alarm setting best practices

EcoStruxure IT forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT forum
  • alarm setting best practices
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
124
Jef
Admiral Jef Admiral
108
gsterling
Captain gsterling Captain
71
APC_Steve
Captain APC_Steve Captain
62
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure IT forum
Solved
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 02:45 PM . Last Modified: ‎2024-04-08 01:12 AM

0 Likes
7
1234
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 02:45 PM . Last Modified: ‎2024-04-08 01:12 AM

alarm setting best practices

Is there any kind of "best practice"  documentation for settings for sensors and alarms for StruxureOn monitoring a Symmetra PX500? I'm thinking like thresholds for voltages, temps, and other things that should be monitored.

(CID:116363150)

Labels
  • Labels:
  • Asset Advisor
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 02:45 PM . Last Modified: ‎2024-04-08 01:12 AM

0 Likes
4
1234
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 02:45 PM . Last Modified: ‎2024-04-08 01:12 AM

Hi jsears,

This is not necessary, since the above-mentioned UPS is native supported by all Schneider Electric software, for example, StruxureWare DCE and StruxureOn GW. I.e., this means that all necessary Device alerts are already provided and pre-configured by the manufacturer.

I have in operation a pair of such UPSs for the sixth year and the only alert (threshold), that I setup at my discretion - Battery Temperature. The manufacturer, i.e. Schneider Electric, it is preconfigured, that if the overall temperature of the big battery array reaches 60°C, a warning (not critical) about battery overheating is generated. And one day last year, due to the fact, that this threshold is greatly overstated and is not critical in the understanding of the DCE server, three battery modules have become useless (damaged). And all because of the short circuit in the batteries in one battery module. This led to a sharp heating of all three battery modules to the boiling point of the electrolyte (>100°C). At the same time, at least six more battery modules were heated up (>70°C). All this led to the fact that the battery enclosure was covered with water vapor from overheated batteries.

In order to avoid such critical incidents in the future, I setup the threshold on the DCE server for Battery Temperature to a maximum of 38°C for one hour. If this threshold is exceeded, then a critical alert is generated, not a warning. Why 38°C? But because at a temperature, that is registered by the server DCE (via NMC2 card in UPS), the actual temperature of the batteries will already be about 48...50°C. Since the temperature sensors of the battery modules do not touch the batteries themselves, they only measure the air temperature near them 😀.

With best regards.

 

(CID:116363165)

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 7
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 02:45 PM . Last Modified: ‎2024-04-08 01:12 AM

0 Likes
4
1235
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 02:45 PM . Last Modified: ‎2024-04-08 01:12 AM

Hi jsears,

This is not necessary, since the above-mentioned UPS is native supported by all Schneider Electric software, for example, StruxureWare DCE and StruxureOn GW. I.e., this means that all necessary Device alerts are already provided and pre-configured by the manufacturer.

I have in operation a pair of such UPSs for the sixth year and the only alert (threshold), that I setup at my discretion - Battery Temperature. The manufacturer, i.e. Schneider Electric, it is preconfigured, that if the overall temperature of the big battery array reaches 60°C, a warning (not critical) about battery overheating is generated. And one day last year, due to the fact, that this threshold is greatly overstated and is not critical in the understanding of the DCE server, three battery modules have become useless (damaged). And all because of the short circuit in the batteries in one battery module. This led to a sharp heating of all three battery modules to the boiling point of the electrolyte (>100°C). At the same time, at least six more battery modules were heated up (>70°C). All this led to the fact that the battery enclosure was covered with water vapor from overheated batteries.

In order to avoid such critical incidents in the future, I setup the threshold on the DCE server for Battery Temperature to a maximum of 38°C for one hour. If this threshold is exceeded, then a critical alert is generated, not a warning. Why 38°C? But because at a temperature, that is registered by the server DCE (via NMC2 card in UPS), the actual temperature of the batteries will already be about 48...50°C. Since the temperature sensors of the battery modules do not touch the batteries themselves, they only measure the air temperature near them 😀.

With best regards.

 

(CID:116363165)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 02:45 PM . Last Modified: ‎2024-04-08 01:12 AM

In response to DCIM_Support
0 Likes
0
1234
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 02:45 PM . Last Modified: ‎2024-04-08 01:12 AM

Thank you.  I am a bit confused though.  When I go into the "Alarms" area of my StruxureON GW, There is nothing listed. When you say "that all necessary Device alerts are already provided and pre-configured by the manufacturer", what does that mean – that if some pre-configured item goes out of proper range we will get notifications even if we don't manually configure alarms?

(CID:116363221)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 02:45 PM . Last Modified: ‎2024-04-08 01:12 AM

In response to DCIM_Support
0 Likes
0
1234
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 02:45 PM . Last Modified: ‎2024-04-08 01:12 AM

Hi jsears.

Yes of course: a large number of necessary alerts is "programmed" in the NMC2 card for this UPS. Templates of these Device alerts already are in the special DDF-file signed with the digital signature on the StruxureOn GW server on the path C:\ProgramData\StruxureOn Gateway\1.0.3\ddfs\ddf_bundle\default\se-ddf.jar. And of course templates of these alert not aren't displayed in the StruxureOn GW web-interface anywhere. But, for example, on the StruxureWare DCE server they after all can be seen in the form of the long list:

And the Alarms tab on the StruxureOn GW server is intended only for setup of the user alerts/thresholds if necessary, especially if it concerns 3d party devices (not Schneider Electric).

With best regards.

(CID:116363283)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 02:45 PM . Last Modified: ‎2024-04-08 01:12 AM

In response to DCIM_Support
0 Likes
0
1234
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 02:45 PM . Last Modified: ‎2024-04-08 01:12 AM

I'm sorry, I know I'm being dense here, but the documentation for this product is really lacking in any helpful information.  Does what you just explained mean that I do not have to do anything in order for all the standard device alerts to be monitored and reported by Schneider RMS?

(CID:116365161)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 02:45 PM . Last Modified: ‎2024-04-08 01:12 AM

In response to DCIM_Support
0 Likes
0
1234
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 02:45 PM . Last Modified: ‎2024-04-08 01:12 AM

Hi jsears,

You all understood correctly.

 As can be seen from my screenshot, Symmetra PX 500 has more than 200 programmed alerts. And all these alerts are already configured in the StruxureOn GW software. Therefore, you do not need to configure anything 😀.

You can test this in practice, for example:

  1. open the front door of the IO Enclosure or the side door of the MBwD Enclosure (depending on the design of the UPS) - in SxOn GW, an information alert about open doors should occur;
  2. make a selftest UPS (from its touchscreen on the front doors of IO Enclosure) - in SxOn GW one warning and one information alerts about the selftest should occur.

With best regards.

(CID:116365170)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 02:45 PM . Last Modified: ‎2024-04-08 01:12 AM

0 Likes
0
1234
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 02:45 PM . Last Modified: ‎2024-04-08 01:12 AM

Add, please, to this post one more tag of "symmetra".

Thanks.

(CID:116363289)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 02:46 PM . Last Modified: ‎2023-10-22 04:25 AM

0 Likes
0
1234
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 02:46 PM . Last Modified: ‎2023-10-22 04:25 AM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of