need to incorporate LIVE PME data in DCE. How can this be done?

EcoStruxure IT forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT forum
  • need to incorporate LIVE PME data in DCE. How can this be done?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
126
Jef
Admiral Jef Admiral
111
gsterling
Captain gsterling Captain
71
APC_Steve
Captain APC_Steve Captain
65
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure IT forum
Start a Topic
Solved
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 05:29 PM . Last Modified: ‎2024-04-08 12:11 AM

0 Likes
4
1815
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 05:29 PM . Last Modified: ‎2024-04-08 12:11 AM

need to incorporate LIVE PME data in DCE. How can this be done?

Our client uses PME for energy management, but the data center admin group needs certain energy meter data points in DCE for alarming of Data Center related power issues.

Can anyone CONFIRM if this is even possible?

The problem is that some of the devices which are currently linked and monitored by PME cannot be "polled" by a second SCADA software (ie:DCE) due to networking/gateway issues. Therefore, the data MUST come from PME. 

As a possible workaround, our research showed that we can make certain data points available as  OPC DA data. Can DCE use this? Is there another way to do this?

There is a plethora of marketing collateral which presents the Struxureware ''suite''  as one big  happy, compatible family....  Help needed to make this true

 

Thanks in advance and sorry for the sarcasm

(CID:122095232)

Labels
  • Labels:
  • Data Center Expert
  • power monitoring expert
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 05:29 PM . Last Modified: ‎2024-04-08 12:11 AM

1 Like
2
1816
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 05:29 PM . Last Modified: ‎2024-04-08 12:11 AM

Hi Gilles,

 

There is no native option to pull PME data into DCE. The only way to get live data is for DCE to poll another system. This data can be in the form of either Modbus over IP or SNMP. It can communicate using HTTP as well but that is only for NetBotz devices specifically. 

 

The only way for DCE to import OPC data would be by using some sort of OPC to Modbus gateway. DCE could then add that as a modbus device. This would also take up node licenses in DCE as each device being monitored uses a node license.

 

The other option is to have DCE monitor the device directly via SNMP or Modbus and DCE can output modbus data on up to 247 slave devices if the customer has the AP95MODBUS license key.

 

Thanks,

Steve.

(CID:122095239)

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 05:29 PM . Last Modified: ‎2024-04-08 12:11 AM

1 Like
2
1817
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 05:29 PM . Last Modified: ‎2024-04-08 12:11 AM

Hi Gilles,

 

There is no native option to pull PME data into DCE. The only way to get live data is for DCE to poll another system. This data can be in the form of either Modbus over IP or SNMP. It can communicate using HTTP as well but that is only for NetBotz devices specifically. 

 

The only way for DCE to import OPC data would be by using some sort of OPC to Modbus gateway. DCE could then add that as a modbus device. This would also take up node licenses in DCE as each device being monitored uses a node license.

 

The other option is to have DCE monitor the device directly via SNMP or Modbus and DCE can output modbus data on up to 247 slave devices if the customer has the AP95MODBUS license key.

 

Thanks,

Steve.

(CID:122095239)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 05:29 PM . Last Modified: ‎2024-04-08 12:11 AM

In response to DCIM_Support
0 Likes
0
1815
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 05:29 PM . Last Modified: ‎2024-04-08 12:11 AM

Modbus data output by DCE, That is interesting. Is there a full list of other hidden features where license keys are required?

Regards,

J

(CID:122686376)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 05:29 PM . Last Modified: ‎2024-04-08 12:11 AM

In response to DCIM_Support
0 Likes
0
1816
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 05:29 PM . Last Modified: ‎2024-04-08 12:11 AM

Hi John,

 

Sorry, no. That's about it. We monitor SNMP, modbus, and NetBots based on node licenses. You can get surveillance licenses for NetBotz with cameras.

You can query DCE through the web API, check this site and the software downloads page for info. I can link them if you need...  But the only  output you can get with a license is Modbus. Sorry but no OPC, Bacnet, or other protocols. 

 

Steve

(CID:122686384)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 05:29 PM . Last Modified: ‎2023-10-22 09:32 PM

0 Likes
0
1816
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 05:29 PM . Last Modified: ‎2023-10-22 09:32 PM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore