Why NBES0305 is misrecognized in NBRK0451

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • Why NBES0305 is misrecognized in NBRK0451
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
127
Jef
Admiral Jef Admiral
111
gsterling
Captain gsterling Captain
71
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure IT Forum
Start a Topic
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 09:26 AM . Last Modified: ‎2024-04-08 03:32 AM

0 Likes
5
878
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 09:26 AM . Last Modified: ‎2024-04-08 03:32 AM

Why NBES0305 is misrecognized in NBRK0451

Hi Team,

There is a misrecognition issue about NBES0305 , pls kindly help me on this .

When NBES0305 is plugged into NBRK0451 without connecting any third-party sensor , the sensor type is recognized normally as "Voltage" . But when our customer connected NBES0305 to a third-party Voltage transformer . It's weird that the sensor type of NBES0305 in AV will change into "Door" and the "Status"  is failure .

 

The secondary output of the Voltage transformer is between DC 0~5 V . And I've made our customer measure the output Voltage and its value was DC 2.2 V. Then the customer had reconnected and updated the firmware of netboz to V4.5.3 . But the phenomenon still existed.

 

it's normal when there is no sensor connected with NBES0305:

Sensor type is changed when the third-party Voltage sensor sensor is connected :

 

(CID:110010627)

Labels
  • Labels:
  • NetBotz
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 5
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 09:26 AM . Last Modified: ‎2024-04-08 03:32 AM

0 Likes
3
878
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 09:26 AM . Last Modified: ‎2024-04-08 03:32 AM

Hi Eric,

 

Have you tried another sensor? 

What version of botzware (firmware) was originally running on the 450?

Have you tried another 450 (if possible)?

Have you tried multiple ports on the 450?

Is it connected directly or through a sensor pod? Try connecting directly to the bot?

Is there anything else connected to the 450? If so, does disconnecting other components change the issue?

What happens if you simply connect a 1.5v battery to the cable, does it read a value or still change to a door?

 

Steve

 

 

(CID:110010848)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 09:26 AM . Last Modified: ‎2024-04-08 03:32 AM

In response to DCIM_Support
0 Likes
0
878
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 09:26 AM . Last Modified: ‎2024-04-08 03:32 AM

Hi Steve,

Happy Christmas to you and thanks a lot for your respond.

Because there is no extra sensor or 450 on site , customer haven't tried another sensor or 450 yet .  The sensor is connected directly to 450 and I've made customer tried different ports . The firmware version is V4.5.3 , besides ,1*NBES0308 , 1*NBES0307 were connected directly to 450  , 2*AP9335TH were connected to NBPD150  and a third-party current transformer was connected to 4-20mA input port . 

I will make the customer remove other sensors and connect a 1.5V battery to test it.

Thanks very much

Eric

(CID:110010957)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 09:26 AM . Last Modified: ‎2024-04-08 03:32 AM

In response to DCIM_Support
0 Likes
0
878
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 09:26 AM . Last Modified: ‎2024-04-08 03:32 AM

Hi Steve,

Sorry to brother you again , regarding on this issue . Our customer has adopted the following actions.

  1. Update the Netboz firmware and client version to V4.5.3 .


  1. Replace another NBES0305 0~5V cable.
  2. Then simply connect a 1.5v battery to the cable.

But once again , it was misrecognized as a " Vibration " sensor .


At Last ,our customer replaced the 1.5V battery with the 0~5V Voltage transformer again, it's werid that this time it was misrecognized as a "Temperature  sensor" .


I guess maybe it's a bug issue about Netboz . I am considering whether I have to replace another Netboz for the customer . Could you please help me on this issue .


Thanks very much

Eric

 

(CID:110014470)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 09:26 AM . Last Modified: ‎2024-04-08 03:32 AM

In response to DCIM_Support
0 Likes
0
878
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 09:26 AM . Last Modified: ‎2024-04-08 03:32 AM

Hi Steve,

Could you please take a look at this issue about NBES0305.

I've purchased 1*NBES0305 and tested in lab.

Netboz : NBRK0550      Firmware : V4.5.3     Sensor: NBES0305 and a 1.5V battery


Test  procedure as below:

1:Connect only NBES0305 to common sensor port1 first  . (Without battery )

Sensor type and value displayed in AV are normal.

 

   

2:Connect the 1.5V battery (Red wire + and Black wire - )

Then sensor type changed automatically 


3: I tried on different port3 and port6. The error still occurs .

4:Then I downgrade the firmware of Netboz to V4.4.0 . But the phenomenon is exactly the same with above.

Any help ,  appreciated.

Eric

(CID:111939502)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 09:26 AM . Last Modified: ‎2023-10-22 04:20 AM

0 Likes
0
878
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 09:26 AM . Last Modified: ‎2023-10-22 04:20 AM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.