What's this mean, and how do I fix it?

EcoStruxure IT forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT forum
  • What's this mean, and how do I fix it?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
124
Jef
Admiral Jef Admiral
110
gsterling
Captain gsterling Captain
71
APC_Steve
Captain APC_Steve Captain
65
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure IT forum
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 04:51 AM . Last Modified: ‎2024-04-08 11:32 PM

0 Likes
3
723
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 04:51 AM . Last Modified: ‎2024-04-08 11:32 PM

What's this mean, and how do I fix it?

Critical:

The Disk Array write cache on server ISXCentral is disabled.

 

Please see the diagnostic information below. If a scheduled BBU calibration will start soon or is in progress, you may disregard this message. Otherwise, please contact Data Center Expert Support for assistance correcting this state as soon as possible.

 

With a disabled write cache, system performance will be greatly reduced resulting in possible data loss and software failure.

 

Diagnostic Information:

ERROR:BBU Current Cache Policy value is WriteThrough but should be WriteBack.

WARNING:Replace BBU battery. Full charge capacity is low.

INFO:BBU battery capacity is 25.89% (Full Charge is 492 of the 1900 mAh Design Rating).

INFO:BBU calibration was last performed Fri 05/20/2016 11:52:59 EDT and is next scheduled for Thu 08/18/2016 11:52:59 EDT based on RAID clock current reading of 08/03/2016 07:43:50.

(CID:106892043)

Labels
  • Labels:
  • Data Center Expert
Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
  • All forum topics
  • Previous Topic
  • Next Topic
Replies 3
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 04:51 AM . Last Modified: ‎2024-04-08 11:32 PM

0 Likes
0
723
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 04:51 AM . Last Modified: ‎2024-04-08 11:32 PM

Hi Chris,

 

The RAID array on the physical DCE enterprise server has a battery which loses charge potential as time goes on (usually 2-3 years) and must be replaced.  The reason this is a critical alarm within DCE is that the RAID controller will change the way data is written to the hard drives when the battery potential is low.  On a loaded system this will cause DCE to not be able to write data to the drives fast enough and cause DCE to overload and potentially crash.

 

I believe this issue can be addressed by calling tech support to schedule getting a battery replacement and instructions on how to do so.

 

-Scott

(CID:106892047)

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 04:51 AM . Last Modified: ‎2024-04-08 11:32 PM

0 Likes
0
723
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 04:51 AM . Last Modified: ‎2024-04-08 11:32 PM

Hi Chris,

 

As the message states, the raid battery is low. If the system is running a battery test which it will do intermittently, this may be normal. If it is not running a test, then the battery is low. 

 

If if the battery is low because of age or use, it may need to be replaced. You will have to verify the issue and warranty with tech support. If it is under warranty we can replace the battery, if not, you wil have to purchase a new one from Dell. 

 

Is is there an issue with the server's operation?  

 

Steve. 

(CID:106892048)

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 04:51 AM . Last Modified: ‎2023-10-31 11:43 PM

0 Likes
0
723
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 04:51 AM . Last Modified: ‎2023-10-31 11:43 PM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of