Virtual sensor reading unplugged

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • Virtual sensor reading unplugged
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
126
Jef
Admiral Jef Admiral
111
gsterling
Captain gsterling Captain
71
APC_Steve
Captain APC_Steve Captain
65
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure IT Forum
Start a Topic
Solved
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 03:04 AM . Last Modified: ‎2024-04-09 12:04 AM

0 Likes
8
1264
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 03:04 AM . Last Modified: ‎2024-04-09 12:04 AM

Virtual sensor reading unplugged

Hi

I have Netbotz temperature sensors added to a virtual sensor but it goes unplugged all the time. i have looked to see if its maybe the sensors losing connection but it doesn't. What else can cause the virtual sensor to show unplugged ?

Thank you

(CID:106204837)

Labels
  • Labels:
  • Data Center Expert
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 03:04 AM . Last Modified: ‎2024-04-09 12:04 AM

0 Likes
6
1264
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 03:04 AM . Last Modified: ‎2024-04-09 12:04 AM

Hi Quinton,

 

What are you using to create this virtual sensor? If it's NetBotz sensors, I have seen instances where one of the sensors used to create the virtual sensor does not respond on every post. This could cause something similar to what you're seeing.

 

Are they SNMP values, NetBotz, or Modbus sensors used to create the virtual sensor? If you run a report on the sensors that make up the virtual sensor and the virtual sensor itself, do you see values for each sensor for all periods? How many do you have and are they all doing this?

 

Steve

(CID:106204844)

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 8
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 03:04 AM . Last Modified: ‎2024-04-09 12:04 AM

0 Likes
6
1265
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 03:04 AM . Last Modified: ‎2024-04-09 12:04 AM

Hi Quinton,

 

What are you using to create this virtual sensor? If it's NetBotz sensors, I have seen instances where one of the sensors used to create the virtual sensor does not respond on every post. This could cause something similar to what you're seeing.

 

Are they SNMP values, NetBotz, or Modbus sensors used to create the virtual sensor? If you run a report on the sensors that make up the virtual sensor and the virtual sensor itself, do you see values for each sensor for all periods? How many do you have and are they all doing this?

 

Steve

(CID:106204844)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 03:04 AM . Last Modified: ‎2024-04-09 12:04 AM

In response to DCIM_Support
0 Likes
0
1264
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 03:04 AM . Last Modified: ‎2024-04-09 12:04 AM

I'm using DCE to create the virtual sensors and it consists of the netbotz temperature sensors they are netbotz sensors, when i generate the sensor history report for those sensors I don't see any break in the graph where any of them might have disconnected. Ive had this issues before but it has gone away now its back and not on all just a selected few. Strange is when i say edit on this virtual sensor and then ok the value returns but a few mins later its back as unplugged

(CID:106204846)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 03:04 AM . Last Modified: ‎2024-04-09 12:04 AM

In response to DCIM_Support
0 Likes
0
1264
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 03:04 AM . Last Modified: ‎2024-04-09 12:04 AM

Quinton, Can you verify the time settings on the DCE server and NetBotz are the same? Are you using multiple NetBotz or just multiple sensors from the same NetBotz appliance? Steve

(CID:106204848)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 03:04 AM . Last Modified: ‎2024-04-09 12:04 AM

In response to DCIM_Support
0 Likes
0
1264
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 03:04 AM . Last Modified: ‎2024-04-09 12:04 AM

Steven I checked the unit and the time is ahead of the DCE server. I'm using multiple sensors from this one Netbotz unit. Why would humidity sensors on the same unit not do the same thing on DCE its from the same appliance? Its only the temperature virtual sensor doing this

(CID:106204893)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 03:05 AM . Last Modified: ‎2024-04-09 12:04 AM

In response to DCIM_Support
0 Likes
0
1264
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 03:05 AM . Last Modified: ‎2024-04-09 12:04 AM

Hi Quinton, The posts from the NetBotz appliance may not include all data from every sensor. Add to that the fact that the virtual sensors have a different time that they are calculated and posted, there are a number of variables that could cause the DCE server to not see the sensors properly. As for times, I have also seen issues where a NetBotz appliance may post surveillance for instance. The NetBotz appliance in this case is ahead of DCE in the time setting. If you look for the images for the last hour you will not see it because DCE sees the time as in the future. If you check surveillance for a time frame including the future, you will see the images. That's why I'm thinking the time may be effecting what we see here. Can you sync them up and see if it helps? Steve

(CID:106205013)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 03:05 AM . Last Modified: ‎2024-04-09 12:04 AM

In response to DCIM_Support
0 Likes
0
1264
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 03:05 AM . Last Modified: ‎2024-04-09 12:04 AM

Hi Steven I changed the time settings and it looks like it helped. Thank you

(CID:106205104)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 03:05 AM . Last Modified: ‎2024-04-09 12:04 AM

In response to DCIM_Support
0 Likes
0
1264
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 03:05 AM . Last Modified: ‎2024-04-09 12:04 AM

Great to hear Quinton...so it was just the time then. Thanks for the update, Steve

(CID:106205137)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 03:05 AM . Last Modified: ‎2023-10-31 11:41 PM

0 Likes
0
1264
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 03:05 AM . Last Modified: ‎2023-10-31 11:41 PM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore