dce can not read ACRC600 unit

EcoStruxure IT forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT forum
  • dce can not read ACRC600 unit
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
125
Jef
Admiral Jef Admiral
111
gsterling
Captain gsterling Captain
71
APC_Steve
Captain APC_Steve Captain
65
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure IT forum
Start a Topic
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 12:04 AM . Last Modified: ‎2024-04-05 04:42 AM

0 Likes
11
1145
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 12:04 AM . Last Modified: ‎2024-04-05 04:42 AM

dce can not read ACRC600 unit

Hi 

I have new DCE VER 7.4.3 Intalled on castemer sit and i have on sit the new 

ACRC600 the DCE do not marck the unit as coolling and it staced on SNMP device

can i get DDF fille to fix it ?

(CID:125213674)

Labels
  • Labels:
  • Data Center Expert
  • DDF
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 11
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 12:04 AM . Last Modified: ‎2024-04-05 04:42 AM

0 Likes
2
1145
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 12:04 AM . Last Modified: ‎2024-04-05 04:42 AM

Hi Yaniv Rozenbaum,

It's very likely that there is no support for this device, because there is no information on the DEVICE SUPPORT page:

If this is the case, I recommend creating the appropriate device support request. How to do this is perfectly described in topic .

With respect.

(CID:125213710)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 12:04 AM . Last Modified: ‎2024-04-05 04:42 AM

In response to DCIM_Support
0 Likes
0
1145
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 12:04 AM . Last Modified: ‎2024-04-05 04:42 AM

The unit is Schneider INROW UNIT so i hop thay have DDF for it .

from the costemer point of view- if he Buying full system from the same vandor i do not need to have  problams monitoring the same vendor units 

 

(CID:125213735)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 12:04 AM . Last Modified: ‎2024-04-05 04:42 AM

In response to DCIM_Support
0 Likes
0
1145
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 12:04 AM . Last Modified: ‎2024-04-05 04:42 AM

Hi Yaniv Rozenbaum,

I understand you perfectly, so I hope that the support for this device still exists and you will get the necessary DDF-file.

With respect.

(CID:125213770)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 12:04 AM . Last Modified: ‎2024-04-05 04:42 AM

0 Likes
0
1145
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 12:04 AM . Last Modified: ‎2024-04-05 04:42 AM

Hi Yaniv Rozenbaum,

I today checked: I recommend as a temporary solution to try the new free software Schneider Electric StruxureOn GW 1.1.1.16 (https://struxureon.com/download-and-set-up-struxureon-gateway/).

It definitely has the support ACRC600 Series CRAC via SNMP.

With respect.

(CID:125213933)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 12:04 AM . Last Modified: ‎2024-04-05 04:42 AM

0 Likes
2
1145
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 12:04 AM . Last Modified: ‎2024-04-05 04:42 AM

From the device support page previously linked by spezialist, request the latest rev of "apc_acrd2g.xml" DDF. I believe this is the correct DDF for ACRC600 units as well. Coincidentally, I am working on making sure this DDF gets included into the next release of DCE automatically.

(CID:125214010)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 12:04 AM . Last Modified: ‎2024-04-05 04:42 AM

In response to DCIM_Support
0 Likes
0
1145
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 12:04 AM . Last Modified: ‎2024-04-05 04:42 AM

Hi Angela Clark and Yaniv Rozenbaum,

Indeed, on the above DEVICE SUPPORT page, ACRD CRAC 600 Series support for DCE-server is declared:

I hope these DDF-files are also suitable for ACRC CRAC 600 Series.

P.S.: free software Schneider Electric StruxureOn GW 1.1.1.16 is supported, however, separately for ACRC600 Series CRAC via SNMP and separately for ACRD600 Series CRAC via SNMP. It is strange that this fact is not displayed on DEVICE SUPPORT.

With respect.

(CID:125214026)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 12:05 AM . Last Modified: ‎2024-04-05 04:42 AM

In response to DCIM_Support
0 Likes
0
1145
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 12:05 AM . Last Modified: ‎2024-04-05 04:42 AM

Hi Angela Clark

I  get the fille i will test it on the 18/10

when i by on sit of the expert .

i will update you all if it is working or not .

 

(CID:126160452)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 12:05 AM . Last Modified: ‎2024-04-05 04:42 AM

0 Likes
0
1145
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 12:05 AM . Last Modified: ‎2024-04-05 04:42 AM

Hi Yaniv Rozenbaum,

Have you solved your problem or not?

With respect.

(CID:126159010)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 12:05 AM . Last Modified: ‎2024-04-05 04:42 AM

0 Likes
0
1145
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 12:05 AM . Last Modified: ‎2024-04-05 04:42 AM

Hi Yaniv Rozenbaum,

I am notifying of a very good new functionality of HELP CENTER EcoStruxture IT (DCIM Support) after its recent move and update.

I suggest that you follow Angela Clark recommendations and create a request for downloading the SNMP DDF-file for the Schneider Electric ACRD60X device. After you receive the corresponding download invitation, you can check the proposed SNMP DDF-file in conjunction with the real devices that you are using.

And after that, by going back to the Device Support page, you will get the opportunity to leave your response about whether this DDF-file works for you or not:

This will help developers and the DCIM community to make the DDF-file even better 😀.

With respect.

(CID:126159488)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 12:05 AM . Last Modified: ‎2024-04-05 04:42 AM

0 Likes
0
1145
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 12:05 AM . Last Modified: ‎2024-04-05 04:42 AM

Hi Yaniv Rozenbaum,

You have successfully solved your question or not?

With respect.

(CID:126167546)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 12:05 AM . Last Modified: ‎2023-10-22 04:29 AM

0 Likes
0
1145
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 12:05 AM . Last Modified: ‎2023-10-22 04:29 AM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore