Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

kW and Breaker Mappings

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • kW and Breaker Mappings
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
126
Jef
Admiral Jef Admiral
111
gsterling
Captain gsterling Captain
71
APC_Steve
Captain APC_Steve Captain
65
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure IT Forum
Start a Topic
Solved
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 01:06 AM . Last Modified: ‎2024-04-09 12:43 AM

0 Likes
9
1381
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 01:06 AM . Last Modified: ‎2024-04-09 12:43 AM

kW and Breaker Mappings

I've done the sensor mapping to hundreds of breakers with great results and for some reason I cannot get a few to display properly in DCO. As you can see the device is associated from DCE and DCO is reading the values, but it doesn't show up in the power layout tab.

 

I've been troubleshooting for hours and don't see why it wont populate... So I need more eyes and brains to look at it.

(CID:105468511)

Labels
  • Labels:
  • Data Center Expert
  • Data Center Operation
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 01:06 AM . Last Modified: ‎2024-04-09 12:43 AM

0 Likes
0
1383
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 01:06 AM . Last Modified: ‎2024-04-09 12:43 AM

I looked through the user manual and stumbled upon time synchronization. I enabled DCE as the NTP server and pointed DCO at it. Problem solved. I can't confirm it was that or the reboot... Does that make sense???

(CID:105469651)

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 9
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 01:06 AM . Last Modified: ‎2024-04-09 12:43 AM

0 Likes
0
1383
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 01:06 AM . Last Modified: ‎2024-04-09 12:43 AM

Hi Jared, In general it might take at least few minutes (depending on the setup) until the 'fresh' associated power measurements being displayed in DCO. Thanks for sharing the screen captures, but unfortunately it is unclear to me what (which device) is being configured and how. It would be great, if I could see some illustrations and descriptions, so I can follow the "setup"/configuration. By the way, I've noticed apparently a cooling device have been highlighted/selected in your screen capture, if that's the object then as far as I know it is not expected to show (or associate) the power reading on CRAC's/cooling devices in DCO. Kind regards

(CID:105468696)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 01:06 AM . Last Modified: ‎2024-04-09 12:43 AM

0 Likes
0
1383
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 01:06 AM . Last Modified: ‎2024-04-09 12:43 AM

Jef, Thanks for the reply!! I've had them sitting there for days... Every single cabinet that I've put in lately is having the same issue. Even across multiple rooms on the server. I was using the middle cabinet in the 1st screen capture as an example. The second capture is the "red" PDU in the rack proving that DCE is seeing current readings. DCO is not displaying that information like 100 others in the same drawing. I've rebooted the DCO server and that didn't fix it. I thought it might have been a hung service or something. As for the cooling device, I'm in device association mode is why it's grayed out. It's irrelevant to me at this time. My setup is I have "A&B'd" ISX PDUs that have BCMs. I am polling those devices through DCE and they are feeding DCO. Devices are associated and sensors are mapped to the respective panels and breakers. There are hundreds of breakers in this "room" that are functioning correctly. Just recently had these racks populated so I tried to get them setup. Now nothing new I add is displaying kW on the power layout like the other racks.

(CID:105468758)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 01:06 AM . Last Modified: ‎2024-04-09 12:43 AM

0 Likes
0
1383
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 01:06 AM . Last Modified: ‎2024-04-09 12:43 AM

One thing I've noticed when I go into and view the breaker panel in the PDU the problem breakers are not inheriting a value in the measured column despite DCE showing a value.

Panels.png

(CID:105468761)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 01:06 AM . Last Modified: ‎2024-04-09 12:43 AM

0 Likes
0
1383
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 01:06 AM . Last Modified: ‎2024-04-09 12:43 AM

Hi Jared, Many thanks for the additional info, I guess, the problem breakers (according to the image Panels.png) would the breakers at Position 53, 54 and 55, right? I was wondering it is possible to share a screen capture of the Sensor Mapping window that shows/contains these sensors/breakers. Kind regards

(CID:105468905)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 01:06 AM . Last Modified: ‎2024-04-09 12:43 AM

0 Likes
0
1383
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 01:06 AM . Last Modified: ‎2024-04-09 12:43 AM

Let's use these for an example. DCE is showing kW fine and it is not displaying in DCO.

ISX5APNLA2729.png

SensorsISX5APNLA2729.png

(CID:105468968)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 01:06 AM . Last Modified: ‎2024-04-09 12:43 AM

0 Likes
0
1383
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 01:06 AM . Last Modified: ‎2024-04-09 12:43 AM

Hi Jared, That's strange, unfortunately I don't have a clear answer for that - usually it might take some time or even a day to see the newly configured measurements. By the way, I was wondering about the version of the running DCO. I've noticed that it might be a 7.4.x setup, right? If possible, I would suggest upgrading the product to the latest version (currently 7.5), and see if that helps. The latest version contains many enhancements, so it is worth to give it a chance. If that doesn't help, I guess the next step could be to check a backup & the logs files. Kind regards

(CID:105469151)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 01:06 AM . Last Modified: ‎2024-04-09 12:43 AM

0 Likes
0
1384
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 01:06 AM . Last Modified: ‎2024-04-09 12:43 AM

I looked through the user manual and stumbled upon time synchronization. I enabled DCE as the NTP server and pointed DCO at it. Problem solved. I can't confirm it was that or the reboot... Does that make sense???

(CID:105469651)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 01:07 AM . Last Modified: ‎2024-04-09 12:43 AM

0 Likes
0
1383
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 01:07 AM . Last Modified: ‎2024-04-09 12:43 AM

Hi Jared, That sounds really great, many thanks for sharing. Yes, in my mind both would make sense - if for some reason(s) (such as routing/network related 'disconnections') DCE "stops" sending the requests to DCO, then rebooting the server would refresh the communication. And the importance of system time synchronization is discussed here: https://dcimsupport.apc.com/display/UAOp74/The+Importance+of+System+Time+Synchronization+for+Accurat... Kind regards

(CID:105469606)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 01:07 AM . Last Modified: ‎2023-10-31 11:20 PM

0 Likes
0
1383
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 01:07 AM . Last Modified: ‎2023-10-31 11:20 PM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.