hello.
i have question.
leak rope sensor. what's the maximum possible distance?
with netbotz 450.
thanks
(CID:110005444)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 08:09 AM . Last Modified: 2024-04-08 03:58 AM
Hi Yongjin,
Maximum distance is 100 feet. That can be using cat5 extensions before the leak rope or extending the leak rope NBES0308 itself using the extension NBES0309.
Thanks,
Steve
(CID:110005453)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 08:09 AM . Last Modified: 2024-04-08 03:58 AM
Hi Yongjin,
Maximum distance is 100 feet. That can be using cat5 extensions before the leak rope or extending the leak rope NBES0308 itself using the extension NBES0309.
Thanks,
Steve
(CID:110005453)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 08:09 AM . Last Modified: 2024-04-08 03:58 AM
Thank you!
(CID:110005516)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 08:09 AM . Last Modified: 2023-10-22 04:41 AM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.
Link copied. Please paste this link to share this article on your social media post.
You’ve reached the end of your document
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.