This question was originally posted on DCIM Support by ADEKUNLE AGBOKE on 2019-09-12
Hi,
We have Sepam series 40, series 60 in our facility and wish to add them to DCE for remote monitoring. Is this possible? how?
If not what alternative do i have
(CID:148769331)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 10:07 PM
This answer was originally posted on DCIM Support by Valentin Kozlov on 2019-09-12
Hi!
You need to go to https://ddf.ecostruxureit.com/ page and download DDF file for your device.
Then you should upload that ddf to DCE and run discovery with appropriate IP and slave ID.
Sepam should be connected to the network via Modbus TCP.
(CID:148769405)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 10:07 PM
This answer was originally posted on DCIM Support by Valentin Kozlov on 2019-09-12
Hi!
You need to go to https://ddf.ecostruxureit.com/ page and download DDF file for your device.
Then you should upload that ddf to DCE and run discovery with appropriate IP and slave ID.
Sepam should be connected to the network via Modbus TCP.
(CID:148769405)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 10:07 PM
This comment was originally posted on DCIM Support by ADEKUNLE AGBOKE on 2019-09-13
Dear Kozlov,
Thanks. please advise on possible devices i can use to establish MODBUS TCP/IP.
(CID:148769578)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 10:07 PM
This comment was originally posted on DCIM Support by Valentin Kozlov on 2019-09-13
We usually works with SE's TSXETG100 and Link150 gateways. This devices convert Modbus protocol to ModbusTCP.
(CID:148769582)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 10:07 PM
This comment was originally posted on DCIM Support by ADEKUNLE AGBOKE on 2019-09-13
Thanks for your support. Kozlov
(CID:148769590)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 10:08 PM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.