Posted: 2020-07-05 11:21 PM . Last Modified: 2024-04-03 12:09 AM
Dear team,
Ihave installed APC Symmetra PX 48KW and customer is using AKCP Pro Server monitoring solution, they wanted to get UPS logs and measurements from UPS, Your kind support is required for this solution.Server data sheet is attached below.
https://s3-us-west-2.amazonaws.com/akcp-downloads/AKCP-ProServer/APS+.pdf
Looking forward for your prompt response.
MS
(CID:151063557)
Dear Muhammad,
Symmetra PX 48 KW Network Management Card(NMC) supports SNMP version 1, 3 and SNMP Traps in order to be integrated with Network Management Systems(NMS).
SNMP and SNMP traps can be configured on the NMC web interface as per the NMS system requirements.
Symmetra PX 48 KW NMC Management Information Base(MIB) is available to be downloaded from the below link:
https://www.apc.com/shop/in/en/products/POWERNET-MIB-V4-3-1/P-SFPMIB431
If you are looking for SNMP OIDs of Symmetra PX 48 KW apart from MIB file for reading the UPS Measurements, then you can use any freeware MIB browser and poll the UPS NMC to get the required OIDs.
Step 1: Download the SNMP MIB Browser from the below link:
http://ireasoning.com/download/mibpro/setup.exe
Step 2: Install the MIB Browser
Step 3: Launch the MIB Browser and Load MIB File of device
Step 4: Once the MIB file is loaded, please type the IP Address of the device and Click on Advance option, and type the details such as community string name: public as shown below in the screen shot.
Read Community: public or type the configured community string name
And then click on Ok
Step 5: You can then navigate to the tree as shown below for the device to find the specific OIDs.
For SNMP traps which are configurable, traps are initiated or sent from the NMC itself to NMS. So no specific SNMP OIDs.
I hope this helps.
(CID:151063583)
Dear Muhammad,
I hope this helps.
(CID:151063583)
Thanks alot for your support.
(CID:151584887)
Posted: 2020-07-05 11:21 PM . Last Modified: 2023-10-22 04:04 AM