Motor protection in TT earthing system

Power Distribution and Digital Support

Join experts & peers to learn, share and engage about the key trends of electrical distribution around safety, availability, efficiency and connectivity, as well as power standards & regulations. From design to implementation and operation, let’s discuss how digital and software are transforming your business and your day-to-day work.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Power Distribution IEC
  • Power Distribution and Digital Support
  • Motor protection in TT earthing system
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Genghiz
Captain Genghiz Captain
93
Gregoire_Brun
Commander Gregoire_Brun Commander
80
J_Travostino
Sisko J_Travostino Sisko
70
View All

Recommended Forums

  • Comunidade de Soluções Elétricas

  • Expert on Demand for Standards & Regulations

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Power Distribution and Digital Support
Start a Topic
Solved
ZR
Crewman ZR
Crewman

Posted: ‎2021-12-29 02:35 PM . Last Modified: ‎2024-11-22 04:25 AM

0 Likes
3
1944
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-12-29 02:35 PM . Last Modified: ‎2024-11-22 04:25 AM

Motor protection in TT earthing system

Dear All,

 

I'm trying to configure a control panel used in location with TT earthing system.

For generic load after initial project calculation a RCD is added and since protection device is from Acti9 family, recalculation returns no errors.

For motor load there is a different story.

So after initial calculation a following error is generated:

 
Ecodial TT prva napaka.jpg

 

 

Which also make sense, but after configuring RCD, error still persist with message:

Ecodial TT druga napaka.jpg

 

Does that mean that there is no protective device for motor protection in TT system on offer from SE?

And no, I didn't have "withdrawable" option set to yes.

 

Does anyone know the solution for this problem? Any advice would be nice.

BR from ZR.

Labels
  • Labels:
  • Power Distribution Software
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Genghiz
Captain Genghiz Captain
Captain

Posted: ‎2022-01-03 01:30 AM

0 Likes
2
1938
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-01-03 01:30 AM

Hello

Here is our comments on the query;

 

Cause : 

 

* Along with the motor protection; there is no 'integrated RCD' available.

 

* As the calculation is already ended up, with not able to find the 'add on RCD'

 

Suggestion :

 

The suggestion is to try with the choice of "Separate RCD" to get device selected.

 

Further : 

If the provided suggestion is not working well, then please come back to us with the 'project file (.eac)' for further analysis.

 

Thank you

See Answer In Context

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
Genghiz
Captain Genghiz Captain
Captain

Posted: ‎2022-01-03 01:30 AM

0 Likes
2
1939
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-01-03 01:30 AM

Hello

Here is our comments on the query;

 

Cause : 

 

* Along with the motor protection; there is no 'integrated RCD' available.

 

* As the calculation is already ended up, with not able to find the 'add on RCD'

 

Suggestion :

 

The suggestion is to try with the choice of "Separate RCD" to get device selected.

 

Further : 

If the provided suggestion is not working well, then please come back to us with the 'project file (.eac)' for further analysis.

 

Thank you

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

ZR
Crewman ZR
Crewman

Posted: ‎2022-01-03 07:06 AM

In response to Genghiz
0 Likes
1
1935
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-01-03 07:06 AM

Dear Genghiz,


After choosing "separate RCD" calculation goes through without error.

Ecodial offers RH10M as separate RCD.


I'm wondering why configuration of motor starter Tesys U even with LUCM, which has integrated RCD function, doesn't go through.


BR

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Genghiz
Captain Genghiz Captain
Captain

Posted: ‎2022-01-09 08:21 PM

In response to ZR
0 Likes
0
1920
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-01-09 08:21 PM

Hello

Thanks for the confirmation, that the project file has been successfully completed the calculation. 

 

Further to your inputs;

the possible consideration of motor protection devices with integrated RCD, and the associated selection conditions will be verified with the product development team.

 

Thanks and Regards,

Ecodial Expert Support.

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore