Standalone T/H Sensor

EcoStruxure IT forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT forum
  • Standalone T/H Sensor
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
124
Jef
Admiral Jef Admiral
110
gsterling
Captain gsterling Captain
71
APC_Steve
Captain APC_Steve Captain
64
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure IT forum
Solved
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 05:25 PM . Last Modified: ‎2024-04-04 11:56 PM

0 Likes
4
1095
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 05:25 PM . Last Modified: ‎2024-04-04 11:56 PM

Standalone T/H Sensor

Hi,

 

I need to monitor temperature and humidity on some IDF rooms.

We have Netbotz250 unit in the server room and where possible we are using remote T/H sensor connected directly to NB250 sensor port using CAT6 copper cable or trough Netbotz 150. 

On some location we only have fiber from server room to IDF switch so the solution above is not possible.

The actual only solution is to install a NB250 to each IDF .. but for only one sensor the solution is too expensive.

Do you know if there is a T/H sensor that can be connected to a Network port and managed directly by DCE ?

(CID:131958537)

Labels
  • Labels:
  • Data Center Expert
  • NetBotz
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 05:25 PM . Last Modified: ‎2024-04-04 11:56 PM

0 Likes
1
1095
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 05:25 PM . Last Modified: ‎2024-04-04 11:56 PM

Do you have any APC rack PDUs deployed in your IDF?  The newer 2G rack PDUs allows a temperature sensor to be connected.  It would be easier to justify upgrading a PDU with an additional temperature/humidity sensor purchase.

(CID:131958769)

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 05:25 PM . Last Modified: ‎2024-04-04 11:56 PM

0 Likes
0
1095
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 05:25 PM . Last Modified: ‎2024-04-04 11:56 PM

Hi Stefano,

 

Sorry but no. The NetBotz sensor pods and a-link sensors are not IP addressable and the communications across the cat-5 a-link connection is not TCP/IP. If the "IDF" room has a UPS in it, perhaps that UPS has a network management card to which you can often connect a temperature sensor. You could also look at wireless sensors if it is close enough and there's not much interference. 

 

Steve

(CID:131958545)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 05:25 PM . Last Modified: ‎2024-04-04 11:56 PM

0 Likes
1
1096
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 05:25 PM . Last Modified: ‎2024-04-04 11:56 PM

Do you have any APC rack PDUs deployed in your IDF?  The newer 2G rack PDUs allows a temperature sensor to be connected.  It would be easier to justify upgrading a PDU with an additional temperature/humidity sensor purchase.

(CID:131958769)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 05:26 PM . Last Modified: ‎2024-04-04 11:55 PM

In response to DCIM_Support
0 Likes
0
1095
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 05:26 PM . Last Modified: ‎2024-04-04 11:55 PM

No we still have the rack mount 1U PDU on the IDF due the low numbers of socket needed 

the PDU upgrade is more expensive that install a new NetBoot 250 in the idf 

(CID:131958809)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 05:26 PM . Last Modified: ‎2023-10-22 03:58 AM

0 Likes
0
1095
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 05:26 PM . Last Modified: ‎2023-10-22 03:58 AM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of