Struxureware ITO and DCO not communicating...any resolution?

EcoStruxure IT forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT forum
  • Struxureware ITO and DCO not communicating...any resolution?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
124
Jef
Admiral Jef Admiral
110
gsterling
Captain gsterling Captain
71
APC_Steve
Captain APC_Steve Captain
65
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure IT forum
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 06:57 AM . Last Modified: ‎2024-04-10 01:50 AM

0 Likes
9
883
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 06:57 AM . Last Modified: ‎2024-04-10 01:50 AM

Struxureware ITO and DCO not communicating...any resolution?

(CID:82640984)

Labels
  • Labels:
  • Data Center Operation
  • Tags:
  • IT Optimize
Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
  • All forum topics
  • Previous Topic
  • Next Topic
Replies 9
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 06:57 AM . Last Modified: ‎2024-04-10 01:50 AM

0 Likes
0
883
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 06:57 AM . Last Modified: ‎2024-04-10 01:50 AM

I'm trying to integrate Struxureware Operations 7.3.6 with Struxureware ITO client downloaded from SXW DCO 64 bit 7.3.6. As per snapshots configuration on Windows 2008 server seems to be okay as DCM on Windows 2008 is opening fine. I checked the services as well and all running okay. As the Windows 2008 is running on my laptop as VM so firewall shouldn't be an issue. I tried running sudo sed -i -e "s/^#%sudo/%sudo/g" /etc/sudoers.d/itodiscovery Just in case we can loosen the security between the two but nothing works... Any solution to this...

(CID:82640988)

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 06:57 AM . Last Modified: ‎2024-04-10 01:50 AM

0 Likes
0
884
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 06:57 AM . Last Modified: ‎2024-04-10 01:50 AM

Hi Vineet,

 

Seems like the ITO server is running as you also describe. The reminder of the integration must be done from the DCO client. You can find some information regarding external system configuration and viewing data from the following links: Configuring external system integration & Viewing external system data

There are more related information to be found at the bottom of the documentation page as links.

Hopefully this clarifies otherwise please don't hesitate to get back. 

 

/Søren

(CID:82641016)

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 06:58 AM . Last Modified: ‎2024-04-10 01:50 AM

0 Likes
1
884
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 06:58 AM . Last Modified: ‎2024-04-10 01:50 AM

Hi I have done the configurations in SXW Ops External device configurations as well and each time I click on test with the IP address of the ITO server SXW DCO VM is not able to detect it.

 

(CID:82641022)

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 06:58 AM . Last Modified: ‎2024-04-10 01:49 AM

In response to DCIM_Support
0 Likes
0
884
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 06:58 AM . Last Modified: ‎2024-04-10 01:49 AM

Hi, and have you tried if there are network connectivity between the 2 servers. Using the console of the DCO server and then trying to ping the ITO server? And you have followed the install guide for ITO? http://dcimsupport.apc.com/display/UAOps73/Installing+IT+Optimize The port that is being used by default by ITO is 8090 and that port must be opened in the firewall if any. (Once ITO server is running it uses the following ports for discoveries: http://dcimsupport.apc.com/display/UAOps73/StruxureWare+Data+Center+IT+Optimize+firewall+and+port+re... )

(CID:83230738)

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 06:58 AM . Last Modified: ‎2024-04-10 01:49 AM

0 Likes
3
884
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 06:58 AM . Last Modified: ‎2024-04-10 01:49 AM

Hi Finally the riddle is resolved and I have enclosed my findings in this Word document. So that all can benefit. The issue was in the way Windows 2008 server sets the Domain Firewall policy and finally all is connected fine.

https://dl.dropboxusercontent.com/u/104815007/ITO%20to%20DCO%202.docx

 

(CID:83230735)

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 06:58 AM . Last Modified: ‎2024-04-10 01:49 AM

In response to DCIM_Support
0 Likes
0
884
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 06:58 AM . Last Modified: ‎2024-04-10 01:49 AM

Great to hear! Would it be possible for you to post your findings directly in the community as an answer. That would be great for future reference?

(CID:83230739)

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 06:58 AM . Last Modified: ‎2024-04-10 01:49 AM

In response to DCIM_Support
0 Likes
0
884
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 06:58 AM . Last Modified: ‎2024-04-10 01:49 AM

How do I put it on community?

(CID:83656706)

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 06:58 AM . Last Modified: ‎2024-04-10 01:49 AM

In response to DCIM_Support
0 Likes
0
884
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 06:58 AM . Last Modified: ‎2024-04-10 01:49 AM

You could edit the answer or create a new answer to this thread to include the information from the document.

(CID:83656783)

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 06:58 AM . Last Modified: ‎2023-10-31 11:37 PM

0 Likes
0
884
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 06:58 AM . Last Modified: ‎2023-10-31 11:37 PM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of