 AM

0 Likes
1
531
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2025-04-08 12:54 AM

Hi Johnny, 

I tested with same issue. After some tests i found that YOU MUST ALSO change 'EventType' property.

Like :

res=await sdkClient.IObjectManagement.DeleteObject({objectPath:'/GSVA11_S06000/BACnet Interface/Application/BACnet Alarm/Out of range event parameters'})
res=await sdkClient.IAdvanced.CreateObject({path:'/GSVA11_S06000/BACnet Interface/Application/BACnet Alarm/Floating limit event parameters',typeName:'bacnet.pt.eventparameters.FL',isHidden:true})
res=await sdkClient.IAdvanced.SetPropertyValue({propertyPath:'/GSVA11_S06000/BACnet Interface/Application/BACnet Alarm/EventType',value:new Long(4)})
await sdkClient.ISession.Save()
 

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 2
MikaelBodereau
Lieutenant MikaelBodereau Lieutenant
Lieutenant

Posted: β€Ž2025-04-08 12:54 AM

0 Likes
1
532
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2025-04-08 12:54 AM

Hi Johnny, 

I tested with same issue. After some tests i found that YOU MUST ALSO change 'EventType' property.

Like :

res=await sdkClient.IObjectManagement.DeleteObject({objectPath:'/GSVA11_S06000/BACnet Interface/Application/BACnet Alarm/Out of range event parameters'})
res=await sdkClient.IAdvanced.CreateObject({path:'/GSVA11_S06000/BACnet Interface/Application/BACnet Alarm/Floating limit event parameters',typeName:'bacnet.pt.eventparameters.FL',isHidden:true})
res=await sdkClient.IAdvanced.SetPropertyValue({propertyPath:'/GSVA11_S06000/BACnet Interface/Application/BACnet Alarm/EventType',value:new Long(4)})
await sdkClient.ISession.Save()
 
Reply

Link copied. Please paste this link to share this article on your social media post.

JohnnyCarlsen
Lieutenant JohnnyCarlsen Lieutenant
Lieutenant

Posted: β€Ž2025-04-08 02:51 AM

In response to MikaelBodereau
0 Likes
0
523
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2025-04-08 02:51 AM

Thanks Mikael, it was just what I needed πŸ‘πŸ˜€. In my case EvenType has to be 5 of "Out of range"

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

Β 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings Β© 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore