I'm trying to configure Energy Efficiency and I'd like to know what means the errors showed when try to evaluate the Energy System. I found two different errors:
"Invalid configuration for subsystem Critical Power Distribution"
"Critical power distribution must be present, measured and connected to UPS or Switchgear"
Best regards,
Enric Climent
(CID:124527337)
Posted: 2020-07-03 11:18 PM
This answer was originally posted on DCIM Support by Rana Ajmal on 2017-09-14
Dear Enric,
The system needs a minimum energy system configuration to provide you with a calculated PUE/DCiE value. An energy system must at least include:
The below post which describes the tips for configuring Energy Efficiency.
https://dcimsupport.apc.com/questions/105464925/tips-for-configuring-energy-efficiency-
https://dcimsupport.apc.com/display/public/UADCO8x/Energy+system+configuration
BR,
Rana
(CID:124527381)