the measured load exceeds the total estimated load of connected equipment

EcoStruxure IT forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT forum
  • the measured load exceeds the total estimated load of connected equipment
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
124
Jef
Admiral Jef Admiral
109
gsterling
Captain gsterling Captain
71
APC_Steve
Captain APC_Steve Captain
62
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure IT forum
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 04:28 PM . Last Modified: ‎2024-04-03 05:05 AM

0 Likes
8
895
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 04:28 PM . Last Modified: ‎2024-04-03 05:05 AM

the measured load exceeds the total estimated load of connected equipment

Good day 

Please assist

Under recommendation tab, DCO reports UPS "the measured load exceeds the total estimated load of connected equipment" I cant begin to think where to start to troubleshoot this issue.

I understand what the error is saying, however not sure where to "look" to solve.

Do i simply increase the estimated load more than measured load?

Please assist.

Regards

(CID:138808712)

Labels
  • Labels:
  • Data Center Operation
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 8
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 04:28 PM . Last Modified: ‎2024-04-03 05:05 AM

0 Likes
6
895
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 04:28 PM . Last Modified: ‎2024-04-03 05:05 AM

A few things to check, between DCO model and the actual rack itself:

 

1.Compare asset inside the rack in DCO vs actual, see if there is any server not yet modeled, or any extra equipments connected to rack PDU in that rack (I've seen stuff plugged to rpdu from phone charger,  portable dehumidifier, etc...)

 

2. Check adjusted name plate rating of assets in the rack in DCO versus actual asset's power supply rating

 

3. Check actual rack, see if there any 'cross tapping' of power to the rack PDU from outside of the rack. e.g server from next rack tapping to this particular rack's rpdu or cascaded rpdus from other racks.

 

4. Check if it is the correct measured rack PDU/BCPM (from DCE/ETL) associated in the DCO's rack PDU

 

(CID:138809173)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 04:29 PM . Last Modified: ‎2024-04-03 05:05 AM

In response to DCIM_Support
0 Likes
0
895
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 04:29 PM . Last Modified: ‎2024-04-03 05:05 AM

Thank you Christopherus... will check and feedback!

(CID:138809782)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 04:29 PM . Last Modified: ‎2024-04-03 05:05 AM

In response to DCIM_Support
0 Likes
0
895
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 04:29 PM . Last Modified: ‎2024-04-03 05:05 AM

Hi Chris

I found some "gremlins" and also some new servers that we not added to DCO. I have corrected the power (nameplate and adjusted) values - on Monday 25th Feb and still error remains. I have checked and all changes have been applied.

Is there anything else i can try ?

Thank you for effort to assist!

Kind regards

(CID:140708741)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 04:29 PM . Last Modified: ‎2024-04-03 05:05 AM

In response to DCIM_Support
0 Likes
0
895
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 04:29 PM . Last Modified: ‎2024-04-03 05:05 AM

'gremlins', interesting... 😂

I missed out to recommend checking the server to phase (L1,L2,L3) mapping, especially if you are using 3phase rack PDUs, as that may translate to estimated load on incorrect phase of the UPS.

 

Do set the preference to show all 3 phase in the tool tip at power tab when you moused over a rack / UPS, as that will help you to graphically identify the loading by phase on rack.

 

As you are looking at UPS level, that means you need to investigate every racks under that UPS, ensuring there is no such recommendations on the rack.

 

Use the power dependency view in the DCO client to investigate the estimated load, for every racks.


Also ensure you are associating the correct digital power meter or UPS reading for the UPS modle in DCO.

 

That's pretty much what I'd do.

The link to the recommendation is below.

https://sxwhelpcenter.ecostruxureit.com/display/UADCO8x/The+Measured+Load+of+the+UPS+Exceeds+the+Tot...

 

 

(CID:140708959)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 04:29 PM . Last Modified: ‎2024-04-03 05:05 AM

In response to DCIM_Support
0 Likes
0
895
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 04:29 PM . Last Modified: ‎2024-04-03 05:05 AM

Gremlins, servers that is connected to external racks and adapters that are plugged in PDUs that are not connected to any equipment LOL! 

- server to phase (L1,L2,L3) mapping = I have verified. We are using 3phase and single phase RPDU's

-Tool tip = i have options Custom properties, Recommendations, Alarms and Tags selected. I do not see Power Phase. Should i enable External Systems ? When i mouse over a server, i do see Power connections and I can see phases, L1,L2,L3.

-Ensuring there is no such recommendations on the rack. = I do not have any recommendations on the rack. Recommendation Error is coming from the UPS. Should i compare Estimated load and Measured per rack instead ?

-DCO client to investigate the estimated load, for every racks. = This will take me some time but I will get to it.

Will feedback soonest.


Thank you Chris!


(CID:140709029)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 04:29 PM . Last Modified: ‎2024-04-03 05:05 AM

In response to DCIM_Support
0 Likes
0
895
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 04:29 PM . Last Modified: ‎2024-04-03 05:05 AM

As long as you can see the phase loading when you mouse over, that will help to check which rack to narrow down.

 

If the message is only on the UPS, perhaps check if you are indeed getting the right reading of UPS associated?

The measured is peak measured for 30 days, which can be changed in preferences for the period.

 

Alternative:

If you are fairly confident on the measured peak data, especially if you have all measured rpdus, you can use 'predicted power', which is calculated from measured power multiplied by a factor. That might be easier than reviewing every rack's name plate. You can change the min/max factor multiplier to 1, if your DC condition is fairly stable.

 

Have a look here:

 

https://sxwhelpcenter.ecostruxureit.com/display/UADCO8x/About+predicted+power?queryString=predicted

 

Edit:

Gremlins, servers that is connected to external racks and adapters that are plugged in PDUs that are not connected to any equipment LOL! 

Well, that happened :'/

 

Regards,

Chris

(CID:140709087)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 04:29 PM . Last Modified: ‎2024-04-03 05:05 AM

In response to DCIM_Support
0 Likes
0
895
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 04:29 PM . Last Modified: ‎2024-04-03 05:05 AM

i found the rack that could be an issue. Its the only rack in our DC that has a negative remaining capacity. I am not sure if it could be an issue. See attached.

I have verified all equipment inside the rack. I have looked at nameplate and adjusted values all seems OK.  See below UPS error;

 

 

(CID:140709167)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 04:29 PM . Last Modified: ‎2023-10-22 09:37 PM

0 Likes
0
895
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 04:29 PM . Last Modified: ‎2023-10-22 09:37 PM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of