Posted: 2020-07-03 12:56 PM . Last Modified: 2024-04-08 01:47 AM
(CID:111415671)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 12:56 PM . Last Modified: 2024-04-08 01:47 AM
Hi Bill,
The SNMP V3 phrases are based upon user name and password for the appliance itself.

Once you've created one and their password, go to SNMP version 3 configuration and select that user and add him:

It's just that simple.
Steve
(CID:111415678)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 12:56 PM . Last Modified: 2024-04-08 01:47 AM
Steve;
I have two unique phrases for snmpv3. Where do the two of them go? I could put one of them under the user password slot, but that still leaves the second.
Thanks
(CID:111938161)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 12:57 PM . Last Modified: 2024-04-08 01:47 AM
Hi Bill,
In NetBotz, there is only the one password / passphrase. If you're using for instance MD5 and DES, both protocols would need to use the same passphrase. I've configured and tested this in a free version off iReasoning and I am able to get results:

Here I use the "snmp_v3_user" for user name and "my_long_v3_SNMP_password" for both passphrases.
Steve
(CID:111938158)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 12:57 PM . Last Modified: 2023-10-22 04:19 AM