Symmetra PX250/500: how to add the temperature of individual battery modules string in DCE

EcoStruxure IT forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results forΒ 
ShowΒ Β onlyΒ  | Search instead forΒ 
Did you mean:Β 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT forum
  • Symmetra PX250/500: how to add the temperature of individual battery modules string in DCE
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
124
Jef
Admiral Jef Admiral
110
gsterling
Captain gsterling Captain
71
APC_Steve
Captain APC_Steve Captain
64
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure IT forum
DCIM_Support
Picard DCIM_Support
Picard

Posted: β€Ž2020-07-04 05:10 PM . Last Modified: β€Ž2024-04-05 12:00 AM

0 Likes
13
1943
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2020-07-04 05:10 PM . Last Modified: β€Ž2024-04-05 12:00 AM

Symmetra PX250/500: how to add the temperature of individual battery modules string in DCE

Hi all!

So, due to the permanent aging of the battery in the Symmetra PX250/500 series UPS, these battery modules began to often fail ☹️. Practically malfunctions of the battery modules lead to their overheating. If we rely only on the built-in Device Alarms this UPS series, DCE software will inform us of the overheating of the battery module with a warning (not critical) with its exact location. For example:

The battery temperature is above ambient +20 degrees C or above 50 degrees C. Located on Battery enclosure 1 level 3 pos ABC.

Since this Device Alarm is only a warning, not the fact that its appearance quickly react staff. As a result, due to the very high temperature of the battery modules for a long time, they are damaged. To what it can lead I already described in topic . 

Therefore, as I described in the above mentioned topic, I created in the DCE software for the Battery Temperature sensor of this UPS an acceptable for me сritical Threshold Alarms. Thus, the service personnel quickly reacts to battery failures and does not wait until their temperature is high, for example, no more than 38...40 Б and regardless of the ambient temperature.

But since the above mentioned device sensor is one and there are a lot of battery modules in UPS enclosures, it is necessary for the service personnel to determine by themselves on the UPS LCD touchscreen which battery modules string is overheated and faulty?

Note: this UPS series can have up to eight battery enclosures, each of which can have up to eight battery levels with six battery modules each (two battery modules strings in each of three battery modules).

I was a bit surprised when I found out, that with SNMP protocol this series of UPSs has the ability to indicate the current temperature of each battery modules string. In addition, using the same SNMP protocol, you can find out the UPS Internal Temperature (not the batteries temperature, but the ambient temperature near the MIM and RIM, i.e. the UPS controllers). Why DDF-team did not include this useful information in the corresponding DDF-file(s) for DCE software for Symmetra PX250/500 UPS series is unclear...

First I wanted to use the standard way to add the required OIDs using the Supplemental OIDs option in DCE software. But I did not succeed, because it was impossible to specify a multiplier for the temperature value.

Therefore, I developed my own small DDF-file "APC Symmetra PX 250/500 Battery Modules Temperature", which, after importing into the DCE software, adds temperature sensors for the individual battery modules string and the internal temperature of the UPS. For example:

Then I just added the corresponding Threshold Alarms to each new temperature sensors and set it up like this:


The main thing here is that you must specify Yes for Return To Normal Requeres User Input.

The sequence of actions of the staff is very simple. In the event of this critical alarm, personnel must remove the required battery modules string from the UPS battery enclosure: its exactly location is indicated in the critical alarm (this is clearly seen in the screenshot above). After that, the temperature sensor of this battery modules string switches to the Unplugged state with the battery type "BatteryNotRecognized". Then the personnel in the DCE software simply make a manual Resolved state for this critical alarm and that's it πŸ˜€.

 

(CID:130682722)

Labels
  • Labels:
  • Data Center Expert
  • DDF
  • Tags:
  • symmetra
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 13
DCIM_Support
Picard DCIM_Support
Picard

Posted: β€Ž2020-07-04 05:10 PM . Last Modified: β€Ž2024-04-05 12:00 AM

0 Likes
0
1943
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2020-07-04 05:10 PM . Last Modified: β€Ž2024-04-05 12:00 AM

Hi spezialist,

Thanks for this information. Please submit your DDF changes to Device Support so they can be officially incorporated into the supported DDF. http://sxwhelpcenter.ecostruxureit.com/devices

Best regards,

Jackie

(CID:130682812)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: β€Ž2020-07-04 05:10 PM . Last Modified: β€Ž2024-04-05 12:00 AM

0 Likes
0
1942
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2020-07-04 05:10 PM . Last Modified: β€Ž2024-04-05 12:00 AM

Dear Jackie Lehr,

Of course, I did so, but unfortunately, since May 4, I have not received any feedback:

Very thanks for the support.

(CID:131960308)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: β€Ž2020-07-04 05:10 PM . Last Modified: β€Ž2024-04-05 12:00 AM

0 Likes
0
1942
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2020-07-04 05:10 PM . Last Modified: β€Ž2024-04-05 12:00 AM

Hi spezialist,

The device support team is working on requests as quickly as possible. It usually takes 4 - 6 weeks. Work is in progress to improve the process. We appreciate your patience in the meantime.

Best,

Jackie

(CID:131960582)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: β€Ž2020-07-04 05:11 PM . Last Modified: β€Ž2024-04-05 12:00 AM

0 Likes
0
1942
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2020-07-04 05:11 PM . Last Modified: β€Ž2024-04-05 12:00 AM

Ok, very thanks for the support.

(CID:131960593)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: β€Ž2020-07-04 05:11 PM . Last Modified: β€Ž2024-04-05 12:00 AM

0 Likes
0
1942
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2020-07-04 05:11 PM . Last Modified: β€Ž2024-04-05 12:00 AM

I'm having similar issue and trying to find OID's that can measure battery temperature inside enclosure/level/position to monitor them (had few batteries with +45^C temperature), but I'm unable to find any OID's related to that.

Could anyone provide me with correct OID? Running Symmetra PX500 with 3 full enclosures.

(CID:137110261)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: β€Ž2020-07-04 05:11 PM . Last Modified: β€Ž2024-04-05 12:00 AM

0 Likes
0
1942
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2020-07-04 05:11 PM . Last Modified: β€Ž2024-04-05 12:00 AM

Dear Just User,

To begin with, you can look and find overheated battery modules on the Symmetra PX250/500 UPS touch screen display. Have you tried it?

With respect.

(CID:137110270)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: β€Ž2020-07-04 05:11 PM . Last Modified: β€Ž2024-04-05 12:00 AM

0 Likes
0
1942
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2020-07-04 05:11 PM . Last Modified: β€Ž2024-04-05 12:00 AM

Thank you for fast reply. Yes, I can get required information from the touch screen, but the idea is to read that information using SNMP and write a script to be used in Nagios to monitor it.

That's why those OID's are interesting, as you wrote "with SNMP protocol this series of UPSs has the ability to indicate the current temperature of each battery modules string" (as I have been unable to find them)

(CID:137110283)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: β€Ž2020-07-04 05:11 PM . Last Modified: β€Ž2024-04-05 12:00 AM

0 Likes
0
1943
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2020-07-04 05:11 PM . Last Modified: β€Ž2024-04-05 12:00 AM

Dear Just User,

Ok, below are the required SNMP OID's with a brief explanation:

.1.3.6.1.4.1.318.1.1.1.4.1.4.0 - UPS Internal Temperature
.1.3.6.1.4.1.318.1.1.1.13.3.2.1.9 - *0.1 Battery Temperature (arrays start from 1 to 16 for all enclosure and levels)
.1.3.6.1.4.1.318.1.1.1.13.3.2.1.7 - Battery Type (arrays start from 1 to 16 for all enclosure and levels)
.1.3.6.1.4.1.318.1.1.1.13.3.2.1.2 - Battery Level (arrays start from 1 to 8 for all enclosure and levels)
.1.3.6.1.4.1.318.1.1.1.13.3.2.1.1 - Battery Enclosure (arrays start from 1 to 8 for all enclosure)

The same information can be found in the official document PowerNet MIB v4.2.6

I hope this is what you need.

With respect.

(CID:137110297)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: β€Ž2020-07-04 05:11 PM . Last Modified: β€Ž2024-04-05 12:00 AM

0 Likes
0
1943
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2020-07-04 05:11 PM . Last Modified: β€Ž2024-04-05 12:00 AM

Omg, that's exactly what I was looking for. I believe it was my mistake that newest powernet I could find was v4.1.0, there's no mention about it in there.

Thank you so much!

(CID:137110303)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: β€Ž2020-07-04 05:11 PM . Last Modified: β€Ž2024-04-05 12:00 AM

0 Likes
0
1943
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2020-07-04 05:11 PM . Last Modified: β€Ž2024-04-05 12:00 AM

Ok, I'm glad this my tip was helpful to you πŸ˜€.

(CID:137110306)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: β€Ž2020-07-04 05:11 PM . Last Modified: β€Ž2024-04-05 12:00 AM

0 Likes
0
1943
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2020-07-04 05:11 PM . Last Modified: β€Ž2024-04-05 12:00 AM

Hey spezialist, thanks for sharing this useful information! πŸ˜€

(CID:137110791)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: β€Ž2020-07-04 05:12 PM . Last Modified: β€Ž2024-04-05 12:00 AM

0 Likes
0
1943
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2020-07-04 05:12 PM . Last Modified: β€Ž2024-04-05 12:00 AM

Thank you for your appreciation, but unfortunately =SE= has not yet implemented the above mentioned improvements in DCE software ☹️.

In addition, as I wrote in topic , the battery age for Symmetra PX250/500 is still not displayed in DCE software. In my DDF-file, I also successfully implemented it πŸ˜€.

With respect.

(CID:137110849)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: β€Ž2020-07-04 05:12 PM . Last Modified: β€Ž2023-10-22 04:05 AM

0 Likes
0
1943
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2020-07-04 05:12 PM . Last Modified: β€Ž2023-10-22 04:05 AM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings Β© 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of