Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

Refridgerant Distribution Unit (RDU) not loading sensors on DCE v7.4

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • Refridgerant Distribution Unit (RDU) not loading sensors on DCE v7.4
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Cory_McDonald Champion
159
Jef
Jef Leader
114
gsterling
gsterling Mentor
77
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure IT Forum
Start a Topic
DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 04:27 PM . Last Modified: ‎2024-04-03 05:05 AM

0 Likes
11
1871
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 04:27 PM . Last Modified: ‎2024-04-03 05:05 AM

Refridgerant Distribution Unit (RDU) not loading sensors on DCE v7.4

Hi Team,

We recently reset our DCE v7.3.1 due to unavoidable issues, loading up the configuration file on new DCE v7.4 the RDU which were previously loading sensors now doesn't as shown in the images attached.

The part number for the NMC is AP9537, firmware v5.1.4 as attached and the RDU is

Kindly do we need to get DDF files sor this as well, didn't think APC equipment needed DDF.

Thank you.

(CID:138808542)

Labels
  • Labels:
  • Data Center Expert
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 11
DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 04:27 PM . Last Modified: ‎2024-04-03 05:05 AM

0 Likes
0
1869
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 04:27 PM . Last Modified: ‎2024-04-03 05:05 AM

Dear Mashwiz,

That is, you deployed from restore image a fresh DCE-7.3.1 and then immediately updated it to version 7.4.(what is the exact version)? Did I understand you correctly?

With respect.

(CID:138809138)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 04:27 PM . Last Modified: ‎2024-04-03 05:05 AM

0 Likes
0
1869
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 04:27 PM . Last Modified: ‎2024-04-03 05:05 AM

Hi Spezialist,

We have an existing DCE v7.3.1 physical server which couldn't boot up after restarting for reasons not known.

So I managed to get the configuration backup before this happened, I then proceeded to install a fresh DCE v7.3.1 on the same server.

Loaded up the configuration file then proceeded to upgrade to DCE v7.4 and that's when I discovered I coudn't see the sensors for the RDU though they were discovered.

 

(CID:138809144)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 04:27 PM . Last Modified: ‎2024-04-03 05:05 AM

0 Likes
0
1869
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 04:27 PM . Last Modified: ‎2024-04-03 05:05 AM

From your comments:

So I managed to get the configuration backup before this happened, I then proceeded to install a fresh DCE v7.3.1 on the same server.

Immediately after that, could you see the sensors of your RDU (before upgrading to version 7.4. ???)?

With respect.

(CID:138809147)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 04:27 PM . Last Modified: ‎2024-04-03 05:05 AM

0 Likes
0
1869
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 04:27 PM . Last Modified: ‎2024-04-03 05:05 AM

unfortunately didn't check this and I had limited time on site to do the installation a fresh.

Thank you.

(CID:138809600)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 04:28 PM . Last Modified: ‎2024-04-03 05:05 AM

0 Likes
0
1869
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 04:28 PM . Last Modified: ‎2024-04-03 05:05 AM

Dear Mashwiz,

From your comments:

...unfortunately didn't check this and I had limited time on site to do the installation a fresh.

The fact is that it is important and without this check it is difficult to help you with something...

With respect.

(CID:138809606)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 04:28 PM . Last Modified: ‎2024-04-03 05:05 AM

0 Likes
0
1869
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 04:28 PM . Last Modified: ‎2024-04-03 05:05 AM

Hi Spezialist,

The RDUs sensors were visible in the previous DCE v7.3, reason why I never checked after the reset. My request is to know whether DCE v7.4 has issues loading RDU sensors.

Thank you.

(CID:138809745)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 04:28 PM . Last Modified: ‎2024-04-03 05:05 AM

0 Likes
0
1869
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 04:28 PM . Last Modified: ‎2024-04-03 05:05 AM

Dear Mashwiz,

But after all, you had to check after uploading the DCE-7.3.1 configuration backup,  that all devices and their sensors are normally visible. And only then perform the upgrade to version DCE-7.4.???

Tell us, please, what exactly is the cooling device model (not the NMC version)?

Tell us please, was the DCE-7.3.1 configuration backup possibly too old (outdated), and the problem is simply in the wrong IP addresses or the SNMP community name of the cooling devices? Can you send a DCE-7.3.1 configuration backup to your analysis?

What I mean is that if no additional/custom DDF-files were used, then you should have had no problems after upgrading to DCE-7.4.??? and subsequently to the latest version of DCE-7.6.0.

With respect.

(CID:138809758)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 04:28 PM . Last Modified: ‎2024-04-03 05:05 AM

0 Likes
0
1869
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 04:28 PM . Last Modified: ‎2024-04-03 05:05 AM

Hi Spezialist,

Thank you for your prompt response.

After the upgrade, I removed all the RDU from the device list and discovered them again.

RDUs were discovered with their new IPs but can't load sensors, you have to launch the device in order to log in to it to see the status of the RDU.

Model no. is ACDA901, let me know how I can send you the configuration file. Should I send you a dropbox link?

Thank you.

(CID:138809790)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 04:28 PM . Last Modified: ‎2024-04-03 05:05 AM

0 Likes
0
1869
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 04:28 PM . Last Modified: ‎2024-04-03 05:05 AM

Dear Mashwiz,

Ok, first try to get the SNMP DDF-file for your ACDA901 cooling devices from the Device Support resource and import it to the DCE software. How to do this step by step can be seen on my screenshots:


Within a couple of business days you will receive a notification about downloading the necessary DDF-file.

Secondly, to check my suspicions, please send me to a private e-mail not the entire DCE-7.3.1 configuration backup, but only a part of it with DDF-files: this is the only /opt directory (it has a small size).

With respect.

(CID:138809803)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 04:28 PM . Last Modified: ‎2024-04-03 05:05 AM

0 Likes
0
1868
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 04:28 PM . Last Modified: ‎2024-04-03 05:05 AM

Dear Mashwiz,

Tell us, please, did you solve your problem or not?

With respect.

(CID:139693933)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 04:28 PM . Last Modified: ‎2023-10-22 03:45 AM

0 Likes
0
1868
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 04:28 PM . Last Modified: ‎2023-10-22 03:45 AM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore