DCO cannot connect to ITO

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • DCO cannot connect to ITO
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
126
Jef
Admiral Jef Admiral
111
gsterling
Captain gsterling Captain
71
APC_Steve
Captain APC_Steve Captain
65
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure IT Forum
Start a Topic
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 02:46 PM . Last Modified: ‎2024-04-08 01:12 AM

0 Likes
12
1391
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 02:46 PM . Last Modified: ‎2024-04-08 01:12 AM

DCO cannot connect to ITO

I was doing device discovery on several subnets, perhaps too many at once...
Seems like it got hung because discovery stopped working and DCO stopped responding.

When I relaunched DCO, I could no longer run Server Discoveries. I get the following error message in DCO when I start it up:
"Unable to retrieve discoveries for all ITO servers. The following errors occurred: - : Internal Server Error"

I restarted the Windows VM that ITO runs on, no change.
I restarted the Linux VM that DCO runs on, no change.

When I go into DCO > System Setup > External Systems Config and click Test, all come back OK including ITO.
I deleted and re-added the ITO server, no change. 

When I look in DCO > Planning > Data Center  and go to the Server Discoveries tab, I don't see any of the Server Discoveries I've run; nor can I create new ones.

When I do netstat -an |grep 8090, I don't see connections established on either ITO or DCO server.

 

Is there something I am overlooking here?

 

(CID:116363161)

Labels
  • Labels:
  • Data Center Operation
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 12
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 02:46 PM . Last Modified: ‎2024-04-08 01:12 AM

0 Likes
8
1391
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 02:46 PM . Last Modified: ‎2024-04-08 01:12 AM

Hi Mike Ryan,

It for you today I answered how to reboot of Linux server with ITO installed a question? I for some reason don't find the today's post on this matter...

Concerning your problem with ITO: You were precisely convinced, that all components of the ITO server normally work?

I am always glad to help.

(CID:116363180)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 02:46 PM . Last Modified: ‎2024-04-08 01:12 AM

In response to DCIM_Support
0 Likes
0
1391
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 02:46 PM . Last Modified: ‎2024-04-08 01:12 AM

Yes, I deleted the earlier question because ITO actually turned out to be on a Windows server.
I'm not sure how to check if all components of my ITO server are working normally.
All was working well until I started doing discovery on a few domains at once, Discover locked up and now I am in the situation I described above.

How shall I check whether ITO is working normally?

(CID:116363187)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 02:46 PM . Last Modified: ‎2024-04-08 01:12 AM

In response to DCIM_Support
0 Likes
0
1391
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 02:46 PM . Last Modified: ‎2024-04-08 01:12 AM

Hi Mike Ryan,

Ok, for a start, you can visit the your ITO server at the address https://ITO_server.domain:8643/ or https://ITO_server.domain:8643/DataCenterManager/ ?

On Windows server the firewall is enabled or not?

The PostgreSQL and Intel DCM system services are in a running state?

With best regards.

(CID:116363274)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 02:46 PM . Last Modified: ‎2024-04-08 01:11 AM

In response to DCIM_Support
0 Likes
0
1391
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 02:46 PM . Last Modified: ‎2024-04-08 01:11 AM

Hi Mike Ryan,

You have precisely fulfilled all requirements for installation of ITO software on Windows server?

For example from StruxureWare Data Center IT Optimize Server Requirements:

The hostname of the StruxureWare Data Center: IT Optimize/StruxureWare Data Center: Server Access server must be DNS resolvable from all StruxureWare Data Center Operation clients. 

It is recommended that StruxureWare Data Center: IT Optimize servers connected to StruxureWare Data Center Operation match the version.

Windows specific requirements:

  • IT Optimize must be installed by an Administrator level user.
  • The IT Optimize services must run as a user which has been granted the "Logon as a Service" privilege. Instructions are available here: http://technet.microsoft.com/en-us/library/cc794944(v=ws.10).aspx
  • StruxureWare Data Center: IT Optimize license must be installed on the Data Center Operation server.

With best regards.

(CID:116363342)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 02:46 PM . Last Modified: ‎2024-04-08 01:11 AM

In response to DCIM_Support
0 Likes
0
1391
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 02:46 PM . Last Modified: ‎2024-04-08 01:11 AM

Yes, I can get to https://ITO_server.domain:8643/DataCenterManager

No, on the Windows ITO server the firewall is not enabled.

PostgreSQL is not installed on my system (but EnergyCenterMySQL is up and running.)
Intel DCM is not installed on my system (but EnergyCenter is up and running.)

As far as whether everything was installed properly, I believe it was as it was all installed under direction of Schneider techs and our initial install and support were done when Schneider engineers were here.
Also, everything worked just fine until the time when I ran too many searches at once and caused it to hang.

(CID:116921087)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 02:46 PM . Last Modified: ‎2024-04-08 01:11 AM

In response to DCIM_Support
0 Likes
0
1391
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 02:46 PM . Last Modified: ‎2024-04-08 01:11 AM

Ok, then Jef Faridi really is right (read his answer).

 By the way, tell me exactly, what is your DCO version, StruxureWare ITO (with Server Access) version and Energy Suite version?

With best regards.

(CID:116921089)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 02:47 PM . Last Modified: ‎2024-04-08 01:11 AM

In response to DCIM_Support
0 Likes
0
1391
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 02:47 PM . Last Modified: ‎2024-04-08 01:11 AM

Adding to some of the comments previously mentioned.

On a windows server ITO should have two processes which are installed and running in the windows services panel. They are called "schneider electric energycenter" and "schneider electric energycenter database". Both should be present, and running.

To test whether ITO is running open a browser and browse to https://:8090/

If you get a ITO login window, then ITO services are running (at least the web service is running).

For the Intel DCM component, the previous comment post is correct in that you remote desktop to the ITO server you should be able to open a browser and browse to address http://localhost:8688/DataCenterManager/

If browsing to that address does not produce an Intel DCM window, check for the DCM services in the windows services control panel. There should be five services which start with "Intel(R)", they should all be started.

 

If none of the DCM services exist, then DCM was not installed.

The most common reason DCM is not installed when ITO is installed is when the ITO installer is executed directly from the ITO zip file which was downloaded from schneider. The proper procedure is to download the ITO zip, extract all of the contents of the zip file to a temp folder, then run the ITO installer from the temp folder.

If the ITO installer is executed from the zip file then it will not be able to find the DCM installers because they are also still in the zip file.

If DCM was not installed you can still install it manually by double clicking the "install_dcm.bat" file in the extracted temp folder. Wait for that to finish, then run the "install_vGateway.bat" file in the same temp folder. Do NOT run the DCM and vGateway exe files directly, if you do they will not be configured to talk to ITO.

 

Regards

Greg Sterling

(CID:116364277)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 02:47 PM . Last Modified: ‎2024-04-08 01:11 AM

In response to DCIM_Support
0 Likes
0
1391
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 02:47 PM . Last Modified: ‎2024-04-08 01:11 AM

Hello guys,

Thanks Greg Sterling for useful post.

And to verify from MS Windows cmd (for example, MS Windows 2012 Core or MS Windows 2016) status of all system services, belonging to the SxW ITO software, simple run this commands:

powershellquery_services.bat@echo off echo ======================================================= echo Schneider Electric StruxureWare ITO services status: sc query EnergyCenter sc query EnergyCenterMySQL echo ======================================================= echo Intel DCM and KVM services status: sc query VirtualGatewayProxy sc query DatacenterManagerServer sc query DatacenterManagerSnmp sc query DatacenterManager sc query "Intel(R) DCM Database Server"  

With best regards.

(CID:116364326)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 02:47 PM . Last Modified: ‎2024-04-08 01:11 AM

In response to DCIM_Support
0 Likes
0
1391
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 02:47 PM . Last Modified: ‎2024-04-08 01:11 AM

Thanks for posting the status check script.

(CID:116364427)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 02:47 PM . Last Modified: ‎2024-04-08 01:11 AM

0 Likes
1
1391
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 02:47 PM . Last Modified: ‎2024-04-08 01:11 AM

Hi Mike,

Based on the description, it seems you are trying to discover a very large number of networks at one go and/or the ITO server hardware configuration might be less than system requirements/expectations.That might be basically the reason for the ITO database stopped responding. 

The minimum system requirements is mentioned here:StruxureWare Data Center IT Optimize Server Requirements

It might make sense to start with few discoveries at a time and see how it goes. The network bandwidth might also be taken into account and perhaps avoiding to run large discoveries at one go. I think one of engineers have tested (some time ago) discovery of 90 networks in one go, which seemed to be beyond the capability to handle.

To test/verify the ITO installation, as described in the following page: Installing IT Optimize

Browse to the ITO-Lite client, https://localhost:8090, (default port, might be different in your setup)

Browse to the DCM server GUI to test connectivity to the Intel DCM server, http://localhost:8688/DataCenterManager/

You might also want to check if DCM and IT Optimize services running on the Windows host.

 

PS. not related to this case, if you are running DCO 8.0.2 (potentiality vulnerable for memory leak), then I would suggest upgrading the product to the latest version (currently 8.1).

Kind regards

(CID:116363396)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 02:47 PM . Last Modified: ‎2024-04-08 01:11 AM

In response to DCIM_Support
0 Likes
0
1391
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 02:47 PM . Last Modified: ‎2024-04-08 01:11 AM

Thanks!

When I checked the ITO-Lite client at https://localhost:8090/ I saw everything there was still hourglassing, even after a reboot.

I restarted the EnergyCenterMySQL and EnergyCenter services and everything came back OK on the ITO Lite client.

I restarted DCO and all looks OK.

We do frequently have issues with slow network, I think you may be onto something with that suggestion.

As I move forward, I will only do one subnet at a time and see how it goes, thanks for your help!

(CID:116363661)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 02:47 PM . Last Modified: ‎2023-10-22 01:43 AM

0 Likes
0
1391
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 02:47 PM . Last Modified: ‎2023-10-22 01:43 AM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore