EcoStruxure Power Design Forum
Schneider Electric support forum to share knowledge about installation and usage for Electrical Network Design and Calculation Software (Ecodial, Ecostruxure Power Design).
Link copied. Please paste this link to share this article on your social media post.
Posted: 2022-01-17 09:50 PM . Last Modified: 2024-11-22 04:25 AM
Dear All:
I have a case. Please see the picture below. It is allowed to use NSX-L type for distribution load protection. Why dose NSX-HB1 type is mandatory used for motor load under the same transformer? the system voltage is 500V. If you need the original file please let me know. chi.yang@se.com
Thanks a lot in advance.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2022-01-18 03:06 AM
Dear Chi,
Thanks for the given project file for the analysis.
For your information, the selection of ‘motor starter(s) and the possible protection device(s)’ are defined as a coordination, by the line of business. Ecodial is making the selection based on the same.
For the network voltage ; 500 volts
For the motor ratings of ; 22 kW or 30 kW
For the startup type; DOL type
For the thermal Protection Type, as 'integrated or separated', and
based on the selection of coordination; there are only a few possible solutions available.
Type 1 |
Type 2 |
GV3L 40 GV3L 50 GV3P 40 GV3P 50 NSX 100* MA 50 * Micrologic 2.2-M 50A * Micrologic 6.2 E-M 50A |
GV3L 40 GV3L 50 GV3P 40 GV3P 50 NSX 100 HB1 MA50 * Micrologic 2.2-M 50A * Micrologic 6.2 E-M 50A NSX 100 HB2 MA50 * Micrologic 2.2-M 50A * Micrologic 6.2 E-M 50A |
So, You will be getting the result from one this possible solution.
Thanks & Regards,
Ecodial Expert Support
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2022-01-18 03:06 AM
Dear Chi,
Thanks for the given project file for the analysis.
For your information, the selection of ‘motor starter(s) and the possible protection device(s)’ are defined as a coordination, by the line of business. Ecodial is making the selection based on the same.
For the network voltage ; 500 volts
For the motor ratings of ; 22 kW or 30 kW
For the startup type; DOL type
For the thermal Protection Type, as 'integrated or separated', and
based on the selection of coordination; there are only a few possible solutions available.
Type 1 |
Type 2 |
GV3L 40 GV3L 50 GV3P 40 GV3P 50 NSX 100* MA 50 * Micrologic 2.2-M 50A * Micrologic 6.2 E-M 50A |
GV3L 40 GV3L 50 GV3P 40 GV3P 50 NSX 100 HB1 MA50 * Micrologic 2.2-M 50A * Micrologic 6.2 E-M 50A NSX 100 HB2 MA50 * Micrologic 2.2-M 50A * Micrologic 6.2 E-M 50A |
So, You will be getting the result from one this possible solution.
Thanks & Regards,
Ecodial Expert Support
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2022-01-18 03:11 AM
Dear Chi,
To comment on the image, enclosed by you.
There is no relationship (Or an influence) between the 'protection device' proposed for the load circuits over the motor circuits.
Thanks & Regards,
Ecodial Expert Support
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.