My monthly StruxureOn report indicated a 5 point decrease from the previous month, but there was no explanation as to the cause of the decrease. There were no alarms. How do I determine the cause?
(CID:124527767)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 11:23 PM . Last Modified: 2024-04-05 04:57 AM
Hi jsears,
The reason for the change in the score is an increase in the battery temperature on the UPS. The battery temperature has gone from our recommended value to a higher temperature. A higher battery temperature can decrease the lifetime of the battery. This is what have caused the decrease in the score.
Thanks
Jesper Bjerregård
(CID:125213281)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 11:23 PM . Last Modified: 2024-04-05 04:57 AM
Hi jsears, thanks for posting.
Sorry to hear you're having trouble. Let's hope you find your answer here.
Kind regards Ditte
(CID:125208476)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 11:23 PM . Last Modified: 2024-04-05 04:57 AM
Hi jsears,
The reason for the change in the score is an increase in the battery temperature on the UPS. The battery temperature has gone from our recommended value to a higher temperature. A higher battery temperature can decrease the lifetime of the battery. This is what have caused the decrease in the score.
Thanks
Jesper Bjerregård
(CID:125213281)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 11:23 PM . Last Modified: 2023-10-22 04:21 AM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.
With achievable small steps, users progress and continually feel satisfaction in task accomplishment.
Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.
of