EcoStruxure IT forum
Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-04-05 06:49 AM
I am seeing multiple [object Object] results in a basic query. These are returning from a recently created custom property called "Room Name" by a user. The custom property is a basic text field with no list or other features. Is this correct? I cannot seem to filter on 'contains value' or any filter for that matter.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-04-25 04:30 AM
Hi Nigel,
Sharing a short update here,
It appears using 'ROOM_NAME' as custom properties causing sql query problem/errors in web-client Equipment Browser. Captured a bug report, so it can be fixed in future version(s).
As a current work-around/solution, I've suggested to add/configure a new/another custom properties (like room_name or Room_name) and then Consolidate 'ROOM_NAME' to the newly configured property.
Kind regards,
Jef
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-04-15 11:30 PM
Hi Nigel,
That's right, content of the configured custom properties should basically be a text.
The following article describes custom properties in ITA:
https://community.se.com/t5/Editing-properties/Custom-properties-in-ITA/ta-p/447081
As an example, I have configured custom properties like 'Status' and 'website' for a rack and a server (in my setup). Here is an illustration of what Equipment Browser would display for the selected filters (in Show Columns):
If you are seeing unexpected entries (like [object Object]), then I guess:
it might be browser related and you might want to reload the page and/or try with cleared cache,
or it might be something with the setup (that might need to be investigated).
Kind regards,
Jef
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-04-23 07:09 AM
Hi Nigel,
Sorry, I just noticed this.
I will contact you and open an investigation ticket.
Kind regards,
Jef
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-04-25 04:30 AM
Hi Nigel,
Sharing a short update here,
It appears using 'ROOM_NAME' as custom properties causing sql query problem/errors in web-client Equipment Browser. Captured a bug report, so it can be fixed in future version(s).
As a current work-around/solution, I've suggested to add/configure a new/another custom properties (like room_name or Room_name) and then Consolidate 'ROOM_NAME' to the newly configured property.
Kind regards,
Jef
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.