Posted: 2020-07-05 10:08 PM . Last Modified: 2024-04-03 12:34 AM
Hi! I'm having estimated load values in measured PDUs even when the adjusted nameplate values were set to 0. Yesterday while working on this, the values were correct (no estimated values in measured PDUs), but today when I opened DCO, I found this issue.
I'd appreciate some elightenment.

(CID:148769482)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 10:08 PM . Last Modified: 2024-04-03 12:34 AM
Hello Javier.
One quick question. In the tools menu, preferences, how is the "power capacity" item set in your DCO installation? Is it set to "predictive power" like below?

If yes, then the estimated load in racks with measured power will be based on the measured power values, not the derated nameplate values in the assets themselves.
If is set to adjusted nameplate, then we have to look elsewhere.
Regards
Greg Sterling
(CID:148769797)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 10:08 PM . Last Modified: 2024-04-03 12:34 AM
It is set in "Predicted Power"
Question: With this option, in racks where there is no posibillity of measurment, the load is taken from the adjusted nameplate too?
(CID:148769800)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 10:08 PM . Last Modified: 2024-04-03 12:34 AM
Yes/Correct. If a rack does not have measurements, then the estimated load will be based on the standard nameplate or derated nameplate.
Regards
Greg Sterling
(CID:148769805)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 10:08 PM . Last Modified: 2024-04-03 12:34 AM
Thank you very much. It worked!
Kind regards
(CID:148769803)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 10:08 PM . Last Modified: 2023-10-22 04:10 AM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.
Link copied. Please paste this link to share this article on your social media post.
You’ve reached the end of your document
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.