TLS1.2 or 1.3 to send e-mail

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • TLS1.2 or 1.3 to send e-mail
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
126
Jef
Admiral Jef Admiral
111
gsterling
Captain gsterling Captain
71
APC_Steve
Captain APC_Steve Captain
65
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure IT Forum
Start a Topic
markus.albisser
Ensign markus.albisser
Ensign

Posted: ‎2025-03-18 07:17 AM

0 Likes
8
997
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-03-18 07:17 AM

TLS1.2 or 1.3 to send e-mail

Dear all

 

We try to configure e-mail settings out of the EcoStruxure IT Datacenter Expert. The requirement here is that we have to use either TLS1.2 or 1.3. But in the configuration, I only have the option of STARTTLS, which is not accepted by our mail provider. 

 

Is there a schedule when native TLS1.2 or 1.3 would be implemented? Actually we are on the version 8.3.0.

 

Thanks a lot

Markus

Labels
  • Labels:
  • Data Center Expert
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 8
JLehr
Sisko JLehr Sisko
Sisko

Posted: ‎2025-03-20 08:23 AM

0 Likes
0
964
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-03-20 08:23 AM

Hi @markus.albisser,

 

The Security policy configured in the desktop client System > Server Administration Settings > Server Access > Security Policy option governs that.

 

There's a help center article that has a link to security policy definitions from Red Hat.

 

You'll see that the Default security policy allows TLS 1.2 annd 1.3 protocols.

 

Reply

Link copied. Please paste this link to share this article on your social media post.

markus.albisser
Ensign markus.albisser
Ensign

Posted: ‎2025-03-20 09:00 AM

0 Likes
0
940
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-03-20 09:00 AM

Hi @JLehr 

 

Thank you for your input. I checked the Security Policy Option, we have it set to "Future". According to the documentation it should support TLS1.2 and TLS1.3.

 

But I am not sure if I formulated my question correctly. Here I am not talking about the web access to the server, it is more how to send e-mails. And when I configure System -> Server Administration Settings -> E-mail Settings, I can use the checkbox for "Secure SMTP". But here it tells that the STARTTLS extension is needed. And when I read through the documentation, the initial mail connection is in plain text before the client/server starts the handshake for the encryption cypher. And this is the point that our provider does not accept any plaintext connection, therefore it does not accept STARTTLS. The aim is that the client directly goes into a handshake for TLS1.2 or 1.3 with the server. 

 

Based on this one I am not sure if the DCE supports this one.

 

Thank you

Markus

Reply

Link copied. Please paste this link to share this article on your social media post.

markus.albisser
Ensign markus.albisser
Ensign

Posted: ‎2025-03-27 11:05 PM

0 Likes
0
894
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-03-27 11:05 PM

Dear community

 

I just want to ask if someone knows more about the encrypted mail sending here, instead of STARTTLS. Of course also the question again @JLehr , if I probably misunderstood your feedback?

 

Thanks a lot

Markus

Reply

Link copied. Please paste this link to share this article on your social media post.

JLehr
Sisko JLehr Sisko
Sisko

Posted: ‎2025-03-31 10:39 AM

0 Likes
0
863
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-03-31 10:39 AM

Hi @markus.albisser,

 

We're looking into this further.

 

 

Reply

Link copied. Please paste this link to share this article on your social media post.

JLehr
Sisko JLehr Sisko
Sisko

Posted: ‎2025-03-31 11:10 AM

1 Like
1
859
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-03-31 11:10 AM

Hi Again @markus.albisser,

 

I misspoke. I apologize for that. DCE only supports secure mail via STARTTLS.

 

A feature request was logged to support a TLS negotiation option without STARTTLS, where DCE would negotiate TLS upon connecting to the SMTP server.

Reply

Link copied. Please paste this link to share this article on your social media post.

markus.albisser
Ensign markus.albisser
Ensign

Posted: ‎2025-08-26 06:01 AM

In response to JLehr
0 Likes
0
299
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-08-26 06:01 AM

Hi Sisko

 

I just want to ask if, in the mean time since end of March, there is already a newer version available which supports a full TLS negotiation? If not, is there any timeline when this would be possible?

 

Many thanks

Markus

Reply

Link copied. Please paste this link to share this article on your social media post.

markus.albisser
Ensign markus.albisser
Ensign

Posted: ‎2025-09-09 09:33 PM

0 Likes
0
221
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-09-09 09:33 PM

Hi @JLehr , just want to ask if there is already an ETA given for this feature request, to integrate the native TLS authentication?

Reply

Link copied. Please paste this link to share this article on your social media post.

JLehr
Sisko JLehr Sisko
Sisko

Posted: ‎2025-09-10 03:26 AM

0 Likes
0
219
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-09-10 03:26 AM

Hi @markus.albisser,

 

I logged the request. There is no ETA at this time.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore