Adding Modbus Device Fails (Generac PM-SC)

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase β†’ Use quotes " " (e.g., "error 404")
  • Wildcard β†’ Use * for partial words (e.g., build*, *tion)
  • AND / OR β†’ Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short β†’ Use 2–3 relevant words , not full sentences
  • Filters β†’ Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results forΒ 
ShowΒ Β onlyΒ  | Search instead forΒ 
Did you mean:Β 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • Adding Modbus Device Fails (Generac PM-SC)
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
129
Jef
Admiral Jef Admiral
112
gsterling
Captain gsterling Captain
72
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure IT Forum
Start a Topic
Solved
DCIM_Support
Picard DCIM_Support
Picard

Posted: β€Ž2020-07-03 11:16 PM . Last Modified: β€Ž2024-04-05 04:59 AM

0 Likes
15
3356
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2020-07-03 11:16 PM . Last Modified: β€Ž2024-04-05 04:59 AM

Adding Modbus Device Fails (Generac PM-SC)

Im trying to add our generator panel to Struxureware for monitoring. I see the DDF file in struxureware and when adding the device I select the Generac PM-SC device. When the device is added it changes to failed after about 10-15 seconds and only shows a Communication link failure, no other metrics. 

I have used a Modbus TCP client to poll the device registers and successfully get the correct values back so I know my gateway is working properly. Is there any way I can see why the failure is happening or any advice when adding this device?

 

Thanks!

(CID:124527201)

Labels
  • Labels:
  • Data Center Expert
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
DCIM_Support
Picard DCIM_Support
Picard

Posted: β€Ž2020-07-03 11:16 PM . Last Modified: β€Ž2024-04-05 04:59 AM

0 Likes
9
3356
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2020-07-03 11:16 PM . Last Modified: β€Ž2024-04-05 04:59 AM

Hi Joey Harris,

If, as Rana Ajmal said, all communication settings are correct, it is very possible that your DDF-file is not suitable for your device. It's best to share the exact information about the version of the DCE-server, the version of your DDF-file and the model/type/modification of your device.

As a very good option, I suggest trying a suitable DDF-file for your device, which can be found by searching for the keyword "generac" on page DEVICE SUPPORT, for example as in the screenshot:

Always glad to answer your questions.

(CID:124527418)

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 15
DCIM_Support
Picard DCIM_Support
Picard

Posted: β€Ž2020-07-03 11:16 PM . Last Modified: β€Ž2024-04-05 04:59 AM

0 Likes
0
3356
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2020-07-03 11:16 PM . Last Modified: β€Ž2024-04-05 04:59 AM

Hi Joey,

          can you verify the slave address it should be same on both side device and DCE.

BR,

Rana

(CID:124527327)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: β€Ž2020-07-03 11:16 PM . Last Modified: β€Ž2024-04-05 04:59 AM

0 Likes
9
3357
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2020-07-03 11:16 PM . Last Modified: β€Ž2024-04-05 04:59 AM

Hi Joey Harris,

If, as Rana Ajmal said, all communication settings are correct, it is very possible that your DDF-file is not suitable for your device. It's best to share the exact information about the version of the DCE-server, the version of your DDF-file and the model/type/modification of your device.

As a very good option, I suggest trying a suitable DDF-file for your device, which can be found by searching for the keyword "generac" on page DEVICE SUPPORT, for example as in the screenshot:

Always glad to answer your questions.

(CID:124527418)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: β€Ž2020-07-03 11:16 PM . Last Modified: β€Ž2024-04-05 04:59 AM

In response to DCIM_Support
0 Likes
0
3356
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2020-07-03 11:16 PM . Last Modified: β€Ž2024-04-05 04:59 AM

Using Struxureware 7.4.3 with the Generac PM-SC DDF that I requested from this site. It is version 5. My slave address is 1 which can be confirmed by using that address in my Modbus TCP client I'm running on my laptop. I am able to successfully poll a register that contains the first generators fuel level.

The generator panel is type G and is a Generac Power Manager System Controller wired up to two generators in our utility yard. 

(CID:124527738)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: β€Ž2020-07-03 11:16 PM . Last Modified: β€Ž2024-04-05 04:59 AM

In response to DCIM_Support
0 Likes
0
3356
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2020-07-03 11:16 PM . Last Modified: β€Ž2024-04-05 04:59 AM

Hi Joey Harris,

An interesting problem... Can you share three or four commands and their output to the registers of your generator so that you can see what registers and their values are? Also, can you share your DDF-file that you mentioned? Having this information I can compare and tell you whether your DDF-file matches your generator or not.

Always glad to answer your questions.

(CID:124527891)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: β€Ž2020-07-03 11:17 PM . Last Modified: β€Ž2024-04-05 04:59 AM

In response to DCIM_Support
0 Likes
0
3356
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2020-07-03 11:17 PM . Last Modified: β€Ž2024-04-05 04:59 AM

Ive put screenshots below of my modbus utility returning values from the gateway. Its a bit hard to return anything useful when the generators are not running. Please note that these have an offset of -1 from the documentation I am referencing which I will link below

135 = coolant temp

78 = fuel level %

2583 = battery voltage

(CID:124527899)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: β€Ž2020-07-03 11:17 PM . Last Modified: β€Ž2024-04-05 04:59 AM

In response to DCIM_Support
0 Likes
0
3356
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2020-07-03 11:17 PM . Last Modified: β€Ž2024-04-05 04:59 AM

New file link

(CID:124527912)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: β€Ž2020-07-03 11:17 PM . Last Modified: β€Ž2024-04-05 04:59 AM

In response to DCIM_Support
0 Likes
0
3356
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2020-07-03 11:17 PM . Last Modified: β€Ž2024-04-05 04:59 AM

The generac DDF I recieved from this site

(CID:124527916)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: β€Ž2020-07-03 11:17 PM . Last Modified: β€Ž2024-04-05 04:59 AM

In response to DCIM_Support
0 Likes
0
3356
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2020-07-03 11:17 PM . Last Modified: β€Ž2024-04-05 04:59 AM

Hi Joey Harris,

Sorry for the delay in the answer: I'm still just studying your information. But I can already say that your DDF-file and your generator are incompatible, that's why it does not work. Why it happened, I do not know yet: at the beginning of next week I will write in more detail.

Always glad to answer your questions.

(CID:124528374)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: β€Ž2020-07-03 11:17 PM . Last Modified: β€Ž2024-04-05 04:59 AM

In response to DCIM_Support
0 Likes
0
3356
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2020-07-03 11:17 PM . Last Modified: β€Ž2024-04-05 04:59 AM

Hi Joey Harris,

As I wrote above - your DDF-file is not compatible with your generator.

For your generator, you need to use the Generac MPS Digital Control Panel (v.3) DDF-file, which you can request here on DCIM Support (see my screenshot above).

That you did not lose time, I send you this DDF-file: generac_generator_gpanel - 2 Gens_v2.7z

Always glad to answer your questions.

(CID:125208521)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: β€Ž2020-07-03 11:17 PM . Last Modified: β€Ž2024-04-05 04:59 AM

In response to DCIM_Support
0 Likes
0
3356
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2020-07-03 11:17 PM . Last Modified: β€Ž2024-04-05 04:59 AM

Awesome! I had to manually edit the file to account for the offset of -1 on all the registers but now Struxureware is reading properly!

For readings like battery voltage, the value returned by the panel should be divided by 100 to get the proper decimal place. Is there any way this can be accomplished?

Ex. 2556 / 100 = 25.56 V

(CID:125208768)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: β€Ž2020-07-03 11:17 PM . Last Modified: β€Ž2024-04-05 04:59 AM

In response to DCIM_Support
0 Likes
0
3356
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2020-07-03 11:17 PM . Last Modified: β€Ž2024-04-05 04:59 AM

Well, I corrected this error, here's the new file: generac_generator_gpanel - 2 Gens_v3.zip. Check, please, and report the result.

Always glad to answer your questions.

(CID:125208784)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: β€Ž2020-07-03 11:17 PM . Last Modified: β€Ž2024-04-05 04:58 AM

0 Likes
0
3356
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2020-07-03 11:17 PM . Last Modified: β€Ž2024-04-05 04:58 AM

The slave address is the same as Im using in my Modbus TCP client (1). I requested the latest DDF which seems to be the same version as whats currently installed in our DCE server.

(CID:124527702)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: β€Ž2020-07-03 11:18 PM . Last Modified: β€Ž2024-04-05 04:58 AM

0 Likes
0
3356
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2020-07-03 11:18 PM . Last Modified: β€Ž2024-04-05 04:58 AM

spezialist helped me out and got me the correct DDF for my device. I did find some errors with the offical DDF file such as a typo for phase A currents, values not multiplied properly (battery voltage, current, coolant readings), and all modbus registers have an offset of -1 (at least in our generator panel). Also there was an active alarm for both gen switches being set to Auto so I removed these alarm definitions. Here is what works for me in case it can help anyone else!

https://anonfile.com/e1w821ccb4/generac_generator_gpanel_-_2_Gens_v3.xml

(CID:125208818)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: β€Ž2020-07-03 11:18 PM . Last Modified: β€Ž2024-04-05 04:58 AM

0 Likes
0
3356
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2020-07-03 11:18 PM . Last Modified: β€Ž2024-04-05 04:58 AM

Hi Joey Harris,

Congratulations, wonderful work πŸ˜€.

Therefore, in order for everything to be correct, I suggest you create a Request modification for your generator so that the corrected and working DDF-file is officially available to all customers:

I hope that you will do this and always glad to answer your questions πŸ˜€.

(CID:125208856)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: β€Ž2020-07-03 11:18 PM . Last Modified: β€Ž2023-10-20 04:58 AM

0 Likes
0
3356
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2020-07-03 11:18 PM . Last Modified: β€Ž2023-10-20 04:58 AM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings Β© 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore